I have recently joined a switchgear manufacturing company & I have a question regarding why in a distribution board , there is only earth leakage protection & not an earth fault protection. I mean to say is that there are MCB/MCCB + ELCB/ELR in a sub distribution panels and my understanding is that ELCB will only protect after detecting Earth Leakage current (upto 30A). Also MCB doesn't trip on a ground fault. so during a phase to ground fault, does the elcb provide protection for such large faults?
The elcb principle states that whenever the vectorial sum of phase and neutral currents is non zero (due to earth leakage, earth fault), elcb will trip. But is it safe for an elcb to handle large ground faults?
Re: earth fault,leakage & circuit breaker
10/06/2011 5:00 AM
Earth leakage equipment works by evaluating the vector sum of all currents passing through it. If this sum is higher than its trip setting, it trips.
Slam dunk.
India - Member - New Member
Good Answers: 164
10/06/2011 6:27 AM
There are now devices called "ELMCB"s. These are primarily RCD+MCB combinations, with the ability to sense overload and short-circuit also in addition to earth leakage, maybe capable of interrupting 6 or 10kA.
Good Answers: 164
10/06/2011 7:46 AM
The right name for this device is RCBO - Residual Current Breaker with Overcurrent protection.
Good Answers: 15
Re: Earth Fault, Leakage & Circuit Breaker
10/06/2011 11:24 AM
where did you encounter an earth leakage current of 30A? or did you mean 30mA?
. . . so when you use an RCBO . . . any earth leakage current higher than the set value causes the device to trip and disconnect the circuit . . . any overload current causes the O/L protection to take over and isolate the circuit . . . any very high current caused by short circuit (or "earth fault") causes the device to trip and disconnect the circuit . . .
the device to be used is selected by the specifier to ensure that the interrupting capacity of the device (6kA or 10kA are common in domestic use) selected is more than or equal to the possible "very high current" in the circuit even when there is a direct short circuit (or earth fault).
10/08/2011 12:40 AM
i have not encountered anywhere but i have seen a relay with a setting from 0.03A to 30A.
but when u say an earth fault(phase to ground), normal MCB or MCCBs doesnot trip. i have seen in the catalogues of major brands where they clearly mention whether ground fault protection is provided or not. for eg. in schneider electric, MCCB with TM trip unit doesn't have ground fault protection, while MCCB with Micrologic 6 does. and a normal MCB doesnt provide ground fault protection.
Micrologic 6 trip unit is a costly trip unit and is usually not used in SMDB or SDB.
can u please clear my query?
10/08/2011 1:20 AM
In MCCB with micrologic what is the method used to detect EF?. For other MCCBs too if you connect a core balance transformer or EFR it will trip. Even MCB can be fitted with tripping coil.
pnaban
10/06/2011 11:12 PM
As I understand your above mentioned doubt, so be sure that ELCBs are only for earth leakage protection and MCBs are for short circuit & Overload protection,so the earth fault is also to be considered as Short circuit, therefore If you need to protect a circuit from Earth Leakage + Short circuit then go with the combination of MCB+ELCB.
There are no shortcuts on the road to a great experience.
10/08/2011 12:52 AM
sir can u see my comment no. 7 and help me out?
10/07/2011 12:44 AM
The arrangement in sub DBs or CUs is ok but did you check main switchboards(MSB) where in some they use ELR with core balance transformer while in others they use EFR depending on Amp rating of incoming CB?. Upto what Amp rating of load (or incomer) ELR is used and why?.