Fuse Rate

11/24/2011 4:31 AM

If a 3 phase induction motor takes a current of 123A rms ( Imax= 123*1.414=174A) , What should be the fuse rating that has to be used?

How can i calculate it?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Fuse rate

11/24/2011 4:41 AM

One uses British Standard 7671 with full knowledge of the cable size, type and run. The fuses are there to protect the cable, not the motor; it is the overload device's job to protect the motor.

If in doubt, consult a qualified electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Fuse rate

11/24/2011 5:26 AM

Fuse works on the principle of heating & melting. Thus, only the RMS current matters. I don't undertanf why you have calculated the peak current for fuse selection.

Register to Reply
Commentator

Join Date: Aug 2011
Posts: 93
#3

Re: Fuse rate

11/24/2011 5:46 AM

Thank you that s what i need to know.

I have another doubt in time delay fuses. Just as i have mentioned above for a current rating of 123A rms, should i give my fuse rating as 135% of the nominal value( 123A ) ie. 166A. Or should i give the fuse rating the same of 123A, since time delay fuses will have a definite time delay for any overloads.If i give time delay fuse of rating 166A, it not only exceeds the nominal value upto 166A, but also continues until the time delay of 166A is over.Please correct me if i m wrong.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Fuse rate

11/24/2011 5:50 AM

British Standard 7671 - again. WTF does the wiring look like <sigh>?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #3

Re: Fuse rate

11/24/2011 10:56 AM

Although it is remotely possible to find just the right size fuse to provide proper motor protection on small motors, it is a really bad idea and nearly impossible at the sizes you are dealing with here. Using fuses only provides no protection against single phasing and is a good way to lose a motor.

Read PWSlacks post(s) again. Even if you don't want to acknowledge the British Stds, the principle behind them is the same all over. Thermal overload relays protect the motor, fuses are for short circuit protection. Size the cables to feed the motor, size the fuses to protect the cable against short circuits as per YOUR local installation standards. You appear to be over thinking this.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#10
In reply to #3

Re: Fuse rate

11/24/2011 2:45 PM

Oh come on. Have you never heard of standard component sizing. Good luck finding a 166A fuse. I want you to have a better understanding what happens when a single 100 ampere fuse blows.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#11
In reply to #10

Re: Fuse rate

11/24/2011 4:03 PM

Not half as impressive as the guy previously asking CR4 how to make his own high voltage transformer fuses to save money.

__________________
jack of all trades
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#12
In reply to #11

Re: Fuse rate

11/24/2011 4:29 PM

Missed that one, thank goodness.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#13
In reply to #12

Re: Fuse rate

11/24/2011 9:22 PM

It was a good one

__________________
The reports of my death are greatly exaggerated.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: Fuse rate

11/24/2011 8:21 AM

Consider the starting current(starting method used)and its duration for which the fuse should not blow.

__________________
pnaban
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #5

Re: Fuse rate

11/24/2011 11:24 AM

It's all in BS7671....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#8

Re: Fuse rate

11/24/2011 11:49 AM

Oh, knock it off. There are regional standards for wiring that proscribe the fuse size for the power distribution cables used. A three phase power distribution capable of providing more than 100 amperes continuously at any power distribution voltage is nowhere for an amateur to work, let alone to design.

This is a fabricated homework problem. Has anyone here seen any motor current specified by a manufacturer to three significant figures in such a convenient sequence? I'm waiting to hear that the measured current is actually 123.456 amperes RMS. Then the question will be will the motor overheat? There's also no useful conditionals to the sparse but overly precise information we've been given. Is this current the starting current rating, the locked rotor current rating, continuous current rating, overload current capacity or the running current rating? Similarly we have no idea what is the starting circuitry for this motor; amortisseur windings, starter circutry poles with a centrifugal switch, prime mover?

Then there's the quench problem that this mythical fuse will have to contend with, as the back EMF from this multiple decades of horsepower motor tries to maintain a current draw while the fuse explodes open. Frankly I'm not comfortable of a three phase motor being protected solely by three independant fuses.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#9

Re: Fuse Rate

11/24/2011 2:03 PM

If this isn't a homework question (which it looks like it is), you shouldn't be using fuses for this application due to the valid points mentioned above. What do your local standards say?

If this is what your homework question looks like then that helps to explain the lousy state of knowledge that some graduated engineers I have noticed seem to have when they are taught misleading or illegal electrical practices that they then try and replicate in the industry by not following mandatory electrical safety codes and practices.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#14
In reply to #9

Re: Fuse Rate

11/24/2011 10:29 PM

Before MCB/MCCB were introduced motors/cables were protected by fuses of different types depending on the load characteristics. What we need is some technical literature from reputed fuse manufacturers and more details of the load.

__________________
pnaban
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#15

Re: Fuse Rate

11/25/2011 5:29 AM

Read your local electrical code.

(IIRC, the U.S. NEC allows fuses to be the next standard size up from 1.75 x FLC, and circuit breakers the next standard size up from 2.25 (2.5?) x FLC.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Aug 2011
Posts: 93
#16

Re: Fuse Rate

11/28/2011 9:08 AM

According to fusology i have seen that voltage rating of the fuse should be greater than or equal the circuit voltage. My question is to how much extent does the voltage rating of the fuse can be used?

For eg: i need to use a 4A fuse for a circuit of 24Vdc, i have seen fuses of 4A above 24V such as 32V, 125V, 250V, 600V, 1000V etc. My question is upto how much extent should i take the voltage rating of the fuse? Since this is for electronic circuit application what type of fuse should i use( material), can anyone suggest me?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#20
In reply to #16

Re: Fuse Rate

12/08/2011 12:26 PM

So long as the voltage rating of the fuse exceeds the maximum voltage in the circuit, it is acceptable.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Aug 2011
Posts: 93
#17

Re: Fuse Rate

11/28/2011 9:59 AM

Can ac fuses be applied in dc circuits. What is exactly the difference between ac and dc fuses?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#19
In reply to #17

Re: Fuse Rate

12/08/2011 12:25 PM

None.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#18

Re: Fuse Rate

11/28/2011 11:32 PM

If you are in NEC world, use NEC table 430.52. Per this table, the non-time delay fuse is 300% of motor full load current, the time-delay fuse is 175% of motor full load current for squirrel case motors (other than Design B energy-efficient motor).

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)