Anonymous Poster #1

Electrosctatic Phenomena

12/01/2011 4:18 AM

In our plant (pharmaceutical industry) we have 2 machines (same machines ).

The compressed machine one is installed in the room one and the compressed machine 2 is installed in the room 2.

We produce the same product on both machines.

On the compressed machine 2 we have electrostatic phenomena (on all metallic parts); on the machine, on the table, on the room door, etc. This phenomena is noticed only when the machine is stopped.

Please help!

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: electrosctatic phenomena

12/01/2011 4:20 AM

Please describe the phenomena.

Please describe the machines.

Please detail the material flowing through the machines.

Please describe the earthing arrangments for these machines and why they differ.

Please help the forum to provide the requested help.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: electrosctatic phenomena

12/01/2011 5:56 AM

Please ground/earth all exposed conductive parts. (Just a decent earth connection to the main frame will probably do the job).

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#3

Re: electrosctatic phenomena

12/01/2011 6:57 AM

If everything else is identical, it could be as simple as the humidity level. With room #2 being much dryer than room #1.

I have no idea why having the machine stopped would make any difference.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: electrosctatic phenomena

12/01/2011 8:03 AM

Don't stop machine 2.

Check the flooring. Check all the grounds (not coffee). Control the humidity.

You're there, we're not. Find out what's different about the two installations.

Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#5

Re: electrosctatic phenomena

12/01/2011 8:12 AM

The door? The table?

Another thing to look at is the possibility of the personnel themselves somehow picking up a static charge before entering the room. See what happens if you ground the humans before they enter the room.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#6
In reply to #5

Re: electrosctatic phenomena

12/01/2011 8:22 AM

Good thinking.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Anonymous Poster #1
#7

Re: electrosctatic phenomena

12/01/2011 8:47 AM

This phenomena occurs only when the machine is stopped .and all metallic parts in the room are charged .

It is à compressed machine ( convert the powder on compressed tablet )

We know that the powder is electrically charged ;but why the phenomena occurs only for one machine

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#9
In reply to #7

Re: electrosctatic phenomena

12/01/2011 9:38 AM

I would check for a voltage reading with a multimeter from metal surfaces to grnd and any common or bonded circuits..If you get line voltage reading then, sounds like you have a partial short....Check continuity to ground, isolate section by section...Could be in switch...If you get only static voltage, then would agree with grounding workers entering room...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Member

Join Date: Jan 2007
Posts: 8
#11
In reply to #9

Re: electrosctatic phenomena

12/01/2011 10:09 AM

The room door is also charged

The stainless table (isolate from machine ) in the corner is also charged

All metallic parts in the area are charged

Thanks

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#13
In reply to #11

Re: electrosctatic phenomena

12/01/2011 10:33 AM

It's possible that the floor coatings are different.ie; 1 painted, 1 tile..

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#12
In reply to #9

Re: electrosctatic phenomena

12/01/2011 10:27 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Anonymous Poster #1
#8

Re: electrosctatic phenomena

12/01/2011 8:53 AM

We start by inspecting the both installation ,the ground ;the phases ,amperes, voltage .everything is the same and normal .

Thank you

Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#10
In reply to #8

Re: electrosctatic phenomena

12/01/2011 9:55 AM

"We start by inspecting the both installation ,the ground ;the phases ,amperes, voltage .everything is the same and normal ."

No everything is not the same. You have simply not discovered the disparity.

Is the shut-down switch on one machine perhaps disconnecting a neutral?

__________________
Semper Ubi Sub Ubi
Reply Score 1 for Good Answer
3
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#14
In reply to #8

Re: electrosctatic phenomena

12/01/2011 11:39 AM

Be very careful when you inspect the grounding of the machine. There may be a connection to the ground bus, cable, or connector of the electrical supply to that machine, but that ground may not be reliably bonded to the complete facility electrical system's ground. You may think it is grounded, when in actuality it is floating. It could then develop an electrostatic charge from the movement of the powdered product that has been flowing through it, that is not drained off to ground. Remember that moving fluids (included powders) can build up large static charges. This is dangerous if the powder can be ignited due to a static discharge, causing an explosion (as sometimes happens in grain elevators, coal mills, etc.).

__________________
To get the right answers, first you need to ask the right questions.
Reply Good Answer (Score 3)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#16
In reply to #14

Re: electrosctatic phenomena

12/01/2011 1:35 PM

" but that ground may not be reliably bonded to the complete facility electrical system's ground."

This, to me, sounds like a very plausible explanation...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#18
In reply to #8

Re: electrosctatic phenomena

12/01/2011 10:42 PM

As has been suggested earlier the room with the electrostatic problem may have a drier atmosphere, not allowing the static buildup to self discharge safely.

One thing which may help is to install an air ioniser in the room with the static problem. This approach is used in electronics manufacturing in addition to static dissipative surfaces to bleed any static build up to ground so that static sensitive devices are not damaged.

As has also been mentioned, something about your process is generating the static in the first place. if you can identify that, and you should be able to do so, you have an opportunity to largely quench the static at the source.

Reply
Member

Join Date: Jan 2007
Posts: 8
#23
In reply to #18

Re: electrosctatic phenomena

12/02/2011 4:20 AM

The humidity value for both area is 30%(mor or less 5%)

Thanks

Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#15

Re: Electrosctatic Phenomena

12/01/2011 1:17 PM

Need to ask one question. Do you see an arch to your person as you almost touch the metal, or do you only get shocked when you make contact? If you are seeing an arch it is static electricity. If your getting shocked only when you touch the metal, transit voltage. Need to define which we are talking about.

As far as neutrals being disconnected, I have seen 4 pole MCR's with the grounds wired into one of the contact Poles. Thus no ground on machine when "E" stop was hit. You have to assume anything is possible until proven otherwise.

Reply
Member

Join Date: Jan 2007
Posts: 8
#21
In reply to #15

Re: Electrosctatic Phenomena

12/02/2011 4:15 AM

We shocked when make contact ,that's right .

If it is ;transit voltage the question is what about the second area ?

Thanks

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#17

Re: Electrostatic Phenomena

12/01/2011 3:02 PM

As others have said it is really hard to guess with so little information. It may not be static build up at all, it could be leakage current due to a faulty piece of equipment and insufficient earthing or earth leakage monitoring (ie- potentially lethal).

I would also suggest looking at the building earthing (which may be the culprit).

Let us know what you find please (as well as what country you are in).

__________________
jack of all trades
Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#19

Re: Electrosctatic Phenomena

12/02/2011 12:40 AM

What type of floor do you have in each room? (just guessing, site unseen)

And..."everything" is obviously not right and the two installations can't possibly be the same.(not guessing)

What is your location?

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Anonymous Poster #1
#20
In reply to #19

Re: Electrosctatic Phenomena

12/02/2011 4:03 AM

The floor ( booth area ) is GMPs approval (resin ) .We are in Morocco.

Thanks

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#22
In reply to #20

Re: Electrosctatic Phenomena

12/02/2011 4:16 AM

GMP = Grand Master Poobah??

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#24
In reply to #22

Re: Electrosctatic Phenomena

12/02/2011 4:30 AM

Good guess!!!

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Member

Join Date: Jan 2007
Posts: 8
#25
In reply to #22

Re: Electrosctatic Phenomena

12/02/2011 4:37 AM

Good Manufacturing Practice

Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#26
In reply to #25

Re: Electrosctatic Phenomena

12/02/2011 5:17 AM

Yeh right!!!

You first need to determine whether you have an electrostatic or an electrical energy reticulation and management problem.

Once you know what the problems are the solutions are also spelled out in GMP.

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#27

Re: Electrosctatic Phenomena

12/02/2011 8:41 AM

If the electrical discharge is dissipated (gone) once the machine has been touched, then it is just a static buildup. If the electrical discharges is always present, not being dissipated once grounded, then your problem is excess electrical current leakage. That machine or a component of it has some defects or some deterioration in its isolation has developed? Measure safe allowable leakage current for each and compare.. Good luck!

__________________
vsar
Reply Score 1 for Good Answer
Member

Join Date: Jan 2007
Posts: 8
#28
In reply to #27

Re: Electrosctatic Phenomena

12/02/2011 9:23 AM

What about area doors ( 2 doors ) ;one for access and the second for exit ?.And what about the stainless steel table (for apparatus ) ?. The table is located around 1m from machine without contact .

Thank you

Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#30
In reply to #28

Re: Electrosctatic Phenomena

12/02/2011 10:58 AM

Is the stainless steel table grounded? Is the door frame grounded?

Are there any electrical appliances on the table or leaning against the door frame?

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#34
In reply to #28

Re: Electrosctatic Phenomena

12/02/2011 2:21 PM

You may have two problems, one is a high leakage current in your machine which probably is due to a poorly grounding system, and also the build up of static electricity. Provide a redundant fixed grounding system directly tied or bonded to your power source and The cheapest most economical way to resolve the static issues is to control the humidity level in that equipment room.

__________________
vsar
Reply
Member

Join Date: Jan 2007
Posts: 8
#29
In reply to #27

Re: Electrosctatic Phenomena

12/02/2011 9:26 AM

Once the machine ( or table or doors etc )has been touched the discharge disipate immediatly .

Thank you

Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#31
In reply to #29

Re: Electrosctatic Phenomena

12/02/2011 11:25 AM

Are you & Anonymous Poster #1 the same person? If so why hide behind the anonymous Poster???

Reply
Member

Join Date: Jan 2007
Posts: 8
#35
In reply to #31

Re: Electrosctatic Phenomena

12/03/2011 4:59 PM

Yes ,the same . According to my first experience with the system ( it's my first question in this good team ) ;and it's a gaffe !

Thanks

Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#32
In reply to #29

Re: Electrosctatic Phenomena

12/02/2011 11:57 AM

Install "electrostatic flooring" (ie conductive tiling system) bond the whole lot and make sure the grounding system is correctly designed, implemented and integrated into your facility.

Audit, and ameliorate as required, all legacy electrical and grounding systems.

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#33

Re: Electrosctatic Phenomena

12/02/2011 12:37 PM

First off I would not say the machines are the same. They may do the same work and produce the same results but I would ASSUME that the power to them is fed by different circuits.

Go to the panel that feeds each machine. Inspect the circuit that is feeding the machine that is not "shocking" and then compare that feed to the machine that is. Be sure the ground to the panel and machine are tight and secure. Using an OHM meter simply check the continuity of the earth ground (be sure to power down before opening and checking panels) and do the same with the neutral to ground to be sure it is not picking up "noise" and releasing it at the machine.

Once you have inspected the feed do the same with the machine. OHM the groud to be sure the machine to feed is actualy good. Who knows it may all look good but it may be a break in the ground wire in the insulation.

Start with the basics and check off the list.

__________________
To be or not to be........ok that's a trick question.
Reply
Reply to Forum Thread 35 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); Doorman (1); fixitorelse (2); jack of all trades (1); JohnDG (2); kramarat (2); lyn (1); PeterT (1); PWSlack (1); SolarEagle (5); Stedou73ish (1); targati (7); vsar (2); Wal (5); WAWAUS (1)