Capacitor Bank

10/25/2011 4:40 PM

1)what happens if power factor is leading?

2)what is hot start and cold start in case of HT(6.6kv,3MW motors)?

3)why current drawn by capacitor bank is not added to the system load?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: capacitor bank

10/25/2011 10:30 PM

1) What happens if power factor is leading?

If you are a utility consumer and maintain the power factor leading, it will have the same effect as you maintain it lagging. In this case, you are spending your money (such as for using capacitor bank) and helping the utility for no benefit (unless you maintain it close to unity and get power fator penalty waived).

If your power is supplied from generator and you maintain the overall power factor leading, the generator will be unstable. Synchronous generator is able to supply power to the loads of lagging power factor only.

2) What is hot start and cold start in case of HT (6.6kv, 3MW motors)?

Hot and Cold condition of the motor refer to state of the temperature of the motor as a whole (especially the stator and rotor winding) when the motor is started.

Cold condition: When the temperature of the motor stator and rotor winding is at ambient temperature, the motor is considered 'cold condition'. If a motor remains stopped for relatively long period of time (generally half an hour - depends on motor size), it is considered cold condition and the start of a motor at this condition is called cold start.

Hot Condition: When the temperature of the motor stator and rotor winding is above the ambient temperature, the motor is considered 'hot condition'. If a motor is already hot from either an initial start or a period of recent full-load operation, it is considered hot condition and the start of a motor at this condition is called hot start. The hot start of the motor further raises its temperature to a higher level due to the subsequent restart and cause the motor damage. The motor protection relay generally prevents motor damage by limiting the number of start per hour and/or from further hot starting of the motor.

See this link for more detail: http://findarticles.com/p/articles/mi_qa3726/is_200806/ai_n27900075/ (click Next to move forward)

Note: the answer is copied from my earlier post: http://cr4.globalspec.com/comment/546312

3) Why current drawn by capacitor bank is not added to the system load?

Capacitor current (leading) contributes to reactive load (power), not to the real load (power).

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: capacitor bank

10/25/2011 11:07 PM

3) Although the capacitor current and motor current are added vectorially, the vector directions are somewhat opposed. This results in a decrease of the total current supplied.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Capacitor Bank

10/26/2011 7:53 AM

If the power factor is leading, there is too much capcitance in circuit, and if on a power factor tariff, there will be a financial penalty imposed by the Utility company.

Reduce capacitance in circuit until the power factor approaches unity.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply