10/11/2011 11:32 PM
I WANT TO DESIGN A TRANSFORMER FOR A SHIP. I HAVE ALL THE LOADS CONNECTED TO IT. IT HAS A 415V INPUT AND 230V OUTPUT. NOW I WANT TO CALCULATE THE POWER. FOR THAT I NEED CURRENT. HOW CAN I FIND IT?
Re: CALCULATE THE AMPS OF A LOAD CONNECTED TO THE TRANSFORMER
10/12/2011 12:13 AM
Add up the watts of all the concurrent loads (or all of the connected loads adjusted by a diversity factor). If the power factor (PF) is known, divide the kilowatts by PF to determine the required KVA of the transformer (allowing for some extra to start the largest motor). If the PF is not known, a common assumption is 0.80.
I'm not sure why you need a transformer in the first place. 415 volts in delta equals 230 volts in star.
10/12/2011 8:28 AM
the supply to the DC distribution board is given by the transformer which i mentioned earlier. If you don't mind please tell me that how to determine the current rating of a fuse which is connected to the loads.
10/13/2011 1:28 AM
You are confused man.Even I understood what you need to ask but you don't know how to ask ....Sum up all the connected load (watts) the voltage is 415V so;
Ampere = Watts/ (415 x 1.732 x .8)
Calculate the current as above way...
There are no shortcuts on the road to a great experience.
10/14/2011 12:05 AM
Why overestimation? get the complete Electrical diagram of the system or physically figure out and count all the loads,then consider 20% extra rating for the fuses If you want.
10/14/2011 7:43 AM
we are overestimating because we are designing the system. so, all datas regarding the lighting points and all are assumptions. The requirements will change depending on the customer. that's why we are planning to overestimate.
10/12/2011 12:14 AM
Dear, find below few usefull basic formulas for electrical system design.Do it by your self man...
Symbolic:
E =VOLTS ~or~ (V = VOLTS) P =WATTS ~or~ (W = WATTS) R = OHMS ~or~ (R = RESISTANCE) I =AMPERES ~or~ (A = AMPERES) HP = HORSEPOWER PF = POWER FACTOR kW = KILOWATTS kWh = KILOWATT HOUR VA = VOLT-AMPERES kVA = KILOVOLT-AMPERES C = CAPACITANCE EFF = EFFICIENCY (expressed as a decimal)
DIRECT CURRENT
AMPS=
WATTS÷VOLTS
I = P ÷ E
A = W ÷ V
WATTS=
VOLTS x AMPS
P = E x I
W = V x A
VOLTS=
WATTS ÷ AMPS
E = P ÷ I
V = W ÷ A
HORSEPOWER=
(V x A x EFF)÷746
EFFICIENCY=
(746 x HP)÷(V x A)
AC SINGLE PHASE ~ 1ø
AMPS=
WATTS÷(VOLTS x PF)
I=P÷(E x PF)
A=W÷(V x PF)
WATTS=
VOLTS x AMPS x PF
P=E x I x PF
W=V x A x PF
VOLTS=
WATTS÷AMPS
E=P÷I
V=W÷A
VOLT-AMPS=
VOLTS x AMPS
VA=E x I
VA=V x A
HORSEPOWER=
(V x A x EFF x PF)÷746
POWERFACTOR=
INPUT WATTS÷(V x A)
EFFICIENCY=
(746 x HP)÷(V x A x PF)
AC THREE PHASE ~ 3ø
AMPS=
WATTS÷(1.732 x VOLTS x PF)
I = P÷(1.732 x E x PF)
WATTS=
1.732 x VOLTS x AMPS x PF
P = 1.732 x E x I x PF
VOLTS=
WATTS÷AMPS
E=P÷I
VOLT-AMPS=
VA=1.732 x E x I
HORSEPOWER=
(1.732 x V x A x EFF x PF)÷746
POWERFACTOR=
INPUT WATTS÷(1.732 x V x A)
EFFICIENCY=
(746 x HP)÷(1.732 x V x A x PF)
10/19/2011 9:33 AM
First of all stop using capitals .It amounts to shouting.Now do u want to design a transformer or select a suitable transformer.Both are different.I don't think designing a transformer is your job.It is an expert job.