Schneider Electric NSX Micrologic1-5,6

10/15/2011 3:43 AM

I was going through catalogs of schneider electric NSX circuit breakers and I found this, electronic (micrologic) trip units 1-5 doesn't have inbuilt ground fault protection, But micrologic 6 has a ground fault protection inbuilt and its setting is (0.4-1 )x In. In being the nominal current. so I have 3 queries.

1) Does a normal MCCB protect against phase to ground faults

2) If no, is Micrologic 6 the only option for protection against ground faults. because ELCB or Vigi modules are only for earth leakage protection

3) If yes, why specify it as a separate term or a additional feature in Micrologic 6.

I still didnt get proper answer for my previous post.

http://cr4.globalspec.com/thread/72715#newcomments

thank you

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Schneider electric NSX Micrologic1-5,6

10/15/2011 5:12 AM

You did get an acceptable reply .... an RCBO will trip on an earth leakage of 30mA all the way up to 10 or 15kA.

Not good enough for you?

Micrologic has the feature all right, not only for NSX, also for NS and Masterpact. It still needs a CBCT to sense earth leakage.

This is my last post to you since you insist on remaining anonymous.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Score 1 for Good Answer
Anonymous Poster #2
#2
In reply to #1

Re: Schneider electric NSX Micrologic1-5,6

10/15/2011 5:48 AM

i am batman. common, what difference does it make, to know my identity when i am asking a valid question. you are not being rational here.

i didn't get an acceptable reply , that's why i commented again .http://cr4.globalspec.com/comment/782337/Re-Earth-Fault-Leakage-Circuit-Breaker.

i will be remaining anonymous as long as it takes.

i am not being rude, i just want some answers. coming back to this question

according to my knowledge CBCT is for detection of small currents and not large. its used for earth leakage detection and not earth fault detection. also in micrologic, there s no provision to connect CBCT . if CBCT has to be used , it must be connected to ELR which inturn must be connected to shunt trip coil or undervoltage coil of the breaker. and also for normal MCB there is no proper document saying that it will trip on a phase to ground fault.

anyways i am harry from al-ain, uae

Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#4
In reply to #1

Re: Schneider electric NSX Micrologic1-5,6

10/16/2011 12:39 AM

GA to you KV, I have used Masterpact 4000A with built in GFI 6.0 and they worked perfect at the farm.

__________________
"Real Bass Players" do not use picks
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #4

Re: Schneider electric NSX Micrologic1-5,6

10/16/2011 4:28 AM

Thanks Jim. Glad you have a good experience with the Schneider Masterpact 4000A. i always considered it a masterpiece of design, the constraints on the designers were stupendous, and they still delivered ! i take my hat off to them. Many times, i used to tell my team at GE "We should strive to make a product which will make people say 'Gosh! i wish i had designed that !!!' " The Schneider products, also some of the ABB ones, were in that class.

i had a superlative team, and we did some great products too. i hope you will use some of them sometime....

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#3

Re: Schneider Electric NSX Micrologic1-5,6

10/15/2011 3:05 PM

1) Does a normal MCCB protect against phase to ground faults

YES. MCCB detects ph-gnd faults as overload on faulted phase. However, it takes more time than CBCTwith ELR/ELCB.

2) If no, is Micrologic 6 the only option for protection against ground faults. because ELCB or Vigi modules are only for earth leakage protection.

Ques doesnt matter. bcoz answer to 1st ques is Yes.

3) If yes, why specify it as a separate term or a additional feature in Micrologic 6.

Already answered in 1st question. Takes less time since it works on residual circuit principle.

Reply Score 1 for Good Answer
Anonymous Poster #1
#5
In reply to #3

Re: Schneider Electric NSX Micrologic1-5,6

10/16/2011 1:01 AM

now it makes much more sense.thank you for your help.

also can i get any relevant document supporting your answer.

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #3

Re: Schneider Electric NSX Micrologic1-5,6

10/16/2011 1:38 AM

One small point.... the breaker will sense the eath fault as an overload only when it is > 130% of the rated current, is it not so? If yes, it will not act in the event of an earth leakage or earth fault (this terminology is only semantics. In USA, they are all called ground faults...GFCI is what the RCCB is called over there) below this current. This is dangerous, so it is always better to give earth fault protection.

Sensing can be done by CBCT or by 4 separate CTs one on each phase + one on neutral, summed up. One can perhaps also use Hall-effect sensors or something even more sophisticated.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8

Re: Schneider Electric NSX Micrologic1-5,6

10/16/2011 4:42 AM

As an anonymous poster, with a definite personality problem, no more replies from me......

Do remember that answers here cost nothing, all we ask for are reasonable manners, which are seemingly in very short supply with you.

Bye.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Active Contributor

Join Date: Sep 2010
Posts: 17
#9
In reply to #8

Re: Schneider Electric NSX Micrologic1-5,6

10/16/2011 5:27 AM

reasonable manners?

Have i insulted anyone with profane words? No.

did i ask anything stupid or personal question to offend anyone ? No.

my only mistake is that i was being anonymous. i had my own reasons for that.

anyways if u think thats a crime in CR-4 then here i am.

Reply Off Topic (Score 5)
Reply to Forum Thread 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (1); Anonymous Poster (2); harrybrown (1); Jimh77 (1); kvsridhar (3); muditmah (1)