12kV Fusible Switch - Backfeed

12/14/2011 10:58 AM

I have a spare fusible switch in a lineup and was wondering if I could connect a generator to it and backfeed it?

I am in the NEC/CEC world.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: 12kV fusible switch - Backfeed

12/14/2011 11:09 AM

Could you be more specific? Are you talking about backfeeding into the grid? Could you provide a drawing of your proposed wiring diagram? Are you an Electrician?What type of generator is it? What are it's specifications?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Active Contributor

Join Date: Apr 2011
Posts: 15
#2

Re: 12kV fusible switch - Backfeed

12/14/2011 11:11 AM

It is an existing 12kV, 1200A 3w+g switchgear lineup. I will be racking out the Main circuit breaker to test it and was wondering if a generator could connect to the load side of one of the fusible switches.

I know LV circuit breakers must be designed for this operation...

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: 12kV fusible switch - Backfeed

12/14/2011 11:52 AM

Well from the information you've given, I don't see why not, but without a first hand inspection of the system and proposed alteration, I can't really make a recommendation...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: 12kV Fusible Switch - Backfeed

12/14/2011 11:59 AM

Isn't this the same as feeding the circuit downstream of the switch with a generator?

If so, then why install the switch at all?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5

Re: 12kV Fusible Switch - Backfeed

12/14/2011 7:49 PM

You said...

"It is an existing 12kV, 1200A 3w+g switchgear lineup."

Those numbers make no sense. A 1200 amp switch rated for 12kV is over 14 MVA. That is one honking huge switch.

I am glad you "live2learn", without sounding condescending, perhaps this one is not the one to learn on. The simple fact you are asking this question in this forum scares me.

Leave the playing on this system to someone properly trained in the care of such a system.

Perhaps I am wrong and it was a simple typo that you entered. Take it as gospel, a 12kV station is real not forgivving to "oops".

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#6
In reply to #5

Re: 12kV Fusible Switch - Backfeed

12/15/2011 2:20 PM

Actually, 1200A is a common size of manual disconnect switch at 12kV (600A and even 2000A are also found). The main issues for the OP to address are the following:

1. That the main breaker for the normal supply is racked out and locked in a position that there is no possible way that the generator and the utility could feed the loads at the same time. Without proper synchronization and protection equipment, the results could be dramatic! Also, that there are no other sources of power feeding into the switchgear.

2. That the generator is of adequate capacity to supply the load the OP wants to run.

3. That the generator electrical equipment includes the appropriate protections and controls (AVR, under/overvoltage protection, under/overfrequency protection, reverse power, reverse phase rotation, etc.) that are required for a generator of that size and application. A disconnect switch of the type he describes may have fuses, but those would not be acceptable protection.

4. That the connections be made with attention to all applicable codes and specifications for the voltage level, location & AHJ, and application.

This is not a job for your average electrician, but rather a person or firm who is qualified and experienced in working with medium-voltage equipment and applications.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Apr 2011
Posts: 15
#7
In reply to #6

Re: 12kV Fusible Switch - Backfeed

12/15/2011 5:38 PM

Thanks for the construtive reply. I knew it was common (larger) size. Just looking for a quick sanity check.

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

live2learn (2); North of 60 (1); PeterT (1); PWSlack (1); SolarEagle (2)

Previous in Forum: Substation Lightning Protection   Next in Forum: Urgent Help on Brushless DC Drive

Advertisement