Planning Low Fuel Consumption DC Diesel Generator

10/29/2011 3:55 PM

Dear users, I am a beginner, I need some advice at my prototype.

I have finished my prototype at dc diesel generator

diesel engine : kubota Z-482, 2 cylinders, 6.9KW at 3000 Rpm, water cooled.

alternator : custom spec 3 phase brushless alternator, 4 pole, 1500 Rpm, 8KVA,

DC load : telecommunication equipment 3.12 KW at 52 VDC

the reasons Iuse kubota diesel engine Z-482, because the users said it must two cylinders diesel engine and it must water cooled, and because the peak load only 3.12 KW. so kubota diesel engne Z-482 is worth choice I think, at specific engine speed.

I use custom spec alternator from one of china manufacturer,

4 pole, 1500 Rpm, 8 KVA / 6.4 KW, 6 coil, 12 lead, Iask to manufacturer to make each coil voltage at 55VAC at 1500 Rpm.

each coil use independent full bridge rectifier 50AMP 400V, Iuse 6 pieces full bridge diode rectifier, because the alternator have 6 coils,

capacitor filter 100.000 UF-80 VDC, coil filter 2mH-0.01Ω, use email wire and the diameter of wire 4.7mm.

the AVR was custom, and i make it by my self, and powered from standard battery charger alternator at the engine, he is permanent magnet alternator 22VAC and the rated power about 220 Watt, the AVR power consumption at full load is 30Watts, 15Watt to rotor exciter coil and 15Watts at AVR electronic part.

AVR topology use PWM, power limiter from current limiter feedback (isolation feedback) from load line, load current sense, load voltage sense, and adjustable current limiter 40AMP to 65AMP, and adjustable output voltage too, from 48VDC to 60VDC.

the engine speed set at 2200 Rpm at no load,

no load voltage 55VDC, and at full load 3.12KW the output voltage at 52VDC and the current 60 AMP, than the engine speed goes down to 1900 Rpm. the ripple voltage about 500mV.

total net fuel consumption is 1.4 liters each hours at rated load 3.12KW at output Voltage 52VDC, and at output current at 60Amp.

I tested the fuel consumption for 10 times, and each test time is about 4 hours.

my customer target at fuel consumption is 1.2 liters each hours

did 1.4 liters each hours good enough ?

did the target 1.2 liters each hours still reasonable ?

the engine still okay at full load, because there isn't any smoke out from the muffler which the indicator that the engine not at full load yet. but when i turn the speed at maximum load to 1800 Rpm, the smoke start to see come out from the muffler.

I need advice, what must i do to reach that challenge......

and what i have to do again to make my prototype will be better

Best Regards

Thank You

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: planning low fuel consumption dc diesel generator

10/29/2011 4:07 PM

1.4 lph is very close to the target.

The easiest modifications would be to the intake system or the exhaust system.

Maybe you could find a low restriction air cleaner for the intake.

Or, if you are easily meeting the target sound level, you might consider using a low restriction muffler in place of the standard muffler.

Maybe you could run a test with the air filter removed, to see if that helps lower fuel consumption.

Other modifications will be more difficult.

Also, more efficient alternators, or engines may be available, I don't know.

Good luck, keep us updated.

Register to Reply
Active Contributor

Join Date: Apr 2010
Posts: 12
#2
In reply to #1

Re: planning low fuel consumption dc diesel generator

10/29/2011 4:44 PM

Thanks Lyn

in my long calculations, the alternator efficiency about 86%, and it is good enough for excitation alternator. the branded is china stamford

in my idea : i will try to ask to alternator manufacturer could they rise the efficiency, and i hope they can.

1> maybe from email quality grade, at stator and rotor wire

2> from bearing quality grade,

3> and maybe i will ask multi wire email wiring than single big wire at the coil wiring.

4> and etc

about air filter, i will try it to use 30KW diesel engine air filter, from kubota engine too, because i have a friend there. i think the air filter will have more much air flow area.

about the muffler, maybe i will redesign it, because the prototype it is still use standard muffler from the engine, and about sound level target, i think i will use double muffler but at low restriction type,

about the engine, the two cylinders diesel engine in my country the kubota branded was more easy to find it, ( worth price and worth quality i think ), for the other branded the candidate was at yanmar 2TNV70 and mitsubishi L2E, it is difficult to find in my country.

but, thanks for Your advice Lyn

regards

Register to Reply
Guru

Join Date: Oct 2008
Location: Deepest Darkest Rutherford Oz
Posts: 951
Good Answers: 145
#3

Re: planning low fuel consumption dc diesel generator

10/29/2011 5:59 PM

If you have the govenor/injector pump reset to run at the alternators spec speed of 1500rpm then you will find your improvement in fuel consumption and nvh.

You may be over fueling due to the fact the motor was factory set to be efficient at 3000rpm. See you service agent for the correct setting procedure.

__________________
There are two reasons for a man to do a thing, One that sounds good, and the real one...
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#4

Re: planning low fuel consumption dc diesel generator

10/29/2011 11:00 PM

Diesels run the most economic round the max. couple RPM. You might check that out. Kubota should have the fuel consumption at different loads and RPM.

Is the governor a standard one or a fixed RPM/couple one? As said before the injection pump - can do wonders if you adjust or change the regulator. You need a Kubota for generator. Not for e.g. a small sailboat drive, or car.

Both have a different governor.

__________________
Plenty of room here
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#5

Re: planning low fuel consumption dc diesel generator

10/30/2011 4:53 AM

Interesting blog.

I have a question, how can a 3 phase alternator have 4 poles? You wrote:-

alternator : custom spec 3 phase brush less alternator, 4 pole, 1500 Rpm, 8KVA,

Maybe I need to learn something new here, please explain....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#7
In reply to #5

Re: planning low fuel consumption dc diesel generator

10/30/2011 8:11 PM

Hello Andy,

A 1500 rpm alternator makes 25 mechanical turns a second.

If it only had one magnet on its rotor, a stationary coil on the frame would see first one north pole next to it, then one south pole half a revolution later.

If a passing north pole gives a positive voltage in the stator coil, then a passing south pole gives a negative voltage - it's that famous alternation!

But one + and one - repeated 25 times a second is only 25 cycles a second (Hz).

To get 50 Hz, there have to be magnets on the rotor in a "cross" (cruciform) formation. Then in one turn, the stator coil sees N-S-N-S poles - that is why it is called 4 pole rotor. Try a diagram, the § represents stator coil and • the shaft axis, rotate the rotor around • (ignore the ... - CR4 keeps deleting spaces!)

...N

S • S

...N

...§

The trick is to give the rotor a cross - shaped section and put a magnet or electromagnet winding in each limb. The CR4 entry will not let me put a | and an N on lines under the top S, and similar above bottom S, but I hope you get the idea. The magnets join e.g. S-N-S-N between adjacent limbs of the rotor (at first sight, it seems they cancel each other crosswise).

.....S

N-S•S-N

.....S

To get three phases, stator coils are put (and wired) in pairs 180 degrees apart, on opposite sides of the rotor. You make it with 3 pairs, spaced 120 degrees apart, one phase per pair.

A question for you, how do you get to give your latitude and longitude with an accuracy of 4 inches? Is the reference point the dog's basket?

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#9
In reply to #7

Re: planning low fuel consumption dc diesel generator

10/31/2011 6:15 AM

Google earth........

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
2
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6

Re: Planning Low Fuel Consumption DC Diesel Generator

10/30/2011 5:16 PM
  1. The Kubota data sheet for type 482-E3B [see http://www.kubotaengine.com/products/pdf_en/01_z482_36.pdf] graph gives shaft power rating of 8.1 kW continous at 3000 rpm, falling to 5 kW @ 1800 rpm. N.B. this will be a sea level rating at 15 Celsius and standard values of atmospheric pressure and humidity - if you are up a mountain or hot, wet climate then power reduction can be considerable (due to reduction of oxygen available to burn).
  2. This is gross intermittent rating, I have not researched the standards indicated by Kubota, but I suspect this is a 1 hour rating. Rating for continuous use is 80% of that gross intermittent. You have not indicated your required running time, but I would expect "continuous" for telecoms.
  3. Also gross means without necessary items like water-air cooling fan, 12 volt alternator and maybe water pump which vary with system designed by user. They can use up to 10% of shaft output.
  4. The fuel consumption given at 1800 rpm is 265 grams per kW-hour. You write the engine is visibly smoking at 1800 rpm and required DC output. This probably means it is overloaded, or at least at 1 hour power - but say it is giving 5 kW, it would take 265 x 5 = 1325 grams/hour. Diesel has a specific gravity of about 0.9, so that makes 1.325/0.9 = 1.47 litres per hour. Your measurement of 1.4 litres/hour is no surprise!
  5. Output 3.12 kW for 5 kW input makes 3.12/5 = 0.62 efficiency. The diode bridges will lose 4% and say cooling fan is 4% loss, leaves about 70% efficiency for alternator. I think your figure of 86% alternator efficiency is very high for this size of machine. Did you tell the maker it is rectifier service rather than usual resistive load?
  6. I do not understand why you specified 1500 rpm for alternator! Engine speed of 2200 rpm is a good choice, because it is optimum fuel consumption (and gives power/speed margin for continuous rating and good life), but getting generator for 1500 rpm is mismatched and will lower efficiency - you cannot even be sure the bearings are mechanically good for 1800 rpm, let alone 2200! 110 % of rated speed is over-speed trip for a generator.
  7. Have you measured the DC voltage drop of your filter reactor at rated DC output, engine driven?
  8. Do you mean 100000 microfarad capacitor - remember some countries use "." as decimal separator and "," to indicate 1000s - making your value 100 μF to me! 100000 μF is about 4.4 milliohm reactance at 360 Hz ripple - so 500 mV rms ripple requires about 110 amps rms ripple current through the capacitor. Maybe you have more of a "capacitor input" filter effect with its high peak current and losses than you think?
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8
In reply to #6

Re: Planning Low Fuel Consumption DC Diesel Generator

10/31/2011 6:13 AM

GA

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Active Contributor

Join Date: Apr 2010
Posts: 12
#10
In reply to #6

Re: Planning Low Fuel Consumption DC Diesel Generator

10/31/2011 8:37 AM

hello 67model

thanks for the explanation,

previously i would like to continue Your answer for Andy Germany

Andy Germany, please open en.wikipedia.org/wiki/alternator

and i think we are all clear about N=120 f /P,

N = is a rotational speed in Rpm,

f = is frequency,

P = is number of pole.

and between pole number and phase number there isn't any direct relationship, phase number goes to the way of wiring at the stator slot.

and pole number goes to the output frequency of alternator at given shaft speed from source.

You can make 1phase alternator with 2pole rotor, shaft speed 3000 Rpm and it will have frequency output 50Hz, if You have 4pole it will have 100Hz at same shaft speed,

You can make 3phase alternator with 2pole rotor, shaft speed at 3000Rpm and it will have frequency output 50Hz, if You have 4pole it will have 100Hz at same speed

You can make 3phase alternator with 4pole and to get 50Hz frequency You must turn the alternator shaft at 1500Rpm and if You turn at 3000Rpm it will have the frequency output at 100Hz. and 200Hz at 6000Rpm and go-on. ** sorry if i am wrong **

and 67model about Your explanations,

1500Rpm alternator it will okay to drive by 1800Rpm,

at my prototype, no load speed is 2100Rpm, ( sorry i am wrong, it is not 2200Rpm )

and at full load 3.12Kw (DC LOAD) the engine will goes to 1900Rpm.

it is for continuous duty, ok if follow Your calculation, maybe i am wrong at alternator efficiency calculation,

but the main thing is, can i reduce the fuel consumption again ?

what i must to do....? any part or any system or any modification again to do to reach more low fuel consumption.

at 3phase brushless alternator to get frequency 50 Hz, the alternator drive by engine speed 1500Rpm and for 60Hz electrical system the engine set at 1800Rpm.

and for no load speed, the initial speed setting usually + 5 % to 8% higher from rated speed and it is clear from tolerance frequency range 45 HZ to 55 Hz for 50 Hz system, and 54Hz to 66Hz for 60Hz system.

so 1900Rpm at full load it will have the frequency output 63 Hz it still save for alternator, and still at speed range initial setting at 60Hz system.

for 60Hz system the diesel engine speed usually sett at 1890Rpm,

so 1890Rpm to 1900Rpm i think it is closed enough.

and this dc diesel generator always use at 80% at rated power so the average engine speed not far from 1900 Rpm.

drop voltage at filter choke was 0.6VDC at 60Amp load.

i use 100,000 µF ( one hundred thousand micro farad ) capacitor filter.

yes 1.4 liters maybe it is not surprise, that's away i need advice what must i do to reduce full consumption again

i use 4pole alternator, because my engine speed work at 1900Rpm to 2100Rpm

closed to 1500Rpm alternator rather than to 2pole 3000Rpm alternator

my target was 1.2 liters each hours at 3,120Watt Dc Load, is this still reasonable...?

regards

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11
In reply to #10

Re: Planning Low Fuel Consumption DC Diesel Generator

10/31/2011 9:25 AM

Thanks, got it.

The problem was I was thinking of the stator at first, not the rotor. If the OP had said "rotor" poles, I would not have posted......misunderstanding of terminology only....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#14
In reply to #10

Re: Planning Low Fuel Consumption DC Diesel Generator

11/01/2011 7:38 AM

Saut Syafrudin,

If the generator is designed for 1500 rpm, to get same voltage it must have 26% more turns than if it ran at 1900 rpm.

There is a fixed space for stator copper, so wire cross section must be ~80% of that for 1900 rpm (and the wire length is 126%).

So you have a factor of 1.26/0.8 = 1.58 increase of resistance, which will increase generator loss dramatically at same load current. I expect, at this low voltage, resistive losses are a big part of generator loss. Less loss will be less temperature rise and lower hot resistance - reducing losses more.

I suggest you measure stator winding resistance cold and hot to check its temperature rise and get oscilloscope trace of winding current to calculate I²R loss. 3 phase rectifiers only conduct for 1/3 of cycle in each diode. Oscilloscope trace will also check effectiveness of filter inductor.

FETs in place of diodes can only remove part of ~4% of total loss - you require 20% improvement. Driving 6 x 4 = 24 FETs at the right time will be expensive!

I suggest you consult generator maker on how to best connect windings to have 3 phase output with just 3 terminal output and 6 diodes instead of 24.

67model

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#15
In reply to #14

Re: Planning Low Fuel Consumption DC Diesel Generator

11/01/2011 2:42 PM

Another factor for 1500 rpm generator run at 1900 rpm.

Cooling fan of generator is designed adequate at 1500 rpm - but its power consumption increases on cube law of rotation speed.

So it uses twice the power at 1900 rpm.

Power and fuel is being wasted to over-cool the generator.

Register to Reply
Active Contributor

Join Date: Apr 2010
Posts: 12
#16
In reply to #14

Re: Planning Low Fuel Consumption DC Diesel Generator

11/03/2011 3:48 AM

Dear 67model and all

thanks for your reply,

sorry, if i am not wrong, when we need same voltage at highest speed, so we can reduce the turns of coil.

or we can use more low turns and more diameters of wire to get same voltage but more amps.

because my prototype already almost fixed (but it still need optimizing final results),

so i will do next steep from the last configuration, although it not close for new system or new modifications.

  1. i have ever try to use 3000 Rpm synchronous generator and drive at 1900Rpm to 2100Rpm, the final result 1.6 liters/hours, same KVA same rated voltage, and all same conditions, except generator
  2. and if i use this 300Rpm generator, the generator was 2 pole rotor, the output ripple was more big than if i use 4 pole generator
  3. because the smallest power of 3 phase 4 pole 1500Rpm generator was 8Kva/6.5Kw, so i use them. at custom spec, and i got 1.4 liters/hours
  4. yes, the generator speed at no load was record 2100Rpm, and at full load was 1900Rpm, 3120Watts, 52VDC and 60Ampere

spec of synchronous generator i use now :

  1. 4pole 1500Rpm to 1800Rpm,
  2. 8Kva / 6.5Kw,
  3. rated voltage 55 VAC X 6 Coils independent output, and reconnect-able end lead wire, totally there is 12 end lead wire,

if i am not wrong we must use the power of the diesel engine at range 75% t0 85%, to reach most efficient specific fuel consumption. so the engine speed 1900Rpm is the ideal speed.

because the DC load only 3120Watts, and the Diesel engine must two cylinders and water cooled, so the last configuration in my prototype was the most ideal form. but i still need to rise up the efficiency any more.

and two of my friend / colleague done same thing at they research, they got the best results at 1.6liters/hours .

different 0.2liters / hours, was different fuel consumption at 1,752 Liters / years.

and it is about 2,100 US $ each years.

if i could be reduce 0.2 liters / hours again from 1.4liters / hours , so i will have lowest 4,100 US $ annual cost at fuel only. if compare from my friend research/ my friend prototype.

yes 67model, about fan losses at higher Rpm i agree with You, but it is the consequence.

frankly, 1.4liters / hours was the best results in my country at this present, at the last estimated mass product price of the prototype.

and because my customer still ask me : Can i reduce the fuel consumption again ?,

i said i am try, and i need time.

my prototype dc diesel generator

  1. 3.12 KW
  2. 52 V DC
  3. 60 Ampere
  4. 1.4 liters / hours
  5. no load speed 2100Rpm
  6. full load speed 1900Rpm
  7. ever tested at 24 hours at full load, no change at all output parameter
  8. no change at engine temperature (oil, water, muffler, and engine body)

and at this forum i need help, and need answer, can i reduce fuel consumption again ?

what i must do ?

best regards

saut

sorry for my bad english language

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#17
In reply to #16

Re: Planning Low Fuel Consumption DC Diesel Generator

11/03/2011 7:01 PM

What must you do? You must improve the low generator efficiency which is wasting power and fuel.

I suggested generator design for 1500 rpm, rather than 1900 rpm was increasing winding resistance a lot.

Also, standard r.m.s. winding voltage for 3 phase bridge is 0.74 x mean DC output required + diode voltage drop e.g. [52 x 0.74] + 2 = 40.5 V.

As for design for wrong speed, design for 55 VAC r.m.s. winding nearly doubles winding resistance and losses.

I also think that bringing 3 wires out of generator instead of 12 and using 6 diodes instead of 6 bridges may get less manufacture time/complication as well as lower component cost.

67model

Register to Reply
Power-User

Join Date: Jan 2007
Location: UK S.Northants
Posts: 485
Good Answers: 19
#12

Re: Planning Low Fuel Consumption DC Diesel Generator

10/31/2011 12:33 PM

what's the application? there are references both to a DC load and 50 / 60 Hz. If you want to generate DC, you should be able to use switched FETs instead of diodes and make it more efficient. You will have to do something clever to achieve that but if you have a brushless alternator something like that is happening already and perhaps you are rectifying a switched output and regulating that instead of using switching techniques directly.

Register to Reply
Active Contributor

Join Date: Apr 2010
Posts: 12
#13
In reply to #12

Re: Planning Low Fuel Consumption DC Diesel Generator

10/31/2011 12:42 PM

application for telecommunication equipment

output voltage from the brushless alternator already 42VAC

i use direct rectifier, use full bridge diode.

Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

67model (5); Andy Germany (4); dvmdsc (1); HUX (1); lyn (1); saut syafrudin (4); Tobugrynbak (1)

Previous in Forum: Project   Next in Forum: Extending a 24 Conductor Camera Module Ribbon

Advertisement