Method of Lightning Protection of Movable Machines on Port

12/19/2011 3:21 AM

Hi,

Can you suggest method of lightning protection for rail mounted movable machines on Port viz ship unloaders and ship loaders. How to calculate tolerable Step and Touch potentials since these equipments are mounted on a Jetty.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Method of Lightning Protection of Movable Machines on Port.

12/19/2011 3:28 AM

<...suggest method of lightning protection for rail mounted movable machines on Port viz ship unloaders and ship loaders...>

They are the lightning conductors in themselves, though one method of providing some protection is to put a taller earthed structure in the vicinity, and hope that the lightning strikes that object preferentially.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Method of Lightning Protection of Movable Machines on Port.

12/19/2011 3:40 AM

Pray to Saint Elmo.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
3
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#3

Re: Method of Lightning Protection of Movable Machines on Port.

12/19/2011 5:32 AM

Fom the Australian standard on lightning protection.

Section 6.9.5 says:

"Cranes and other tall lifting appliances used for building construction purposes, shipyards and port installations also require bonding to earth. For cranes or revolving structures mounted on rails, efficient earthing of the rails, preferably at more than one point, will usually provide adequate lightning protection. In special cases, where concern is felt regarding possible damage by lightning to bearings, additional measures may be justified."

What these additional measure are it fails to specify. I would imagine some sort of brushing arrangement would provide adequate parallel shunting.

Found a possible solution here Grounding brush specially made for crane carriage

Read and follow the recommendations in the Oz standard or your own local standards to address all your other sight grounding concerns.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Good Answer (Score 3)
Power-User

Join Date: Mar 2011
Location: Sydney . Australia
Posts: 418
Good Answers: 35
#6
In reply to #3

Re: Method of Lightning Protection of Movable Machines on Port.

12/20/2011 12:31 AM

good post above . are those grounding brushes rated for lightning or for low voltage and static earthing purposes ?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: Method of Lightning Protection of Movable Machines on Port.

12/20/2011 4:01 AM

Their purpose is to brush the %$£& off the rails, so that there is better wheel-to-rail contact, which is where the earthing takes place.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8
In reply to #7

Re: Method of Lightning Protection of Movable Machines on Port.

12/20/2011 5:19 AM

That rail brush manufacturer seems to be addressing a real world need and do describe the use thus:

For ordinary crane rail surface sweeping and grounding discharging

The wheels will still play a big part for sure.

That rail really needs to be properly grounded per standards and accepted practices for this to work properly.

The other lightning risks also need to be addressed in the normal manner (see the link to the Oz standard) to achieve safety and protection in addition to the preferential energy shunting path that the rail provides.

One flash and you're ash

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User

Join Date: Mar 2011
Location: Sydney . Australia
Posts: 418
Good Answers: 35
#9
In reply to #7

Re: Method of Lightning Protection of Movable Machines on Port.

12/20/2011 6:57 AM

i think we need to validate the difference between carbon or copper brushes used to transfer current between two moving surfaces and brushes used to clean the rails

notice some of the brushes on that page have great big braided copper earth straps bolted to them for grounding

the felt ones are grease applicators

and others are purely for cleaning , not grounding

if you earth a lightning strike through the wheels you will blow the bearings to bits , admittedly the mass on the wheels will guarantee a good contact from wheel to rail but how are you proposing to make earth contact with the wheel ?

are you suggesting making the bearings sacrificial ?

take a lightning strike through the wheels and you have a grease fire that can spread and destroy your crane.

Register to Reply
Commentator

Join Date: Jun 2009
Posts: 80
#4

Re: Method of Lightning Protection of Movable Machines on Port

12/19/2011 2:20 PM

To calculate geometry try the Rolling Sphere method.

Register to Reply
Power-User

Join Date: Mar 2011
Location: Sydney . Australia
Posts: 418
Good Answers: 35
#5

Re: Method of Lightning Protection of Movable Machines on Port

12/20/2011 12:08 AM

you have to use a spring mounted brush to scrape and clean the rail track and use a copper contactor or brush rated for the current running along the track , make sure there is no breaks in the track where earthed connection is not made . If its on a Jetty then the earth cable from the track has to run back to shore.

do they have slew bearings ? , if so then slip rings mounted in the center of the slew would be required like those used on wind turbines .

anywhere that has rollers needs protection for the bearings.

you would also look at isolating electronic control cabinets with rubberised mounts , and perhaps putting surge protection on the mains power cables , and on any low voltage sensor cabling such as winch position sensors or loadscale sensors.

what about the operators seat , controls and cabin ?

surge protectors are also available for two way radio antennas which they would have in the operators cabin.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Jan 2012
Posts: 1
#10

Re: Method of Lightning Protection of Movable Machines on Port

01/08/2012 5:44 AM

you have to use a spring mounted brush to scrape and clean the rail track and use a copper contactor or brush rated for the current running along the track , make sure there is no breaks in the track where earthed connection is not made . If its on a Jetty then the earth cable from the track has to run back to shore. that will do for lightning protection.

Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

corlickmark (1); Nah (1); Nothing is Impossible (3); PWSlack (2); Tornado (1); Wal (2)