Anonymous Poster #1

ELCB for Overcurrent & Shortcircuit Protection

12/29/2011 1:10 AM

will 32/40 Amp. ELCB installed in incommer of MCB WILL TAKE CARE FOR over current & short circuit protection , (for domestic installation we need only 9KA RATING) or we need to use MCB sepratly.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: ELCB for overcurrent & shortcircuit protection

12/29/2011 4:32 AM

Are you sure? ELCB installed in INCOMER of MCB or incomer of DB? If you already have an MCB as incomer and add this ELCB to the MCB then the combination is called ELMCB offering Overcurrent + Short Circuiot + Earth Leakage Protection. Else, if you are planning to use ONLY the ELCB as the incomer of the DB, then you will NOT have any over current or short circuit protection. Plain ELCBs do not provide any protection against over current and/or shor circuit. They provide protection against earth leakage only. ELCBs do not have a short circuit breaking capacity, The 9kA you are talking of is the breaking capacity of the MCB.It is strongly suggested to use an MCB of adequate current rating and adequate breaking capacity ahead of the ELCB in the DB.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: ELCB for overcurrent & shortcircuit protection

12/29/2011 6:51 AM

The common usage of the term ELCB does not include overcurrent and short circuit protection. However, you should check the specifics of the particular ELCB you are using, because it might integrate all of these functions. Ask the manufacturer, rather than relying on a generic answer.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: ELCB for Overcurrent & Shortcircuit Protection

12/29/2011 4:17 PM

Rather than an ELCB, choose a suitable RCBO instead.

As the original abbreviation isn't defined, neither is that in this response.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #3

Re: ELCB for Overcurrent & Shortcircuit Protection

12/30/2011 10:09 AM

RCBO's have a different acronym in the US, can anyone tell me what it is I can never remember it.

__________________
The reports of my death are greatly exaggerated.
Reply
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#5

Re: ELCB for Overcurrent & Shortcircuit Protection

12/31/2011 2:20 AM

NO

Reply Score 1 for Off Topic