Maximum Demand in a Single feeder at 11kV feeder

12/01/2011 2:43 AM

Hai,

I want to design a substation of 11kv/433V with maximum demand 4500kVA. But the MRS from which I want to take 11kV incomer feeder having only one spare feeder of 1250A VCB Panel. So my doubt is whether a single feeder is sufficient to meet my Maximum Demand as 4500kVA. The Client is under Central Electricity Authority and not comes under local electrical inspectorate, and the location is Kerala. In Kerala, Kerala state Electricity regulatory commissions (KSERC) rule for KSEB is the maximum contract demand for a new single connection is limited to 3000kVA. So my doubt is that whether in any IS standard specifying any maximum demand for a single feeder at 11kV voltage.

Kindly help me....

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor
Egypt - Member - New Member Engineering Fields - Power Engineering - Pain and Joy

Join Date: Jan 2010
Posts: 19
Good Answers: 1
#1

Re: Maximum Demand in a Single feeder at 11kV feeder

12/01/2011 2:52 AM

it appears that the current for 4500KVA at 11KV will be around 400 to 500 A if the feeder can tolerate 1250A , so it should be O.K to use it for 500A

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Maximum Demand in a Single feeder at 11kV feeder

12/01/2011 3:19 AM

From this, and the other question about trench requirements, it seems that Kerala needs to update its electrical standards. Maybe more emphasis on technical issues, and less on restricting larger facilities. [??]

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: Maximum Demand in a Single feeder at 11kV feeder

12/01/2011 3:29 AM

I second your opinion! Kerala Electrical Inspectorate Authorities are unreasonable in thier demands. They need to update themselves.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #3

Re: Maximum Demand in a Single feeder at 11kV feeder

12/01/2011 3:32 AM

Interesting...I was sort of guessing, but I thought the clues were pretty good.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Maximum Demand in a Single feeder at 11kV feeder

12/01/2011 3:29 AM

Did KSERC give a technical resaon for such restriction on MD?

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Maximum Demand in a Single feeder at 11kV feeder

12/01/2011 11:26 AM

Your loading would be 236A at max loading of 4.5MVA. So the 1200A breaker is well on top of the job. The only thing I would be concerned about is the reliance on one feeder.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: Sep 2011
Posts: 5
#7

Re: Maximum Demand in a Single feeder at 11kV feeder

12/01/2011 11:56 PM

Hi,

Here 11KV side don't have any problem to supply 4.5MVA demand. But, 433V side may have problem considering the FLA and Short circuit current. FLA around 6000A and short circuit amp approx.86kA (considering 7% impedence). 4.5MVA transformer with 433V secondary and 7200A, 433V LV side breaker (100KA rating) are not readily availble in the market. This may be reason for the restriction.

Thanks,

Mari.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#8
In reply to #7

Re: Maximum Demand in a Single feeder at 11kV feeder

12/02/2011 4:12 AM

Dear Mari,

This is the exact reason why there is restirction of Maximum Demand in a particular voltage level.The same is applicable also in respect of the transformer capacity of Utility company from where H.T. power supply is providing.

Thanks,

Manindra

__________________
Manindra
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (2); manindra (1); Mariappan (1); mona sayed (1); TonyS (1); Tornado (2)

Previous in Forum: Use of Breakers   Next in Forum: Electrosctatic Phenomena

Advertisement