Hi ,
We have a 12.5 MVA 34.5 kv / 4.16 kv Power transformer , which has a 3 Wire RTD for Oil temperature monitoring . The transformer is working fine about 65 % only loaded , no abnormal current raise , no faults on the load side recently , the temperature of oil is about 54 Deg C for the last two weeks , as displayed in the DCS trend.
The problem is the transformer tripped on Oil temperature high ( Trip set at 90Degs C ) , though the DCS trend couldn't capture it but the DCS alarm summary has a record stating that the oil temp went high to 106 Deg c suddenly for a fraction of a second and returned back to normal temperature .
During the investigation found all ok with the trip circuit loop , no abnormality of loose termination or a malfunction of Temp monitor controller etc.,. Only thing which was noticed is that though the 3 wire RTD ( 10 Copper ) is connected properly , the cable shield is left ungrounded .
The question is , Can this signal wire pick up stray noise and make the temperature raise to 106 Deg C momentarily and that resulted in a trip ? Is it necessary to ground the shiled of the signal cable ?
Can we conclude the non-earthing of the RTD cable could be the cause for the trip of transformer ? Otherwise , the electrics are perfectly ok .
Request those experienced to offer valuable feedback .
Thanks and best regards,,,,,