10/21/2011 11:29 AM
Dear friends,
I have a close tank which having condansate. distance betweet impulse line tapping is 500mm (tank height). I am using DP type level tx to measure level. what should be the URV & LRV range for this tx?
Pathfinder Tags: Level tx range
Re: Range of LT
10/21/2011 11:39 AM
A range of 500mm of water will do just fine.
Re: Range of LT
10/21/2011 6:59 PM
Hi,
URV and LRV can be calculated using the following formulas:
LRV= PH-PL (level height is at zero percent level)
URV= PH-PL (level height is at 100 percent level)
P=h X S.G. (p=pressure, h=height, S.G.=specific gravity)
PH= pressure on high side
PL= pressure on low side
Thank you
"The older I get -The better I was"
Re: Range of LT
10/22/2011 2:25 PM
hi dharam, to find the value of lrv and urv you must first understand the requirement of process like what should be the minimum level (there might be some pump tripping) or what should be the maximum level so that suction valve start. You can have your lrv and urv 0 and 500 mm but that might not be required by your process. So it is better to talk with your Process people.
I am man of simple taste.
Re: Range of LT
10/23/2011 10:01 PM
ok, but my lrv range is -500mmwc and urv is 0, lt is working fine.
Re: Range of LT
10/23/2011 11:31 PM
HI,
Is the low side of the D/P transmitter connected to the bottom of the tank?
or
Is the low side of the D/P transmitter connected to the top of the tank but it's used as wet leg filled with liquid of a S.G. equal to 1?
If you are using one of these two scenarios then it's possible to have URV=0mm of H2O and LRV= -500mm of H2O