MCB Connections

12/19/2011 12:22 AM

Can we interchange the MCB incoming & outgoing side? What I mean to say is can we connect the incoming cable to outgoing side of the MCB & use the incoming side of the MCB to connect the outgoing cable? Is this practice acceptable?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: MCB connections

12/19/2011 12:40 AM

NO.....What's an MCB?

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Anonymous Poster #1
#2
In reply to #1

Re: MCB connections

12/19/2011 12:52 AM

Miniature Circuit Breaker.

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: MCB connections

12/19/2011 1:01 AM

Then definitely not...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #3

Re: MCB connections

12/19/2011 3:21 AM

Oh, why not? Let the child experiment.

Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#24
In reply to #2

Re: MCB connections

12/20/2011 9:59 AM

I thought MCB was Molded Case Breaker? I'm confused. (SNAFU)

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#36
In reply to #2

Re: MCB connections

12/21/2011 12:20 PM

In industrial settings, MCB means Main Circuit Breaker most of the time, although the M can mean magnetic... or miniature...

Miniature only applies at amperages less than 100A.

__________________
Think big. Drive small.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: MCB connections

12/19/2011 3:29 AM

Why would one want to do that?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#6
In reply to #5

Re: MCB connections

12/19/2011 3:51 AM

i have a MCB incomer and 6 MCB outgoing feeders. and i wanna connect them using a comb busbar. so if its acceptable to connect it like i asked, then i can connect all the MCB in one row(Row DB) without any wires.

thats why i asked whether it is acceptable.

more like this circuit

http://1.bp.blogspot.com/_Dh5hCriDIus/S2-ZelQp8EI/AAAAAAAAAWg/OPtZk1nPegc/s1600-h/Electrical+DB+Picture.JPG

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: MCB connections

12/19/2011 4:39 AM

Simply follow the installation instructions that came with the equipment provided by the distribution board manufacturer.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#8
In reply to #7

Re: MCB connections

12/19/2011 5:46 AM

We are the DB manufacturers. i just newly joined into design. my senior told me it was ok to do such connections. i was just curious about that and hence i asked you guys whether it is acceptable or not.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#10
In reply to #8

Re: MCB connections

12/19/2011 9:16 AM

Does your senior know that you don't trust his judgement?

I can hear the conversation now:

Senior: "Yes Grasshopper, it's ok to hook these gizmos up this way".

You: "Wait, wait Senior, I'll have to check with my anonymous tutors on CR4, whom I've never met and whose qualifications I am ignorant of. They'll tell me if you are correct".

Reply
Anonymous Poster #1
#33
In reply to #10

Re: MCB connections

12/21/2011 6:58 AM

Go make yourself a new door Lyn.

regards,

grasshopper

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #8

Re: MCB connections

12/19/2011 10:31 AM

Then why doesn't the organisation know already? Surely it has procedures and standards for this sort of thing? Surely it has done testing to establish those standards? Surely it has done customer feedback surveying to enhance those standards? What is the world coming to? <sigh>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#15
In reply to #6

Re: MCB connections

12/19/2011 1:13 PM

Wow...that's not crowded at all...

I just don't like those...

Anyway...follow the manufacturer's recommendations...or suffer from your insurance company's lack of compassion when they won't pay out.

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#20
In reply to #6

Re: MCB connections

12/20/2011 1:06 AM

It is because in switchboards when someone do repairs/maintenance/new connections without switching off power, when the incomer is off it is safer to work on the upper portion for connecting new cables,disconnecting old wires etc even if power is available in the downside.

__________________
pnaban
Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#22
In reply to #6

Re: MCB connections

12/20/2011 6:03 AM

Yes you can feed in through the bottom of the MCB and distribute with a comb from the top.

An MCB is none directional in operation.

Using a comb is the neatest and most reliable way to bus out the power to each branch.

Proceed with confidence.

Trust your boss

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#27
In reply to #22

Re: MCB connections

12/20/2011 10:30 AM

BUT place a big warning label on the MCCB to warn the maintenance people that this breaker is wired in reverse of what everybody expect.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#29
In reply to #27

Re: MCB connections

12/20/2011 10:40 PM

A Braille label preferably.

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#31
In reply to #29

Re: MCB connections

12/21/2011 5:34 AM

Yes, in Brail punched right on the live busbars to tell the person why he should have turned the power off first...

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9

Re: MCB connections

12/19/2011 8:37 AM

I hope it's acceptable, otherwise I've got 30+ years of switchboards I've installed to rip out!

__________________
The reports of my death are greatly exaggerated.
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#11
In reply to #9

Re: MCB connections

12/19/2011 9:18 AM

AHAA! So yer the ONE!!!!

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #9

Re: MCB connections

12/19/2011 10:32 AM

Keep it quiet. No-one will notice....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#14

Re: MCB Connections

12/19/2011 11:37 AM

Most MCBs are marked 'Line' and 'Load' at the terminals. They MUST be connected as marked, otherwise they are likely to explode and maybe kill people.

If the MCB terminals are NOT marked, then you are free to connect line and load as you wish.

These being single-break devices, it is rather more difficult to clear a short circuit when the line is connected to the bottom terminal/s.

Why this elementary question ? One young engineer who asked this question in a MNC in India was shown the door. Rather cruel, but then the company was paying top salaries and quite rightly expected an engineer to know this.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#16
In reply to #14

Re: MCB Connections

12/19/2011 1:14 PM

Come on guys, the young ones have to learn somehow and from someone.

I can't think of a better place than here to obtain unbiased, competent answers along with excellent feedback/critique to affirm, confirm, or clear up confusion when faced with uncertainy.

What happened to "No such thing as a dumb question"?

What? You mean there is such a thing? Oh no, I have erred again.

Thank you all for the excellent forum, the good humor, vast knowledge base, wealth of information, and for taking the time to share your skills, intellect, and knowledge with this hillbilly.

HAVE A GREAT HOLIDAY SEASON!!

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#18
In reply to #16

Re: MCB Connections

12/19/2011 9:47 PM

i agree that young engineers need to learn from experts. After retirement, i have spent a lot of time in training young engineers in switchgear design and peripheral fields. But this question is rather elementary in my opinion, since MCBs are clearly marked 'Line' and/or 'Load'. The question of connecting such an MCB the other way shouldn't have occurred at all. On the other hand, the IEC says that if the manufacturer does not want to restrict the connection, he must test it by feeding the power from the top as well as the bottom. So, no marking means one is free to connect it either way.

So, IMHO, the question is redundant.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#17

Re: MCB Connections

12/19/2011 2:20 PM

It is my experience that the vast majority of AC miniature circuit breakers that are available down here in the antipodes can be fed from either end without any problem. This includes Schneider, GE, MG, Hager, GE, Allen-Bradley and some other minor brands.

I have seen DC-only MCBs that are fussy about which end they are fed from, but as other posters have noted these are always marked as such.

__________________
paulusgnome
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#25
In reply to #17

Re: MCB Connections

12/20/2011 10:05 AM

Is it true that they are installed the other way up in the southern hemisphere, so as to counteract the Coriolis Effect?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#26
In reply to #25

Re: MCB Connections

12/20/2011 10:11 AM

Depends on point of manufacture. If you'r in the northern hemisphere, and you import from the southern hemisphere, the MCB is installed right side down. and vice versa if from the southern hemisphere and importing from the northern hemisphere.

Or is it the otherway around?

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#35
In reply to #25

Re: MCB Connections

12/21/2011 7:54 AM

Whether in southern or northern hemisphere gravity is downwards. Therefore top/bottom need not be changed.

__________________
pnaban
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#37
In reply to #35

Re: MCB Connections

12/22/2011 9:55 AM

Thanks for that advice. It's good to know that the information here is reliable...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Feb 2009
Posts: 176
Good Answers: 6
#19

Re: MCB Connections

12/20/2011 12:22 AM

If you are in Australia I have found that the MCB's do not specify the line & load sides on the MCB's (miniture circuit breakers) only on RCD's (residule current devices / saftey switches / earth leakage circuit breakers) .

I have seen the load & line sides in both directions on the same brand MCB's in many occasions i have not reciently seen any MCB's stateing any identification on the line & load terminals.

it is senceing current only so what differance will it make which direction of current flow is in as it is AC

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#21
In reply to #19

Re: MCB Connections

12/20/2011 1:24 AM

It is somewhat more complex than that.

The MCB is a single-break device. The fixed contact is encompassed by the arc chute, and the arc products are deionised, cooled and ejected uneventfully when the incoming power is on that side...ie, when the fixed contact is 'live' or 'hot'.

If the power feed is from the bottom, the entire moving contact, the flexible connector, the trip system...everything is live/hot after the arc is quenched. Chances of restrike/flashover are much higher than if the top was live.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#44
In reply to #21

Re: MCB Connections

12/26/2011 9:11 PM

In some switchboards the outgoing MCB/MCCBs are mounted horizontally in which case what should be the polarity(in/out,left/right)?.

__________________
pnaban
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#45
In reply to #44

Re: MCB Connections

12/26/2011 9:21 PM

If Line/Load are not marked, it doesn't matter. However, it is a good practice to keep the fixed contact side connected to the busbar.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#46
In reply to #21

Re: MCB Connections

12/29/2011 6:41 AM

But, then, how this problem is overcome in modern "NO-LINE-LOAD-BIAS" MCBs?

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#47
In reply to #46

Re: MCB Connections

12/29/2011 8:00 AM

By several small design improvements as needed....to wit :

1. Ensure no inter-phase bridging of ionised gases immediately after arc is quenched ... an example here (3 pole MCCB though)

2. When two or three MCBs are 'ganged' to make a multiphase one, the possible leakage path at the trip point (and any other vulnerable place) must also be blocked as well as possible.

There may be other small things i haven't come across.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#23

Re: MCB Connections

12/20/2011 7:59 AM

Yes. That is how many residential and small industrial circuit breaker boxes operate. The feed comes in through the screw terminal of the large circuit breaker and that feeds the bus bars which the individual distribution breakers are attached to.

That was common practice on residential installations of Federal Pacific C/B panels about 50 years ago and is still done on some installations now, although modern panels have a dedicated master breaker.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Reply
Power-User

Join Date: Sep 2011
Location: Near the New Madrid Fault. USA
Posts: 269
Good Answers: 1
#28

Re: MCB Connections

12/20/2011 11:28 AM

No.

__________________
It's not Rocket Science
Reply
Active Contributor

Join Date: Dec 2009
Location: Karachi, Pakistan
Posts: 22
#30

Re: MCB Connections

12/21/2011 12:56 AM

Yes you can do it. Technicaally there is no problem. But the good paractice is to follow the Manufacturer instruction and Incoming and out going Cables on recommended points and save the accidents may occur by third person who is maintaining the facility.

__________________
Khawaja Raisuddin, Manager Project Technical
Reply
Anonymous Poster #1
#32

Re: MCB Connections

12/21/2011 6:51 AM

So whats the final verdict. "acceptable" or "not acceptable". some gurus say it is acceptable and some say its not.

Anyway i am going with "acceptable".

Reply
Active Contributor

Join Date: Dec 2009
Location: Karachi, Pakistan
Posts: 22
#34
In reply to #32

Re: MCB Connections

12/21/2011 7:14 AM

Fine Go ahead.

__________________
Khawaja Raisuddin, Manager Project Technical
Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#38

Re: MCB Connections

12/23/2011 4:37 AM

I know what I know and I know it is ok because I've always done it that way.

Or is it?

From a functional logical view point it is ok. Even with this directional arcing idea that was posted, which I don't buy. (except for DC apparently )

I tried to find a manufacturer's recommendation and couldn't find one except for DC applications where I found words that said line in and line out mattered.

The buss comb manufacturers said it could go in either the line in or line out sides of the circuit breakers.

Clipsal had a drawing which showed a main breaker fed from the top and a busscomb across the bottom to the branch circuit breakers with load wiring on top. Direction doesn't' seem to matter for branch circuits then? It still ended up neat with all wiring on top instead of the bottom.

I couldn't find an application note to say it was OK or over wise.

Did anyone else have a sniff around the internet and find anything concrete?

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
3
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#39
In reply to #38

Re: MCB Connections

12/23/2011 6:55 AM

This is from the catalogue of a rather popular MCCB.

The performance of single-break circuit breakers is known to be different when the feed is from the bottom. This is the reason that IEC 60947-2 specifies that one additional SC test be carried out with connections required when the terminals are not specifically marked 'Line' and/or 'Load'

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Good Answer (Score 3)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#40
In reply to #39

Re: MCB Connections

12/23/2011 12:09 PM

Pardon the typo....

.....carried out with connections required reversed when the terminals......

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#41
In reply to #39

Re: MCB Connections

12/26/2011 2:58 AM

GA Sridhar with supportive data

__________________
Subramanyam
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#42
In reply to #41

Re: MCB Connections

12/26/2011 3:53 AM

Thank you.

Though the line/load polarisation is gradually disappearing, it exists in a small percentage of devices. Unfortunately, this aspect is not generally known, and manufacturers naturally underplay it. It may be good to publicise it a little i thought.....

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
United Kingdom - Member - New Member Hobbies - Musician - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member Hobbies - Fishing - New Member

Join Date: Mar 2007
Location: South-east corner of Spain 50 48 49.24N 2 28 27.70W
Posts: 1508
Good Answers: 31
#43

Re: MCB Connections

12/26/2011 5:31 PM

Another thing to remember when working on circuits is to test them to make sure they are dead and without a charge before you work on them, even after you have tripped the breaker! Only takes some idiot to connect up wrong a junction box and you could have a circuit getting fed by two breakers!

__________________
“It's kind of fun to do the impossible.” Walt Disney
Reply
Reply to Forum Thread 47 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (5); brettj1au (1); cuba_pete (1); electricalexpert65 (1); K_Fry (1); Khawaja Raisuddin (2); kvsridhar (8); kvsubramanyam (1); lyn (2); marcot (2); Mr. Truman Brain (1); old salt (1); Paulusgnome (1); pnaban (3); PWSlack (6); Ried (2); Rockyscience (1); SHOCKISCAN (1); SolarEagle (3); TonyS (1); Wal (3)

Previous in Forum: Arc Rated Clothing   Next in Forum: DSP

Advertisement