What is the Maximum % Operating Load for a Particular Generator

12/14/2011 12:54 AM

Sir ,

I have a dg set capacity 500 kva, how much % load can i applied on it for it's smooth operation & what is the maximum operating time for it's over loading operation.

Gaurav

india

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#1

Re: What is the maximum % operating load for a particular generator

12/14/2011 1:55 AM

What do you mean by the rating 500kVA-is it standby,prime or continuous?.

__________________
pnaban
Register to Reply
Associate

Join Date: Jul 2011
Posts: 32
#3
In reply to #1

Re: What is the maximum % operating load for a particular generator

12/14/2011 2:24 AM

Sir,

Please help me first by standby, prime & continuous.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4
In reply to #3

Re: What is the maximum % operating load for a particular generator

12/14/2011 3:09 AM

Refer www.catelectricpowerinfo.com/ratings and www.dieselservice and supply.com/generator/faq for standard ratings. Also you should refer "generator sizing"

from Catterpillar or Cummins so that you will consider all aspects(ambient conditions,type of load etc) for proper selection. If you have big motors allowance should be made for starting current. Also fluctuating and periodical loads need care.

__________________
pnaban
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: What is the maximum % operating load for a particular generator

12/14/2011 1:56 AM

Assuming the 500 kva rating is the continuous rating, it can operate indefinitely there. Beyond that, you need to consult the manufacturer's data. It may say something like 10% overload for X period of time, followed by Y period of time at no more than full rating.

If everything is working normally, smoothest operation is likely to be at fairly high load, near or at full rating.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: What is the maximum % operating load for a particular generator

12/14/2011 3:14 AM

It should say in the User Manual supplied with the equipment.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster #1
#6

Re: What is the maximum % operating load for a particular generator

12/14/2011 6:39 AM

Gaurav,

The rating you mentioned should be Continuos rating only. In India the Dg sets are specified that way in general. Also in Indian conditions, for a smooth long term operation the DG should be operated at between 80-90 % of load.

You can overload the set for a very short time, but should be avoided as such. The results can be disastrous in high ambient conditions when you have everything stretched to maximum.

Hope it helps

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: What is the maximum % operating load for a particular generator

12/14/2011 7:25 AM

As close to the full load rating as possible.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: What is the Maximum % Operating Load for a Particular Generator

12/14/2011 10:10 AM

100%. Any more is called an "overload".

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#9
In reply to #8

Re: What is the Maximum % Operating Load for a Particular Generator

12/14/2011 9:31 PM

At what % of load the efficiency of the diesel engine is maximum?.

__________________
pnaban
Register to Reply