Previous in Forum: Control Symbol Meaning   Next in Forum: Elmex Terminal
8 comments
Battery Charging Voltage
10/20/2011 12:30 AM
To charge a 220 DC battery bank what value of charging voltage per cell can be used. Voltage variation can be taken as max- 242V & min- 198 V. Please also suggest the value of float voltage that should be adopted.
lets talk some technical
Good Answers: 12
Re: Battery charging voltage
10/20/2011 12:36 AM
It depends on Battery cell type/ make/ model. All reputed manufacturers mark/label this voltage on the product.
Subramanyam
Re: Battery Charging Voltage
10/20/2011 1:48 AM
Take account of the specific gravity of the electrolyte and not the voltage of charger.
Specific gravity at full charge is 1.26, half charge is 1.197 and discharged is 1.135.
Terminal voltage per cell is an approximate measure since applying load on the battery will cause the voltage to dip or considerably increse if load is removed.
Knowledge sharing is a WIN-WIN situation
Good Answers: 266
10/20/2011 7:26 AM
Float voltage 2.15 volts per cell
To maintain float voltage 2.25 - 2.30 volts per cell
Charge voltage 2.30 - 2.35 volts per cell
I recommend a charger that has an equalizer setting as it will reduce sulfation
Equalizer voltage 2.40 - 2.45 volts per cell.
10/20/2011 7:29 AM
Talk to the manufacturer only - no one should be making suggestions about charging rates or float current without the manufacturers recommendation in hand.
It varies-
10/21/2011 4:32 AM
Well put and really accurate. The first one reading down from the top!!
Good Answers: 110
10/21/2011 12:49 PM
Good answer. No other approach makes sense. Do it right or risk damaging the batteries. Recommended charging currents and voltages at every stage in the charge and equalizing process should be followed.
Think big. Drive small.
Good Answers: 59
10/20/2011 10:43 PM
TALK TO THE MANUFACTURER ONLY, and its website. Even if I assume lead/acid cells, the maker sets charging / discharging / floating. Those values are dependent on the acid density and temperature strongly. Without those curves and charts you are whistling in the dark. The same applies for maintenance schedule. The resulting voltage variation for the whole set is established by the individual cells, and it is whatever it turns out to be.
10/20/2011 11:06 PM
The manufacturers recommendation is very important, particularly with sealed batteries as overcharging can be fatal, but also the depth of charge is important, as in deep cycle situations, with proper deep cycle batteries, (flooded) the equalisation or even daily max. voltage can exceed 2.5 volts. Electrolyte readings are good but one must be aware that many deep cycle batteries have dilute electrolyte (to reduce acid corrosion of plates) and maximum specific gravity is 1.24. Also, many modern (often called smart) regulators, have provision for temperature measurement and corresponding adjustment and again that is something the Manufacturers specifications will have input on. Cheers, Geoff Thomas.
Let's try and think clearly when looking at information and only allow emotions when weighing up options.
Register to Reply 8 comments