what is the differance between
per unit fault calculation or fault calculation?
Re: per unit fault calculation
12/19/2011 5:05 AM
At first glance, the words "per unit".
India - Member - New Member
Good Answers: 164
12/19/2011 6:40 AM
Try here
Re: Per Unit Fault Calculation
12/19/2011 1:00 PM
One's expressed in PU units (a unit-less expression related to the system), the other in units such as amps, volts and VA.
12/19/2011 5:11 PM
The per unit method is a way to make fault calculations.
Good Answers: 444
12/19/2011 9:55 PM
The difference is the amount of time it takes to get the answer. It is easier to calculate the current through a reactance as 1/.05 and see that the current is 20 times the base current; rather than work with the actual phase to phase voltage, convert it to line to ground, divide that by the actual reactance in ohms to get a value in Amps, and then figure out how much greater than normal the current is. It is also how properly trained Power Engineers can spot wannabes during an interview.