Anonymous Poster #1

Installation of Pressure and Temperature Transmitter

09/29/2011 5:46 AM

I Came across an installation of a pressure and Temperature transmitter on a same 1/2 inch pipe..Let me explain the installation in Detail..

A 12 inch pipe has a vertical 1/2 inch nipple,1/2 inch coupling, Through which a 1/2 inch pipe is connected..Just after100 mm there comes a Tee where the RTD is installed at a distance of 200 mm from the tee parallel to the 12 inch pipeline..Going back on the vertical line of the pipeline..after 200 mm , a pressure transmitter is connected... Both the RTD and the Pressure transmitters are provided with a needle valve for isolation...

Is this installation acceptable??

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Installation of Pressure and Temperature Transmitter

09/29/2011 6:08 AM

It's clearly acceptable, as it has been installed. However, it could be improved by putting the RTD in a thermowell inside the main 12in pipeline. Presumably the whole shooting match is lagged so that, thermally, the RTD measures the process temperature, albeit somewhat slugged (rhetorical question)?

It's probably a short-term expedient to save shutting the process down while installing the RTD and getting it operable.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Good Answer (Score 2)
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#2

Re: Installation of Pressure and Temperature Transmitter

09/29/2011 7:43 AM

PWSlack has the right info on the temp. transmitter. Follow it.

There is no need for needle valves in this configuration. Simple ball valves will do; just make sure all wetted parts are compatible with process chemistry.

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Reply
Power-User
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -

Join Date: Sep 2011
Location: Bellingham, WA
Posts: 191
Good Answers: 46
#3

Re: Installation of Pressure and Temperature Transmitter

09/29/2011 8:36 AM

The presence of a needle valve between the RTD head and the tee demonstrates the RTD tip doesn't even make it to the tee, much less the main line. This is a bad installation of an RTD! Not only will there be unnecessary lag time introduced to the temperature measurement because of this, but there will also be an error in the direction of ambient air temperature.

__________________
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Installation of Pressure and Temperature Transmitter

09/29/2011 10:41 AM

Pressure transmitter is OK.

The RTD will never see any fresh process fluid. It will get its reading through thermal conduction of the process fluid and piping. This reading will always be lower than actual fluid temperature, due to heat loss of the stagnate fluid in the piping.

Reply Score 1 for Good Answer
Guru
United States - Member - USA! Hobbies - Musician - Sound Man Engineering Fields - Mechanical Engineering - More than a Hobby Technical Fields - Technical Writing - New Member

Join Date: Oct 2008
Location: City of Roses.
Posts: 2056
Good Answers: 101
#5

Re: Installation of Pressure and Temperature Transmitter

09/29/2011 12:46 PM

Get that temp probe in the main fluid stream or the readings will never be correct!

__________________
Don't believe everything you read on the Internet!
Reply Score 1 for Good Answer
Guru
Engineering Fields - Piping Design Engineering - New Member Egypt - Member - Member since 02/18/2007

Join Date: Feb 2007
Location: Cairo, Egypt
Posts: 1733
Good Answers: 248
#6

Re: Installation of Pressure and Temperature Transmitter

09/30/2011 12:47 AM

• Assembly of Pressure Transmitter with that procedure and using isolating valve is OK.

• But assembly of Temperature Transmitter is not OK, where your suggestion will lead to misreading of actual temperature of current fluid flowing. It will measure a temperature of a steady state portion of fluid, not representing the temperature of the whole fluid.

So you have to use a Thermowell using a NPTF half coupling (or flanged connection depends on the type of Thermowell) welded into 12" pipe which allowing a thermowell to be inserted at fluid inside the pipe, hence no need to use isolating valve.

Note. In case of pipeline less than 4", needed to install a thermowell, we have to make an enlargement to pipe size at portion of assembly of thermowell by welding a segment of pipe with larger diameter not less than 4" into the main line to allow a space inside the fluid for thermowell.

__________________
It is better to be defeated on principles, than to win on lies!
Reply Score 1 for Good Answer
Power-User

Join Date: Dec 2008
Location: Australia
Posts: 143
Good Answers: 24
#7

Re: Installation of Pressure and Temperature Transmitter

09/30/2011 12:59 AM

Just throwing this in the mix as no one else has - we need to consider the purpose of the RTD, as far as I've read, we're all assuming it is for measuring the temperature of the process solution flowing in the main line. This may not be correct.

Perhaps the RTD is not measuring the temp of the fluid in main line, but for some other reason. Perhaps it is to ensure accuracy of the pressure transmitter, or to ensure the PT is not operating above a max operating temperature.

I'd like to think, the engineer who designed the system is smart enough to know that the current configuration couldn't accurately measure the temp of the main process fluid.

Hope this helps.

Anthony

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #7

Re: Installation of Pressure and Temperature Transmitter

09/30/2011 4:22 AM

If the RTD is there to prevent the PT operating above its operating temperature then it will have a shutdown function. That function will be faster if, like many have suggested, the installation is altered so that the souce of heat or cold that could damage the transmitter, i.e. the main process line, is measured and shutdown quickly. Moving it to a thermowell in the main pipeline is still recommended.

Good point, though. The limits of temperatures and pressures of the process fluid are fundamental to most instrumentation and mechanical design considerations. It's strange how many instrumentation and mechanical specialists ignore these data in their postings and enquiries.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Participant

Join Date: Feb 2009
Location: Canada
Posts: 4
#9

Re: Installation of Pressure and Temperature Transmitter

09/30/2011 7:48 AM

As mentioned already, the RTD installation is not correct if trying to measure process temperature. Depending on the process characteristics, the PT installation may also be incorrect. This PT installation is fine for a gas process, but for a liquid process the PT must be installed below the process piping to ensure an accurate reading..

Reply Score 1 for Good Answer
Associate

Join Date: Jul 2011
Posts: 34
Good Answers: 1
#15
In reply to #9

Re: Installation of Pressure and Temperature Transmitter

10/08/2011 3:18 AM

Good point! I just wanted to add too that impulse lines should not be from the bottom of the pipe because of the possible presence of sediments or scale. This is straight from API RP 551. It is ONLY the PT installation that should be below the process piping in liquid service - self venting to avoid pockets of gas being trapped in the instrument.

Reply
Anonymous Poster #1
#10

Re: Installation of Pressure and Temperature Transmitter

09/30/2011 10:34 AM

Hi all,

The RTD and the pressure transmitter are used for the Flow compensation..The PT and RTD are installed just upstrem of the BWT ultrasonic flow sensor.

As i say, this is a 12" flare line. Is there any other alternative other than making a new tap on the pipeline for the thermowell

Cheers

Reply
Commentator
Venezuela - Member - New Member

Join Date: Aug 2010
Location: Venezuela
Posts: 88
Good Answers: 5
#12
In reply to #10

Re: Installation of Pressure and Temperature Transmitter

09/30/2011 10:31 PM

Friend,

As i say, this is a 12" flare line. Is there any other alternative other than making a new tap on the pipeline for the thermowell <---- Is the flare line working right now?...I think yes, right.

How much is the pressure/temperature during normal operation of the plants in this flare line?

Are you flowing some toxic gas or dangerous gas in this line?

Is there any posibility of changes the needle valves by ball valves?

Where is the flow compensation done? (flow transmitter, DCS, Flow computer)

How much money is being losing if the flow measurement is not good or near to the reality?

Is it very important or neccesary/urgent get this temperature?, your boss or manager plant cannot wait to the next major repair in order to install the thermowell in this line.

Regards

JP

__________________
Instruments-guy-SAV
Reply
Power-User
Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - New Member Technical Fields - Technical Writing - New Member Technical Fields - Education - New Member Fans of Old Computers - Apple II -

Join Date: Sep 2011
Location: Bellingham, WA
Posts: 191
Good Answers: 46
#13
In reply to #10

Re: Installation of Pressure and Temperature Transmitter

10/01/2011 8:10 PM

(post deleted by author)

__________________
They call me "lightning" when wielding a hammer, because I never strike twice in the same place
Reply
Participant

Join Date: Mar 2008
Posts: 4
#11

Re: Installation of Pressure and Temperature Transmitter

09/30/2011 3:06 PM

Hello.

The installation is not acceptable.
What exists is a capture to install a pressure transmitter or indicator of pressure, with his respective valve of cut or process and drainage.
The sensors of temperature do not have valve of cut.
If it you wants to measure temperature a capture has to install only for this sensor, in a way such that this measuring the royal(real) value of the temperature that is happening(passing) for the pipeline of 12 ".

Excuse my English since it is very poor.

Edgar

Reply
Active Contributor

Join Date: May 2010
Posts: 11
#14

Re: Installation of Pressure and Temperature Transmitter

10/05/2011 10:37 PM

The Pressure Transmitter is OK. But the Temperature will not measure the liquid in the pipe due to distance velocity lag.

Reply
Anonymous Poster #1
#16

Re: Installation of Pressure and Temperature Transmitter

10/08/2011 7:06 AM

Your comments in this thread are very much appreciated gentle men.

I would again make one point clear in this discussion that the service we are measuring is purely Gas. I believe I have mentioned the line as a flare line.

The line which connects the knock out drum and the Flare. So Its taken for granted that we measure the pressure and temperature of the Gas.

cheers

Reply
Reply to Forum Thread 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Abdel Halim Galala (1); ajwinemaker (1); Anonymous Poster (2); Edgar Espinosa Marca (1); Instruments-guy-SAV (1); Instrumenttech (1); lyn (1); Mikerho (1); PWSlack (2); RVZ717 (1); seg (1); SUMPI (1); tonykuphaldt (2)

Previous in Forum: Velometer and Accelerometer   Next in Forum: Honeywell 7850 Fault

Advertisement