plz when we have a 4-wire gen. 220/127 A, 131A 50 KVA and we conect 15 KVA 220 V single phase load between L1-L2 and another 15 KV 220 V load to L2-L3 what will be the distribution current in L1,L2,L3 and also the effect on the gen.

thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Load Unbalance Effect

12/15/2011 3:07 AM

What is the pass mark?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Member

Join Date: Jun 2009
Posts: 6
#2
In reply to #1

Re: Load Unbalance Effect

12/15/2011 7:31 AM

what do you mean?

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Load Unbalance Effect

12/15/2011 8:23 AM

The original poster put up an exam question.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Member

Join Date: Jun 2009
Posts: 6
#4
In reply to #2

Re: Load Unbalance Effect

12/15/2011 9:40 AM

Actually it"s not an exam question, really I have a generator 220/ 127 V50 KVA 131A and my load 120 lighting poles [220v,250w/pole] distributed in 1100 m line connected together by a 4*16 mm sq cable and the main supply 380/220V 4wire system ( from city net.), I have to use a gen. with A.T.S. as standby source and I have only the mentioned gen. so I need to know the current values in all lines to check if it" s suitable for the conected cable and the effect of unbalance on the the gen., proposal ATS terminal : [ L3g-N, L2g-L3,L1g-L2 ].

thanks for all

Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #4

Re: Load Unbalance Effect

12/15/2011 10:15 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Load Unbalance Effect

12/15/2011 1:21 PM

Line current is easy enough for you to calculate, neutral current is:

In=√((Ia² + Ib² + Ib²) - ((Ia X Ib) + (Ia X Ic) + (Ib X Ic)))

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#7

Re: Load Unbalance Effect

12/15/2011 2:25 PM

Quote"plz when we have a 4-wire gen. 220/127 A V, 131A 50 KVA and we conect 15 KVA 220 V single phase load between L1-L2 and another 15 KVKVA 220 V load to L2-L3 what will be the distribution current in L1,L2,L3 and also the effect on the gen."

Have you heard of vector addition?

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#8

Re: Load Unbalance Effect

12/15/2011 2:31 PM

So KH, are you the imposter Anonymous Poster #1? Why not post the question as KH?

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#9

Re: Load Unbalance Effect

12/15/2011 2:50 PM

KH Quote " Actually it"s not an exam question, really I have a generator 220/ 127 V50 KVA 131A and my load 120 lighting poles [220v,250w/pole] distributed in 1100 m line connected together by a 4*16 mm sq cable and the main supply 380/220V 4wire system ( from city net.), I have to use a gen. with A.T.S. as standby source and I have only the mentioned gen. so I need to know the current values in all lines to check if it" s suitable for the conected cable and the effect of unbalance on the the gen., proposal ATS terminal : [ L3g-N, L2g-L3,L1g-L2 ]."

Have I got this right. You are going to have 120 lts connected L-N from the main supply 220 v and you want to connect them L-L 220 V on the generator during outages. Correct?

Reply
Member

Join Date: Jun 2009
Posts: 6
#10
In reply to #9

Re: Load Unbalance Effect

12/15/2011 4:52 PM

yes correct