Cable Insulation

01/11/2012 9:42 PM

I'm executing a project that applies both Australian Standard and IEC Standard.

The problem is with the cable insulation, the client wants V75 cable insulation (AS Standard), while in the market of our country, we only have V70 cable insulation (IEC Standard). With IEC standard, the next insulation level is V105, and the price is rocketing.

Is there a formula for cable insulation that will prove with a certain continuous nominal current, we need only V70 insulation?

Register to Reply
Pathfinder Tags: cable insulation
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Cable Insulation

01/11/2012 9:56 PM

How about importing some V75-insulated cable, along with showing that it meets or exceeds the V70 standard?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Cable Insulation

01/11/2012 10:45 PM

This should cover it...http://www.transmission-line.net/2010/12/electrical-formulas-for-power-cables.html
Estimated Insulation Resistance of a cable:
IR = K log (D/d)
K = specific insulation resistance in megohs - 1000 feet at 60 Deg. F (K = 2000 for PVC; 50,000 for EPR; 100,000 for XLP)
D = diameter over insulation
d = diameter under insulation
IR = insulation resistance in megohms - 1000 feet. Note that IR is inversely proportional to the cable length. So don't forget to divide the calculated IR for 1000 ft. by your Cable Length (L) then multiplied by 1000.
Be advised that in the real world, the measured IR may not be anywhere close to the calculated IR due to extraneous influences such as humidity, temperature, dirt, etc.

Read more: http://wiki.answers.com/Q/What_is_the_formula_used_to_determine_insulation_resistance_in_a_cable#ixzz1jDC3gX93
http://www.openelectrical.org/wiki/index.php?title=Cable_Sizing_Calculation
Some good info here...http://support.fluke.com/find-sales/Download/Asset/1579160_6115_ENG_C_W.PDF

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Commentator

Join Date: May 2011
Posts: 80
#3

Re: Cable Insulation

01/12/2012 3:25 AM

Thanks for the response,

but the formula is used to get the value of insulation resistance.

The V70 is related to the 70 deg C of insulation. How do I know the final temperature of cable's conductor when it's being loaded to the rated ampacity?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4
In reply to #3

Re: Cable Insulation

01/12/2012 9:02 AM

It's all in the links I provided, including ambient temp effects on insulation, a possible loop hole..

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#5

Re: Cable Insulation

01/12/2012 5:39 PM

There are provisions in AS/3000 (Australian Wiring Rules) and AS/3350 (Electrical Appliances) that may allow for deviation from the V75 requirement.

However, you will find that the approval process will not be worth the time and effort.

Much better an cheaper to import the required wiring\cabling at V75 and build a better, safer product.

The difference between the IEC and AS standards are due to the harsher environment and higher ambient temps found in Australia during the summer.

Take the High Road..

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Local_Eng (1); Sapper (1); SolarEagle (2); Tornado (1)

Previous in Forum: Earthing   Next in Forum: Replacing Obsolete IBGT Modules

Advertisement