Busbar Continuous Current Rating For Multiple Sources

10/16/2011 8:18 AM

Hi,

I have come across a situation, wherein there are two DG set each of 415V, 3 PH, 2.5 MVA capacity connected to two bus sections of LV board with buscoupler in between. Each bus section also has load feeders having aggregate total of approx 2.5 MVA. DG set breakers are of 5000A capacity. DG set will also run in synchronised mode. So each bus section fed by each DG set be rated for 5000A or 2 x 5000A, i,e, 10000A.

Is it practicable to design a busbar of 10000A capacity?

Register to Reply
Pathfinder Tags: busbar sizing multiple sources
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Busbar Continuous Current Rating For Multiple Sources

10/16/2011 5:47 PM

If your bus is laid out like this, nothing needs to be over 5000 A:

(2.5 MVA of loads)-----(1DG)-----(bus tie)-----(2DG)-----(2.5 MVA of loads)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Oct 2011
Posts: 2
#2
In reply to #1

Re: Busbar Continuous Current Rating For Multiple Sources

10/16/2011 9:43 PM

But in this case, if load MVA or a fault MVA on DG-1 load side bus section exceeds say 3 MVA, then it may lead to overheating of busbar as it will be fed by both DGs without exceeding their rated capacity.

Also my second question - is it necessary to have specific locations of DG & bus tie breakers? If my load feeders are fixed & no additional load would be put on then can I go ahead with 5000A bus sections and breaker locations to suit the DG set & LV board layout. This will help reduce DG incoming busduct length and no. of bends.

Do we need to consider fault situation of rating higher than say 3MVA but less than 5.5 MVA. Because all faults higher than 5.5 MVA will trip the DG breakers due to DG overcurrent / earth fault protection.

Register to Reply
Commentator

Join Date: Oct 2009
Location: Dubai,UAE
Posts: 62
Good Answers: 2
#3

Re: Busbar Continuous Current Rating For Multiple Sources

10/17/2011 3:35 AM

It depends upon your required applications and conditions as per your given details, there is no need to run both generators in synchronization mode. It is not required because your each generator can carry all the loads. so 5000A busbar is ok for the full loads. Go as<<<<< DG1----Bus-coupler------DG2>>>>> both DGs can be run parallel or If one DG is failed then buscoupler will allow the other DG to take the loads.

__________________
There are no shortcuts on the road to a great experience.
Register to Reply
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#4

Re: Busbar Continuous Current Rating For Multiple Sources

10/20/2011 6:58 AM

If both DGs are to be run in synchronized mode i.e. buscoupler will normally be in close condition then go for 10000 Amp bus bar. Yes it is practical.

Register to Reply