Soft Start Relay

01/01/2012 1:31 PM

Hi,

I have just destroyed a soft start relay (MCST2450AS, soft start at 50 amps). It was used to limit the inrush current into a 240 volt 45 amp variac. I was thinking of replacing it with a more robust relay (MCSS2490CM, soft start/soft stop at 90 amps). I found the part number in the Crydom catalogue, however, when I type this number into the parts search it does not recognise it. Also, I am in the UK, so, does anyone know the answers to the following questions:

1. Is the Crydom soft start relay the best way to limit inrush current in a variable transformer?

2. Where can I purchase the MCSS2490CM relay (or its equivalent if it is now obsolete) in the UK?

3. Is a phase angle control relay similar to a soft start relay? If so what are the similarities, benefits if any and would this be any better at controlling inrush current?

Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Soft Start Relay

01/01/2012 2:40 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Oct 2010
Posts: 76
#12
In reply to #1

Re: Soft Start Relay

01/02/2012 9:41 AM

Thanks for the update Solareagle.

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#2

Re: Soft Start Relay

01/01/2012 3:47 PM

Why do you need a soft start system on a variac?

Typically they are intended for motor loads.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Soft Start Relay

01/01/2012 5:12 PM

Exactly.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Oct 2010
Posts: 76
#9
In reply to #2

Re: Soft Start Relay

01/02/2012 9:15 AM

When the variac is first switched on it draws in excess of 40 amps.

Register to Reply
Commentator

Join Date: Oct 2010
Posts: 76
#11
In reply to #2

Re: Soft Start Relay

01/02/2012 9:27 AM

They are used for motors, however, they are also used for transformers.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Soft Start Relay

01/01/2012 5:13 PM

Did it close onto a short circuit with inadequate protection? What is the overload trip set at? What are the fuses set at? What is the VA of the load?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Oct 2010
Posts: 76
#10
In reply to #4

Re: Soft Start Relay

01/02/2012 9:19 AM

If there is no load attached the variac still draws in excess of 40 amps for a fraction of a second (inrush current) and the current input meter displays this. The trips are 30 amp D type MCBs.

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#13
In reply to #10

Re: Soft Start Relay

01/02/2012 11:24 AM

So why are you running a 45 amp rated variac on a 30 amp breaker system?

To me thats just asking for inrush current issues.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Soft Start Relay

01/01/2012 11:31 PM

If you are trying to reduce magnetizing (inrush) current to the variac primary, a zero-crossing relay might also work. I'm not sure whether you need either of zero-crossing or soft-start, though. Maybe just a better selection of circuit breaker or fuses on the variac primary?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Sep 2011
Location: Near the New Madrid Fault. USA
Posts: 269
Good Answers: 1
#14
In reply to #5

Re: Soft Start Relay

01/03/2012 11:57 AM

You are correct...Zero crossing SSR is what is needed.

__________________
It's not Rocket Science
Register to Reply
Commentator

Join Date: Oct 2010
Posts: 76
#15
In reply to #14

Re: Soft Start Relay

01/03/2012 1:20 PM

I thought that it should be switched in at the peak of the voltage and not zero crossing. If the mains is applied when at its peak value, inrush current is at its lowest. Conversely, if the mains is applied at the zero crossing point, inrush current will be maximum. So how does a Zero crossing SSR achieve this? If i am obviously missing something, then please explain as I am not an electronics guru. Thanks,

Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#6

Re: Soft Start Relay

01/01/2012 11:33 PM

Yes why do you need a soft start relay? Are you tripping a sensitive circuit breaker due to magnetising current?

Why not fit a series surge resistor in the line then by pass it for normal operation.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#7

Re: Soft Start Relay

01/01/2012 11:44 PM

Variacs...

http://sound.westhost.com/articles/variac.htm#s1

__________________
The square root of nothing is what you make it!
Register to Reply
Power-User

Join Date: Apr 2005
Location: Scotland
Posts: 164
Good Answers: 8
#8

Re: Soft Start Relay

01/02/2012 4:01 AM

You could use one of my solid state relays. They seem to be imune from surge failure and will operate up to 80 amps at 240v. On test I had one switching power to a large pulse transformer for a Sonar transmitter continuously for over 24 hours. Last year I supplied 3phase versions to BAe and they found that the 440V, 15A, SSR was happily taking 12x it's rated current for 500mS while starting up a big fan motor. They also found that the SSR produced 30db less noise than the equivalent Crydom SSR so you don't need line EMC filters. (The SSRs are designed to operate well within the EU and FCI EMC limits).

After 9 years of development, on my own, I now have a patent and am about to go into full production.

Register to Reply
Register to Reply 15 comments

"Almost" Good Answers: