Positive Pressure Ventilation

01/13/2012 4:03 AM

WE HAVE 12350 Cu ft ROOM AND WE NEED POSITIVE PRESSURE ABOUT 500 Pascals;WHAT SHOULD BE THE SUPPLY AND EXHAUST OF THAT ROOM?????/

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: POSITIVE PRESSURE VENTILATION

01/13/2012 5:38 AM

Please turn off Caps Lock.

What is the leak flowrate at 500 pascals?

This is a function of the building design.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jan 2012
Posts: 2
#2
In reply to #1

Re: POSITIVE PRESSURE VENTILATION

01/13/2012 6:00 AM

if we maintain 20000 cfm supply and 15000 cfm exhaust in 12350 cu ft room,how much positive pressure would be inside the room, is that abt 500 pascals???

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: POSITIVE PRESSURE VENTILATION

01/13/2012 7:59 AM

With those figures, the room would increase in pressure until something blows out, like a window, a door or even a roof or wall. The doubling time is 12350/(20000-15000) ≈ 2.5min and 0.2 bar is enough to knock a wall over, so expect something to go BANG in about 30 sec.

No, the incoming and the exhaust rates are the same. What are they at 500 pascals? Once that figure is known, the rest falls into place, because that is the figure needed to size the fan. "Air changes per hour" is a useful number. What is it, please?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: POSITIVE PRESSURE VENTILATION

01/13/2012 7:12 AM

Once again, it depends on how tightly sealed the room is, how often and how long doors might be opened, etc. Even if you can calculate these things, actual installed conditions may vary considerably. One approach would be to size each fan generously, and then use a VFD to control one or the other so as to maintain the desired 500 Pa pressure difference.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#5

Re: POSITIVE PRESSURE VENTILATION

01/13/2012 11:04 PM

Is the ONLY criteria that the space be pressurized to the level indicated? With no concern for temperature or air circulation rate?

IF you only need to pressurize the space, the easiest way is to install a supply fan sized for, say, two air changes an hour (12350 x 2 / 60) = 412, say 420 SCFM at 600 Pa (about 2.5 inches of water) and install an adjustable barometric damper at the exhaust from the room (venting to atmosphere) sized for about 500 FPM airflow velocity (about 120 sq inches). Adjust the damper for the required pressure.

IF you need to maintain a temperature in the room, have that system operate with recirculated air only, with capacity to support the supply air at whatever conditions it is- temperature and humidity to the room conditions.

If the room will see any amount of door openings during an hour, you might want to boost the fan size to twice what was suggested earlier, with a correspondingly larger exhaust.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.