Anonymous Poster #1

Causes of Tripping?

12/25/2011 5:01 AM

Two 132Kv feeder from Substation - A & Substation - B was feeding to substation C by underground system. one of the feeder (A to C) got damaged by external source. due to this damage feeder (B to C) got tripped and Substation C become blockout for 1 hrs.

What is causes of tripping in feeder B to C? how to avoid this in future?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Causes of Tripping?

12/25/2011 5:17 AM
__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Causes of Tripping?

12/25/2011 9:32 AM

Tripping may be caused by over loading due to damage to A to C feeder. Get that fixed.

Tripping may be caused by overindulging in alcohol, too.

Hire a competent electrician to evaluate it and fix it. If you have to ask, you can't fix it.

132kv will turn you into a crispy critter very quickly.

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3
In reply to #2

Re: Causes of Tripping?

12/25/2011 11:50 AM

One way or the other, Lyn, you're close to the root cause here. Hopefully, the actual problem is that this student has already overindulged in alcohol and is now tripping over this homework assignment given during a school break. There is also the disturbing possibility that a power utility has hired people to design their network that know nothing about power grids.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#7
In reply to #3

Re: Causes of Tripping?

12/26/2011 8:25 PM

I have to agree with both you and Lyn. And this does sound like hypothetical home work scenario I often wonder about these AP posts

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Reply
Participant

Join Date: Dec 2011
Posts: 4
#4

Re: Causes of Tripping?

12/26/2011 12:28 AM

In order to know the cause of tripping, first you must check the protection which operated, i.e earth fault relay, overcurrent, differential etc and then start from there. The damage caused by external source is not detailed and I can only assume that there may have been a damage due to excavation, in which case the earth fault relay has operated on both feeders. It would be normal for the feeder from substation A to trip as the fault was direct. The tripping of feeder from substation B is not evident but it can happen, especially if the transformer neutral is connected to earth through an impedance. The problem can be avoided but one must have the full details of the distribution network to work it out.

Reply Score 1 for Good Answer
Participant

Join Date: Dec 2011
Posts: 1
#5
In reply to #4

Re: Causes of Tripping?

12/26/2011 12:38 AM

THANX FOR UR REPLY ,

Reply
Participant

Join Date: Dec 2011
Posts: 4
#6
In reply to #5

Re: Causes of Tripping?

12/26/2011 12:53 AM

Can you confirm if the earth fault relay has operated on both feeders, and can you give details of transformers connected on both feeders.

Reply
Reply to Forum Thread 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dj95401 (1); guest6 (1); Kiscal (2); lyn (1); redfred (1); Tornado (1)

Previous in Forum: Starting of Synchronous Motor Using Cycloconverter and Converter   Next in Forum: Trouble On Variable Frequency Driver

Advertisement