Diesel Generator Starting Time

01/03/2012 5:22 AM

hi,

Generally, emergency diesel generator is kept in electrical powerhouse as standby power source in case of failure of other source coming. What would be the ideal time that it should be started ? - will it be around 3s to 4s or around 13s to 15s - so that emergency loads could be supplied with continuous power.

Regards,

sks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Diesel generator starting time.

01/03/2012 5:23 AM

To supply vital loads during a power break, use an Uninterruptible Power Supply [UPS] between the mains and the vital load.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Diesel generator starting time.

01/03/2012 5:45 AM

It depends on how fast your crystal ball is....

(I'm getting sleepy and will try to think better tomorrow.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Diesel generator starting time.

01/03/2012 6:39 AM

The ideal time for it to start is just before the power failure. As this isn't possible to predict you have to use your judgement or as PWS suggests use a UPS to make up the shortfall.

You have the details, we don't! It's down to your judgment.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: Diesel generator starting time.

01/03/2012 6:49 AM

If you have critical systems that require constant power, PWS is correct, you need a UPS....Sized according to those critical systems on a separate distribution circuit...

http://www.apc.com/products/category.cfm?id=13

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Commentator

Join Date: Jul 2008
Posts: 56
Good Answers: 1
#5

Re: Diesel generator starting time.

01/03/2012 7:05 AM

Agreed with TonyS....the best time would be the time slot between UPS can support the load. In big systems only critical load is supplied by UPS rest of the load will be fed by Diesel Gen only. Generally, Diesel Gen should start feeding load within 6-8 sec.(what we did with our system) because even if we consider the outdoor lighting. Refinery, oil and gas stations don't want to go for blackout for long and it is practical to resume power back as soon as possible.

Register to Reply
Member

Join Date: Oct 2011
Location: India Maharashtra
Posts: 5
#6

Re: Diesel Generator Starting Time

01/03/2012 10:57 AM

If your system requires no power failure , them you want to use UPS system . UPS will give back up for some time . Diesel generator will start as time set by you . And will be restored by DG. So no power failure. NORMAL time to start is 3 sec in auto mode.

__________________
Anilborate198
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#7

Re: Diesel Generator Starting Time

01/03/2012 11:45 AM

An interruption of power can be very short or sometimes very long. Instantaneous interruption lasts only a few cycles before the utility breaker recloses. A delayed reclosure will take maybe 30 seconds depending on the utility setting. There may be more that one delayed reclosure. You need to wait until these events have completed their cycle and then have the generator pickup the load. I would check with the utility to see how long they suggest. However, depending where you are, they may not have a clue.

Register to Reply
Power-User
Hobbies - Target Shooting - New Member

Join Date: Feb 2010
Location: Florida
Posts: 259
Good Answers: 29
#8

Re: Diesel Generator Starting Time

01/03/2012 12:34 PM

Unfortunately, UPS backups can not handle heavy loads. Inductive loads can require 700% more starting current than operating. Inductive motors can be found in many types of equipment: machinery, pumps, compressors..etc. It would be necessary to know for what type of facility the emergency power is needed, because what might be considered "vital" to a hospital is different than one that houses computer equipment.

The key requirement for any emergency diesel system is first to insure that is has a sufficient rating to supply all of the loads that it will be required to power. Even with sufficient power it is necessary to shed and sequence the load in order to maintain frequency and voltage. The time the system must be able to accept full load may be controlled by government agency or an industry standard (or both). Three seconds is pretty darn quick, but not unachievable.

__________________
Si vis pacem, para bellum
Register to Reply Score 1 for Good Answer
Participant

Join Date: Jan 2012
Posts: 3
#9

Re: Diesel Generator Starting Time

01/03/2012 1:17 PM

It all depends on the nature of your load. Some loads could accept few seconds others you have to think of a split of a second, in which you may have to apply a no-break system such as in airports, highly sensitive control centers etc .

Register to Reply
Commentator

Join Date: May 2011
Posts: 84
Good Answers: 1
#10

Re: Diesel Generator Starting Time

01/03/2012 3:16 PM

it takes around 4-5 sec to crank the DG set via starter motor

After, 13-15 sec when normal voltage of DG set develops, it gets closed on dead bus.

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#13
In reply to #10

Re: Diesel Generator Starting Time

01/04/2012 12:09 AM

what is cranking actually? Is it starting the diesel generator from zero conditions?

regards,

sks

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#14
In reply to #13

Re: Diesel Generator Starting Time

01/04/2012 2:40 AM

Why are you asking these questions?

You clearly don't have a clue what you're asking about!

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Off Topic
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#11

Re: Diesel Generator Starting Time

01/03/2012 8:31 PM

Per NEC, it is not more than 10 seconds. Here is the extract from NEC Article 700.12

"Current supply shall be such that, in the event of failure of the normal supply to, or within, the building or group of buildings concerned, emergency lighting, emergency power, or both shall be available within the time required for the application but not to exceed 10 seconds".

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#12

Re: Diesel Generator Starting Time

01/03/2012 10:22 PM

I know that a substation breaker can go thru several timed openings. So when do you start counting to 10. Is it after the last opening of the breaker?

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#15

Re: Diesel Generator Starting Time

01/04/2012 3:35 AM

What do you mean by "start up time"?. Is it time delay set in starting timer or total time elapsed from the moment failure occurred to the moment of supply return from generator?.

__________________
pnaban
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#16
In reply to #15

Re: Diesel Generator Starting Time

01/04/2012 3:40 AM

well, i am unaware about the starting time set up in the timer, would be grateful if you could elaborate........i mean - time from city supply is off to the time the diesel generator supply comes to a load.

regards,

sks

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#17

Re: Diesel Generator Starting Time

01/04/2012 3:42 AM

Sounds like a project for school.. Yes? I suggest you read the DG manufacturers handbook! There are differences in every DG you can obtain.

Small 4 cylinder 75Kva DG start in several seconds whereas large V16 RR engines takes forever to start, then you have to wait for the autosync to work, then the load shedding system to kick in, then the autobreakers to close.... an eternity if you are in darkness.

Does this project include autostart? You haven't actually mentioned it! If you don't have autostart, then the time to restore power is directly proportional to the speed the Man can run to the emergency generator house to switch it on!

__________________
The square root of nothing is what you make it!
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#18
In reply to #17

Re: Diesel Generator Starting Time

01/04/2012 3:48 AM

well........i saw this in my earlier work, when the supply was essential........but they mentioned 3s to 4s for emergency supply for DG, as there was UPS as well.......which could serve supply to the ICU patients.........!!

thanks anyway.......

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#19
In reply to #18

Re: Diesel Generator Starting Time

01/04/2012 6:09 AM

ICU: Intensive Care Unit, a VERY important place in ANY hospital that and operating theatres.

Pity you had not mentioned this before!

In the UK, ICU and Cat 1 theatres have a dedicated power supply, backed up with UPS for ventilators, Heart monitors and all manner of equipment designed to keep the patient alive while undergoing surgery or recovering in ICU. That in itself is not enough to run either department for long, only while the DG is kicking in. Theatres have their own dedicated DG which will because of its size, that is, less than 250Kva.. will start and supply power within a few seconds, supplying essential/critical equipment first, then ancillary equipment second.

ICU in many cases is connected to the theatre DG, or they have a larger UPS for essential/critical equipment and for general power, they will have to wait until the main DG starts, then that only supplies services that have been designated a priority during a power cut.

As for times of starting and restoring power, you still must refer to the instruction book, or test it yourself!

However.. CAUTION. if you are in a hospital environment, and you are thinking of a test, do it when there are no operations.. as I don't think you'll get a thank you from the surgeons if suddenly they are plunged into darkness while removing someone gall bladder!

__________________
The square root of nothing is what you make it!
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#20

Re: Diesel Generator Starting Time

01/04/2012 10:17 AM

You must have ATS Panel in place -Automatic Transfer Switch? It would take 30 seconds or less to automatic start the generator and provide power back on.....

[Speaking from Experience :)]

__________________
--
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#21

Re: Diesel Generator Starting Time

01/05/2012 12:42 AM

Standby Diesel Generator (DG) sets get started automatically in case of failure of main (grid) power with the help of automatic mains failure (AMF) panel in case of sustained under voltage or no voltage. DG set may start within a period of 6 to 8 sec but its circuit breaker will be closed only when it has attained full voltage. Normally the scheme takes care of maximum three consecutive crankings through starter motors, powered by battery. If it fails to start even after three attempts, the starting process is aborted and it requires manual intervention for trouble shooting.

DG power is fed to emergency distribution board for essential loads. The emergency distribution board receives power from two sources i.e grid power and DG power through change over contactor/ circuit breaker. Capacity of DG set is selected on the basis of maximum demand of essential loads, taking into consideration the starting KVA of the largest motor with all other loads including emergency ligting being connected.

For critical loads like automation equipment, computers, life saving equipment and associated lighting where uninterrupted power is required, UPS of adequate capacity and backup time should be used. If long duration power failure is anticipated, UPS may also be fed from emergency DB.

Register to Reply Score 1 for Good Answer
Register to Reply 21 comments

"Almost" Good Answers: