8 comments
Rate Comments: Nested
Anonymous Poster #1

MV HRC FUSE CALCULATION

12/01/2011 11:36 AM

Dear friends

How can i calculate MV HRC Fuse rating for MV Transformer protection. i want to use that fuse in TR primary side.

TR capacity:1000KVA (11/0.4KV)

Voltage:11KV

percentage of impedance:6%

Pls help

Raju

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: MV HRC FUSE CALCULATION

12/01/2011 11:39 AM

Wouldn't it rather depend upon the cable installation?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #2
#2

Re: MV HRC FUSE CALCULATION

12/01/2011 11:42 AM

80A

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: MV HRC FUSE CALCULATION

12/01/2011 11:44 AM

Why?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Participant

Join Date: Dec 2011
Posts: 1
#5
In reply to #2

Re: MV HRC FUSE CALCULATION

12/01/2011 11:51 AM

pls give calculation.

full load current=1000/(1.73*11)=52A

Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: MV HRC FUSE CALCULATION

12/01/2011 11:49 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6

Re: MV HRC FUSE CALCULATION

12/01/2011 12:19 PM

If you cannot calculate this with the information you have, then there are two possibilities.

  1. You do not have enough information to do this calculation.
  2. You are not qualified to do this calculation.

Since you do not demonstrate any comprehension of the terms used, I'll let you guess which reason I think is your problem.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
2
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#7

Re: MV HRC FUSE CALCULATION

12/01/2011 3:41 PM

If the fusing is immediately at the transformer primary (transformer protection only), then the defining parameter is the thermal and mechanical damage curve per IEEE C57.12.00. For this size transformer it falls in Category II. The fuse should be chosen so that the maximum clearing time falls below the damage curve for the rating of the transformer if possible, based on full-load amps (FLA, which another poster calculated as 52 amps) and the % impedance.

Typical fusing for a transformer would be on the order of 150% to not more than 300% of FLA, depending on the installation, the frequency of transformer exposure to external faults, fault current levels, transformer % impedance, etc. The poster who suggested an 80 amp fuse was probably using a 150% recommendation. However, it is best to plot the transformer and fuse curves (in software or on paper) to determine the protection and coordination.

If the fuse is upstream of the primary cables, then the damage curve of the cables can be included on the plot and an attempt made to protect them as well.

__________________
To get the right answers, first you need to ask the right questions.
Reply Good Answer (Score 2)
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#8

Re: MV HRC FUSE CALCULATION

12/01/2011 7:08 PM

You can use the NEC Table 450.3(A). Per NEC Table 450.3(A), the primary fuse rating is not more than 300% of primary rated current (for 600V and over) and the secondary fuse rating is not more than 125% of secondary rated current (for 600V and less). However, do the device coordination for the proper selection of the fuse or get it suggested by the transformer manufacturer.

This link also helps:

https://www.littelfuse.com/data/en/White_Papers/Littelfuse-Protection-Relay-Transformer-Protection.pdf

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 2)
Reply to Forum Thread 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); chowdhury.rajudxb (1); msamad (1); PeterT (1); PWSlack (2); redfred (1); SolarEagle (1)

Previous in Forum: Free Learning PLCs Languages   Next in Forum: NPN, PNP or Namur Configuration

Advertisement