Cable Ampacity Calculator

12/06/2011 3:09 PM

I discovered the calculator at this site below. I am interested in the ampacity of 70MM conductor. A table I have lists 70mm at 220 amps. Using the calculator it produced an answer of 3.52e+3. I get 70 or 3400 depending on how I enter it into my calculator neither of which is correct.

http://circuitcalculator.com/wordpress/category/calculators/electrical-engineering/

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#1

Re: Cable Ampacity Calculator

12/06/2011 3:21 PM

Wareagle,

Could be the due to the calculator being based on some standard and having a "Correction" build in to meet the applicable standard for that country.

The table we use in Australia (AS\NZ 3008) has conditions built in based on the installation so 70mm may support 220A in air, but be derated if installed in conduit.

Likewise volatge drop over a long run may require a step up in size to supply the voltage at the load end or next DB.

So the raw calcs may say 68mm, but 70 is required.

Could also be that the calc is literal and the "numbers" say 68mm, but the next commercially available cable size is 70mm.

Just my thoughts,

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Cable Ampacity Calculator

12/06/2011 4:05 PM

This is a perfect example why I cringe every time we get a novice asking how to calculate the amperage of a cable. Any current capacity formula can only be true for only a specific collection of often unspecified conditions. (At least their unspecified by the one asking the question.) One of the unspecified conditions will be the acceptable temperature range of the insulation on the cable. NEC Article 310 states that 6 AWG TW single-insulated wire is rated for up to 80 amperes but 6 AWG THHN cable is rated for up to 105 amperes. Both cables are copper conductors. Both ratings will be de-rated if the ambient temperature typically exceeds 86°F.

Then there are the large variety of atypical scenarios that breaks any and all standards that then require a real understanding of the physics involved. The continuous amperage capacity of a copper wire in a vacuum must be seriously de-rated unless it is connected to a cryogenic cooled superconducting magnet.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Cable Ampacity Calculator

12/06/2011 4:13 PM

My interest is what is this answer of 3.52e+3. I have never seen ampacity in the form.

Sapper, My chart had the same ampacity as you are showing. I was trying to make the calculator answer equal the same but could not.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4
In reply to #3

Re: Cable Ampacity Calculator

12/06/2011 4:22 PM

This is an echo of the old Fortran format for scientific numbers. In this case "e" is not Euler's number but signifies the power of ten exponent. So 3.52e+3 is actually 3,520.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#5
In reply to #3

Re: Cable Ampacity Calculator

12/06/2011 4:51 PM

Wareagle,

That's what I figured...was only trying to identify the why of the disparity.

Apparently we're on parrallel tracks, but my focus of the explanation was not what you were after.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6

Re: Cable Ampacity Calculator

12/06/2011 5:08 PM

Consider the source. The disparity is based upon using a MIL-STD that is not appropriate for most of our earthbound work. Clicking on the link from the calculator yields the following:

Reference information for the Wire Parameter Calculator at

http://circuitcalculator.com/wordpress/2007/09/20/wire-parameter-calculator/

Wire And Cable Derating Criteria From MIL-STD-975

Wire Size (AWG)

Derated Current (Amperes)

Single Wire

Bundled Wire or Cable

30 1.3 0.7
28 1.8 1.0
26 2.5 1.4
24 3.3 2.0
22 4.5 2.5
20 6.5 3.7
18 9.2 5.0
16 13.0 6.5
14 19.0 8.5
12 25.0 11.5
10 33.0 16.5
8 44.0 23.0
6 60.0 30.0
4 81.0 40.0
2 108.0 50.0
0 147.0 75.0
00 169.0 87.5

Notes:

1. Derated current ratings are based on an ambient temperature of 70°C or less in a hard vacuum of 1E-6 torr.

2. The derated current ratings are for 200°C rated wire, such as Teflon Ô insulated (Type PTFE) wire, in a hard vacuum of 1E-6 torr.

a. For 150°C wire, use 80% of value shown in Table 16.

b. For 135°C wire, use 70% of value shown in Table 16.

c. For 105°C wire, use 50% of value shown in Table 16.

3. The current rating for bundles or cables are based on bundles of 15 or more wires. For smaller bundles, the allowable current shall be determined by IBW = ISW x (29-N)/28 where N = number of wires, IBW = current, bundled wire and ISW = current, single wire.

Digging further...

MIL-STD-975M (NASA), MILITARY STANDARD: NASA STANDARD ELECTRICAL, ELECTRONIC, AND ELECTROMECHNICAL (EEE) PARTS LIST (5 AUG 1994)., This standard is the technical baseline for standardization of EEE parts. The intent of the effort tis to focus part selection on EEE parts used in the design and construction of space flight hardware as well as mission-essential ground support equipment (GSE). The overall objective is to provide the designer with acceptable parts and specifications for procuring those parts for spaceflight missions. The result of this effort should provide the designer with EEE parts, including the necessary criteria pertaining to use, choice, and applications...

Hardly stuff that should be used by electrical engineers or electricians let alone novices.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7

Re: Cable Ampacity Calculator

12/06/2011 11:13 PM

I trust it isn't simply the difference between 70mm (a diameter) and 70mm2 (an area)?

Does the program have a way to display the formulas and logic tree being used?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#8
In reply to #7

Re: Cable Ampacity Calculator

12/07/2011 5:20 AM

Once you get to large currents you have to consider skin effect. Electrons all have the same charge, so the repel each other, and migrate to the outside of the cable. Thus most of the current flows at the perimeter and very little at the centre. This is why in high current busbar systems the centre is dispensed with. Busbars, like cables are rated based on an allowable temperature rise. Sub stations normally use hollow tube busbars. Cooling gas/fluid often flows within the tubes to further increase the current capacity. For larger currents, (typically power station generator to main step up transformer) connections use one of three formats; each phase having a tubular 'O' or toe- to- toe channel '[]' or toe-to-toe angle '<>' configuration.

Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#10
In reply to #8

Re: Cable Ampacity Calculator

12/09/2011 1:18 PM

Sorry, skin effect is a function of frequency, not current magnitude (although it does manifest its effect in varying current density)....

From Wikipedia, the free encyclopedia

Skin effect is the tendency of an alternating electric current (AC) to distribute itself within a conductor with the current density being largest near the surface of the conductor, decreasing at greater depths. The electric current flows mainly at the "skin" of the conductor, between the outer surface and a level called the skin depth. The skin effect causes the effective resistance of the conductor to increase at higher frequencies where the skin depth is smaller, thus reducing the effective cross-section of the conductor. The skin effect is due to opposing eddy currents induced by the changing magnetic field resulting from the alternating current. At 60 Hz in copper, the skin depth is about 8.5 mm. At high frequencies the skin depth becomes much smaller. Increased AC resistance due to the skin effect can be mitigated by using specially woven litz wire. Because the interior of a large conductor carries so little of the current, tubular conductors such as pipe can be used to save weight and cost.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#9

Re: Cable Ampacity Calculator

12/07/2011 4:50 PM

Thanks for your help. I spent a lot of time trying to understand why Euler's number was used in the calculation.

Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

jhhassociates (1); RAMConsult (2); redfred (2); Sapper (2); Tornado (1); wareagle (2)