Partial & Total Discrimination Between 2 Circuit Breakers

09/21/2011 1:00 AM

the discrimination between two circuit breakers 100A(outgoing) & 160A(incoming) is 2KA for schneider & Total discrimination for ABB ......my Question is what does discrimination of 2KA mean? my understanding is that for a fault more than 2KA , incoming breaker will trip thus de-energising the supply of the entire DB. if anyone can explain further, i would be grateful.

thank you

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: partial & total discrimination between 2 circuit breakers

09/21/2011 1:28 AM

I think it's the other way around; the smaller downstream CB should trip at 2KA less fault current (for the same amount of time) than the upstream CB; thereby powering down a smaller part of the total system.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: partial & total discrimination between 2 circuit breakers

09/21/2011 1:42 AM

You may get some knowledge from an earlier thread

http://cr4.globalspec.com/thread/71318

i am surprised by your statement that discrimination is total in ABB (are you referring to Tmax ?) while it is 2kA in Schneider (NSX?). i think even in ABB, discrimination is partial only.

MCCBs are usually current-limiting. They do not have Icw rating. If you have a fault of 50kA on the system, it is quite likely that both MCCBs will trip. Or maybe the upstream or the downstream one. If you MUST have total discrimination up to the system maximum fault level, you have to use an ACB with an Icw rating as the incomer.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster #1
#3
In reply to #2

Re: partial & total discrimination between 2 circuit breakers

09/21/2011 3:09 AM

You may get some knowledge from an earlier thread

http://cr4.globalspec.com/thread/71318

thank you i did gain some.

i am surprised by your statement that discrimination is total in ABB (are you referring to Tmax ?) while it is 2kA in Schneider (NSX?). i think even in ABB, discrimination is partial only.

one of my friends works in ABB in LV switchgear division. he told me that there was total discrimination.but now i did some research and it turns out he was wrong,i was wrong. there is no discrimination between the 2 breakers. sorry

If you have a fault of 50kA on the system, it is quite likely that both MCCBs will trip. Or maybe the upstream or the downstream one.

you are giving 3 answers. The use of words "quite likely" & "maybe" is very fragile, especially when designing . sorry , can u be sure which is the right option. i dont wanna take any risk.

what about my original question of 2KA discrimination?

If you MUST have total discrimination up to the system maximum fault level, you have to use an ACB with an Icw rating as the incomer.

Using ACB for 160A will increase the cost, panel size etc. and ACB range starts from 600A in schneider and lowest setting in that breaker is 250A . so ACB cannot be used.

Reply
2
Commentator

Join Date: Sep 2009
Location: Singapore
Posts: 77
Good Answers: 1
#4

Re: Partial & Total Discrimination Between 2 Circuit Breakers

09/22/2011 1:57 AM

When you say total discrimination it means that the time current curve of two breaker will not intersect. When you say partial discrimination the time current curve will intersect at certain value like in you example it is 2kA. if you have fault on outgoing circuit greater than 2kA both incomer and outgoing will trip. Therefore your breaker will not be coordinated anymore if you have more than 2kA fault on outgoing circuit.

Reply Good Answer (Score 2)
Reply to Forum Thread 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); jonald (1); kvsridhar (1); Tornado (1)

Previous in Forum: DC Motor: Reverse Braking vs Regenerative Braking   Next in Forum: ISF of Current Transformer

Advertisement