Anonymous Poster #1

Elcb Tripping

12/26/2011 12:10 AM

a 3 phase 4kw Motor with no load,is connected through a MCB and a ELCB . i want to know whether MCB or ELCB trips when i remove one of the phases. the voltage is 400v ac.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: elcb tripping

12/26/2011 3:46 AM

i assume it is a 3-pole MCB, and a 4-pole ELCB. The 3-pole MCB is nothing but 3 single-pole MCBs ganged together. This is not sensitive to phase-loss. The ELCB will not sense anything except earth leakage.

So neither device will trip when you remove one of the phases, provided the motor is lightly loaded. If it is running at full load, the two healthy phases will start carrying √3 x FLA, so the MCB will trip on overload in due course.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Good Answer (Score 4)
Commentator

Join Date: Sep 2008
Location: India
Posts: 91
Good Answers: 6
#3
In reply to #1

Re: elcb tripping

12/28/2011 2:55 PM

If it is running at full load, the two healthy phases will start carrying √3 x FLA, so the MCB will trip on overload in due course.

At the time of starting if motor is fully loaded, it might not be able to produce enough starting torque and consume 5 times current which will trip MCB.

At running also if it is full loaded at single phasing condition probably motor will stall.

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4
In reply to #3

Re: elcb tripping

12/28/2011 8:46 PM

Do you mean the situation if the supply is only 2 phases at starting? If so, there will not be any rotating field at all ! The MCB will trip sensing locked rotor current.

Yes, depending on the design, a fully loaded motor may stall on single-phasing, but i have not seen this often. Mostly it continues to run, and the severe negative sequence currents can damage the rotor unless protection is proper.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5
In reply to #1

Re: elcb tripping

12/29/2011 5:23 AM

KVS! Are three pole ELCBs available in the market?

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: elcb tripping

12/29/2011 8:01 AM

Not to my knowledge, 2 and 4 pole are what i have seen.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Commentator

Join Date: Sep 2008
Location: India
Posts: 91
Good Answers: 6
#7
In reply to #5

Re: elcb tripping

12/29/2011 8:26 AM

Generally in motor circuit ELCBs are not used. Fire protection is provided through earth fault relays with trip setting around 300mA. They are of three pole type.

Digital clamp type O/L relays with inbuilt earth fault protection are wided used. Example Siemens 3RB series.

Reply
Power-User
Engineering Fields - Electrical Engineering - Ron Nombri Engineering Fields - Energy Engineering - Ron Nombri Engineering Fields - Power Engineering - Eternal Power Papua New Guinea - Member - Ron Nombri

Join Date: May 2007
Location: Papua New Guinea
Posts: 174
Good Answers: 3
#2

Re: elcb tripping

12/26/2011 7:00 AM

If you want each phase of the three phase supply to the motor to be monitored sensitively. Then you install a "Phase Failure Device". The "phase failure device" will take out all three phases if one phase is low, over voltage, or a short occurrs on it.

__________________
Kind regards, Ron
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Elcb Tripping

07/17/2023 5:18 AM

As the purpose of the <...MCB...> is to protect the wiring, of which details have been withheld from this forum, it is not possible to say.

To protect the <...Motor...>, a motor overload device is needed in addition to the <...MCB...>.

Why anyone would <...remove one of the phases...> is a mystery that remains unsolved.

The <...ELCB...> serves no real purpose if there is no risk of a human being being downstream of it.

If in doubt, consult a qualified local Electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); kvsridhar (3); Lspraba (2); PWSlack (1); Ron Nombri (1)