Static Excitation System n-1 Critrion.

12/26/2011 5:03 AM

Hi,

If the following could be explained:

"The rectifier assembly shall consist of two or more individual bridges (2x100%, 3x50%) fulfilling the n-1 criterion. The system shall supply the nominal excitation current at rated generator conditions with one bridge out of service. The thyristor bridges shall be 50% loaded."

Q1. what is n-1 criterion?

Q2. what is (2x100%, 3x50%)?

Regards,

Saurav Kafle.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: static excitation system n-1 critrion.

12/26/2011 5:13 AM

N-1 means that if you lose one, the remainder still suffice. In your two examples:
a) with two 100% bridges, loss of one still leaves the other one at 100%.
b) with three 50% bridges, loss of one still leaves 2 x 50% = 100%.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#2
In reply to #1

Re: static excitation system n-1 critrion.

12/27/2011 3:28 PM

GA, Tornado. Clear and concise.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Register to Reply 2 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

Previous in Forum: Synchronizing-Reg   Next in Forum: Battery Autonomy

Advertisement