MGE Galaxy 5000

01/05/2012 11:08 AM

Hi,

I have a MGE Galaxy 5000 80 KVA UPS system.

The inverter fuse has blown and I am trying to locate the fuse to change it.

Does anyone know the location of this fuse?

Thanks

Alan

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: MGE Galaxy 5000

01/05/2012 11:15 AM

The original equipment manufacturer knows so much about this fuse that all the details can be found in the operation and maintenance manual that came with the equipment. If unavailable, a replacement may be obtained by using the telephone number that is listed on the original equipment manufacturer's website.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#2

Re: MGE Galaxy 5000

01/05/2012 11:29 AM

Or you can try this

Hey, it's a very slow morning

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: MGE Galaxy 5000

01/05/2012 12:19 PM

lol that 's perfect....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Location: Deepest Darkest Rutherford Oz
Posts: 951
Good Answers: 145
#4
In reply to #2

Re: MGE Galaxy 5000

01/05/2012 12:43 PM

You should PM Lyn with the link to that app, He'd appreciate it

__________________
There are two reasons for a man to do a thing, One that sounds good, and the real one...
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: MGE Galaxy 5000

01/05/2012 4:57 PM

I'm not smart enough to make it work.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6

Re: MGE Galaxy 5000

01/06/2012 5:55 AM

See page 62 for physical location of output fuse. Functional location shown on page 16 in the single line diagram.

There are lots' of other goodies in the manual. Recommended reading.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Participant

Join Date: Jan 2012
Posts: 2
#7

Re: MGE Galaxy 5000

01/06/2012 6:25 AM

APC have the spare fuses and location, they will not inform us on the location as they want to charge £1200 for an engineer to walk through the door and will not supply the fuse alone as they say it is a fit only part and they do not sell them.

We fit different manufaturer UPS Systems so we are capable of changing the fuse if we can locate it?

I have already tried to google the location and have spent hours going through pages and have still not found the location.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8
In reply to #7

Re: MGE Galaxy 5000

01/06/2012 6:53 AM

What is a "fit only part"?

Didn't the URL provided in #6 help you identify the fuse location?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Participant

Join Date: Oct 2011
Posts: 2
#9

Re: MGE Galaxy 5000

01/06/2012 7:47 AM

Well, normally these UPS have Internal Circuit Breakers.. Do check the Breakers also!

http://rep.mgeups.com/edg/edg/manuals/5users.pdf

See Page 17!

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Alanmodular (1); KJK/USA (1); lyn (1); PWSlack (1); SolarEagle (1); Tek (1); Tobugrynbak (1); Wal (2)

Previous in Forum: Difference Between L, M, and H Type Vented NiCd Cells   Next in Forum: Start A Free Spinning Motor

Advertisement