Sulfur Dioxide as Refrigerant

01/23/2012 6:27 PM

Hi, the other day I saw a GE "Globe Top" refrigerator (ca 1930) in a garage sale which looked quite nice and I would like to buy if there is a chance of bringing it back to life again.

This fridge was in quite good conditions, but the owner could not tell me if it works or not. Cables were in poor conditions, so I did not dare to connect it to the power outlet.

Inside the cabinet it had a small evaporator and a couple of shelves. There was no condenser at least, not as I know them (in the rear), therefore I believe that the ball on the top contains both the compressor and the condenser fixed to the interior of the ball. This probably means that the ball did get warm when in operation.

Searching a bit I found that these kind of fridges had Sulfur Dioxide as refrigerant, as Freon was released after WWII. Do you know if there is there any chance of replacing the old refrigerant for Freon or any other substance less potentially toxic as SO2?

__________________
the more I move, the deeper I get stuck !
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Sulfur dioxide as refrigerant

01/23/2012 6:49 PM

I believe this model uses methyl formate, read the links before attempting anything...These repair manuals deal with this period of refrigerator...I don't know of any drop in replacement refrigerant...

" Before the introduction of less-toxic refrigerants, methyl formate was used as an alternative to sulfur dioxide in domestic refrigerators, such as some models of the famous GE Monitor Top. Owners of methyl formate refrigerators should keep in mind that, even though they operate below atmospheric pressure, if evidence of a leak develops, they should take measures to avoid exposure to the ether-smelling liquid and vapor."

The book is called "Servicing Hermetically Sealed Units" by Nickerson and Collins. Another one is "Audels Air Conditioning and Refrigeration" guide. (get an old publication date)

http://en.wikipedia.org/wiki/Methyl_formate

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 2)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #1

Re: Sulfur dioxide as refrigerant

01/23/2012 10:38 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Sulfur Dioxide as Refrigerant

01/23/2012 10:13 PM

From what I have heard about the older SO2 refrigerators, they were often supplied by a central compressor/condenser serving multiple evaporators, as in apartments. I don't know the function of the "globe tops", but the example shown doesn't show any condensing coils. Does any wiring go to it, as would be the case if a compressor was in there?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4
In reply to #2

Re: Sulfur Dioxide as Refrigerant

01/23/2012 10:48 PM

The compressor and condenser are located in the globe, and generate a great deal of heat when running...These type refrigerators are purported to be the most reliable ever made with many still in use today...I know people that said they used to use R-12 as a drop in replacement, but can't personally attest to it's longevity...R-12 has been discontinued for some time now, it's replacement 134-A is used in place now, more efficient but higher pressure....The original SO2 and methyl formate can no longer be used legally, so recharging with either of these is not an option...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2007
Location: Buenos Aires, Argentina
Posts: 1679
Good Answers: 33
#5
In reply to #2

Re: Sulfur Dioxide as Refrigerant

01/24/2012 5:18 AM

As far as I know, both motor anf coils were inside the globe, and yes, the wiring goes to the rear of the globe

__________________
the more I move, the deeper I get stuck !
Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#6

Re: Sulfur Dioxide as Refrigerant

01/24/2012 10:56 PM

The first refrigerant used was ether employed by Perkins in his hand operated vapor compression machine. During nineteenth century so2,methy chloride and co2 found application as refrigerants. After the introduction of fluorocarbons due their excellent thermo-physical properties all natural refrigerants find less application. Recently due international environmental protocols these natural refrigerants get more attention.

Register to Reply
Power-User

Join Date: Apr 2008
Location: Baltimore
Posts: 119
Good Answers: 3
#7
In reply to #6

Re: Sulfur Dioxide as Refrigerant

01/25/2012 7:37 AM

"cool" discussion! :-)

Register to Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#8

Re: Sulfur Dioxide as Refrigerant

01/25/2012 10:01 AM

If I am not mistaken SO2 is considered as an environmental threat or hazard, therefore you may not be able to use it.

Register to Reply
Power-User

Join Date: Apr 2007
Posts: 196
Good Answers: 2
#9

Re: Sulfur Dioxide as Refrigerant

01/25/2012 10:04 AM

how much $$ were they asking for it?

i would have bought it in a heartbeat if the price was right, working condition or not.......

Register to Reply
Guru

Join Date: Apr 2007
Location: Buenos Aires, Argentina
Posts: 1679
Good Answers: 33
#12
In reply to #9

Re: Sulfur Dioxide as Refrigerant

01/25/2012 12:09 PM

Hi reefdiver, they were asking 350 U$S in a garage sale in Buenos Aires...

__________________
the more I move, the deeper I get stuck !
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10

Re: Sulfur Dioxide as Refrigerant

01/25/2012 10:46 AM

Why not update it with modern technology? Probably quieter and also more efficient as well as not being lethal or illegal!!!

Even replacing the insulation will improve the efficiency as well.....

Great box and if properly spray painted, could be a real eye catcher as well.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Apr 2007
Posts: 196
Good Answers: 2
#11
In reply to #10

Re: Sulfur Dioxide as Refrigerant

01/25/2012 10:50 AM

that unit has Americna Restorations written all over it..........

Register to Reply
Guru

Join Date: Apr 2007
Location: Buenos Aires, Argentina
Posts: 1679
Good Answers: 33
#13
In reply to #11

Re: Sulfur Dioxide as Refrigerant

01/25/2012 12:11 PM

As I did not have a camera when I saw it, I got the pic from the Internet just to show what fridge model I am talking about.

__________________
the more I move, the deeper I get stuck !
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#16
In reply to #11

Re: Sulfur Dioxide as Refrigerant

01/25/2012 2:32 PM

...and who is "Americna Restorations"????

Never heard of them before!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Apr 2007
Posts: 196
Good Answers: 2
#18
In reply to #16

Re: Sulfur Dioxide as Refrigerant

01/25/2012 2:57 PM

it is a TV show on the history channel...........they do restorations on some really coll stuff.

http://www.history.com/shows/american-restoration

btw, i googled these and found one listed on Craigs List in Johnstown PA, for $250, hs was asking $450 and is working his way down

Register to Reply
Guru

Join Date: Apr 2007
Location: Buenos Aires, Argentina
Posts: 1679
Good Answers: 33
#14
In reply to #10

Re: Sulfur Dioxide as Refrigerant

01/25/2012 12:14 PM

Hi Andy! I actually thought about updating it. My fear is it probably will loose it´s charm....

__________________
the more I move, the deeper I get stuck !
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#17
In reply to #14

Re: Sulfur Dioxide as Refrigerant

01/25/2012 2:35 PM

If it was not going to be used, I would probably just leave it as a dry cupboard, but if you really want to use it, then it has to be safe and legal....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#15

Re: Sulfur Dioxide as Refrigerant

01/25/2012 12:29 PM

Ah yes the good old days, SO2. I remember in my youth we were demoing an old Creamery Pacific Reach In cooler in a house in the SF bay area. So2 was not common any more it was the regular 22,502,and 12 so I just cut the lines under the house..........that rotten egg smell of the SO2 was........well bad, and I did not know that I could crawl that fast....

So with this one the globe at the top was a static condenser with a "pancake" compressor inside the globe. GE's pancake compressors were bullet proof and very quiet.

I have retrofitted one of these to now 134a, but you are going to need to remote the condensing unit.

Open the globe and cut the suction and liquid line. Install a new cap tube for the evaporator and suction line, 3/8 suction and 1/4 liquid. Use cap-tube sizing chart B for the cap-tube. Once you have made all those connections inside the globe stub the line out the back. A this point you can set a condensing unit anywhere you want under the house is usually best or in a garage. Run the suction and liquid lines between the two and switch the outlet you install with the units cold control.

Winner winner chicken dinner your running and cold again.

__________________
To be or not to be........ok that's a trick question.
Register to Reply
Guru

Join Date: Apr 2007
Location: Buenos Aires, Argentina
Posts: 1679
Good Answers: 33
#19
In reply to #15

Re: Sulfur Dioxide as Refrigerant

01/26/2012 11:47 AM

Thank you a lot for your useful reply! Knowing it is possible, now I ONLY have to do some sweet talk to my wife for her to approve my project!

__________________
the more I move, the deeper I get stuck !
Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: