I am sizing a DC battery bank for my hydro project of 6x200 MW capacity. should i directly multiply my loads(I) with time(t) to get AH capacity of battery or do i need to adopt some other method. If so, then please inform me.
lets talk some technical
Pathfinder Tags: DC battery
Re: DC battery sizing
10/19/2011 1:40 AM
This project is dead on arrival. Battery storage is totally stupid for this much capacity.
(Ignoring 1-phase vs 3-phase, as well as various losses, battery AH = Wt/V; where V is battery voltage, W is load in watts, and t is hours.)
10/19/2011 1:57 AM
Right - 1.2 gW is a fantastic amount of power - sounds like a school assignment to me.
10/19/2011 10:38 AM
One point twenty one gigawatts? One point twenty one gigawatts? Great Scott!
Maybe he's going Back to the Future.
10/19/2011 11:02 AM
If that's the case, he's going to need a "flux capacitor", not batteries
Good Answers: 12
10/19/2011 5:48 AM
GA. Only through dams power in the range of Megawatts can be stored; not by any other mean. But when you have already stored energy in the form "Hydro" why again to store?
Subramanyam
10/19/2011 6:14 AM
actually sir this is our company project. Provide me some information if u have got regarding this subject
10/19/2011 10:26 AM
If you are talking about emergency backup power for your control system then you might say so.
Good Answers: 170
10/19/2011 4:43 AM
If you can mail me your mail ID thro this forum's mailbox, I can send you some battery sizing calculations that we have done for a 2 x 500MW Thermal Power Plant
10/19/2011 5:14 AM
Right - how much storage did you consider?
Good Answers: 12
10/19/2011 5:50 AM
Also you can download free from our company web site: http://hbl.in
Subramanyam
Re: DC Battery Sizing
10/19/2011 10:10 AM
For a power plant of 6x200 MW capacity you will need Essential and Emergency power supplies as follows:
(a)Power supplies for the protection, emergency shut down and switchgear operation rated usually at 110 volts DC.
(b) 220 V Single phase essential power for the anti-condensation heaters, essential lighting and for battery chargers.
(c) 48 volts or 24 volts essential dc power supplies for DCS / SCADA and Communication (instrumentation).
  • Typical rating of 110 volts DC system for the high voltage substation is 30 to 50 kva.
  • Typical rating of 110 volts DC system for the 6x200 MW power house is 30 to 50 kva is separate from the substation.
  • For the essential loads 220 v AC usually a 500 KVA three phase diesel generator is installed and the single phase loads are evenly distributed.
  • 48v / 24 volt requirement is best left to the instrumentation department or should also be around 30 to 50 KVA.