Range of LT

10/21/2011 11:29 AM

Dear friends,

I have a close tank which having condansate. distance betweet impulse line tapping is 500mm (tank height). I am using DP type level tx to measure level. what should be the URV & LRV range for this tx?

Register to Reply
Pathfinder Tags: Level tx range
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Range of LT

10/21/2011 11:39 AM

A range of 500mm of water will do just fine.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Dec 2007
Location: texas
Posts: 92
Good Answers: 8
#2

Re: Range of LT

10/21/2011 6:59 PM

Hi,

URV and LRV can be calculated using the following formulas:

LRV= PH-PL (level height is at zero percent level)

URV= PH-PL (level height is at 100 percent level)

P=h X S.G. (p=pressure, h=height, S.G.=specific gravity)

PH= pressure on high side

PL= pressure on low side

Thank you

__________________
"The older I get -The better I was"
Register to Reply
Associate

Join Date: Sep 2011
Location: India
Posts: 28
#3

Re: Range of LT

10/22/2011 2:25 PM

hi dharam, to find the value of lrv and urv you must first understand the requirement of process like what should be the minimum level (there might be some pump tripping) or what should be the maximum level so that suction valve start. You can have your lrv and urv 0 and 500 mm but that might not be required by your process. So it is better to talk with your Process people.

__________________
I am man of simple taste.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Dec 2008
Posts: 41
#4
In reply to #3

Re: Range of LT

10/23/2011 10:01 PM

ok, but my lrv range is -500mmwc and urv is 0, lt is working fine.

Register to Reply
Commentator

Join Date: Dec 2007
Location: texas
Posts: 92
Good Answers: 8
#5

Re: Range of LT

10/23/2011 11:31 PM

HI,

Is the low side of the D/P transmitter connected to the bottom of the tank?

or

Is the low side of the D/P transmitter connected to the top of the tank but it's used as wet leg filled with liquid of a S.G. equal to 1?

If you are using one of these two scenarios then it's possible to have URV=0mm of H2O and LRV= -500mm of H2O

Thank you

__________________
"The older I get -The better I was"
Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dharam_ver9 (1); jeetu (1); PWSlack (1); wrenchpuller (2)

Previous in Forum: Pressure Transmitter for Cylinder With Grease Medium   Next in Forum: Calibration Standards

Advertisement