How DO should be wired? In dry contacts or need plus(+) & (-) both need, cause when it goes from DO card to any relay Or pushbutton it shows 24volts & when u push it become "0" it means it's used dry contact only positive? Am I right? Do we really wired only plus(positive) in filed from DO to field to back DO card? I really not understand that how DO/DI should wired ? Whats logic used to also for DI wired from card to any sensor or push button ....Might be it silly question but I really want to know ...If some body have drawing ..I will be appriciated
Re: logic for DO & DI ,AI & AO
02/04/2012 10:56 AM
digital output means 24 volt out when DCS or PLC send command you get 24v & run through DO card to your relay solenoid but it's in black & white wire 24 volts ok, no dry contact ......( i mean used black & white as dry there is no polarity as + & - , only +) cause minus (-) already at card , cause plus contact will through all field to sensor and comeback at card...
any confusion
02/04/2012 11:04 AM
if you used 24 volt +& - from digital card to field relay or push button & when it's energized or contact close that time your wired plus & minus are getting short circuit..it cause i alrady measure 24 volt across terminal when stop command from DCS for motor , where 0 volt across start command , actual motor is off not running ...when command comes from dcs start shows 24 & stop shows "0" ? so what about dry contact?
02/04/2012 10:57 AM
Read the manual(s) for your equipment. They'll almost certainly include examples of how to connect various types of input and output.
02/04/2012 11:05 AM
can suggest good documents available at on any site ?
02/04/2012 11:16 AM
What make and model(s) of equipment?
Re: Logic For DO & DI ,AI & AO
02/04/2012 9:36 PM
JohnDG is right. You need to submit the make and model of the PLC, or have you finally delved into the instructions and now feel foolish for not doing so from the outset?
02/06/2012 4:01 AM
RTFM.
Good Answers: 128
02/13/2012 9:45 PM
Anonymous,
The word "circuit" is chosen because it means that there is a complete path from the power source through the controlling device to the load and finally returning to the power source. This is true for AC, or DC. For DC devices, the polarity will be very important whenever you are using transistors.
For a digital/discrete input device, the "load" is the digital/discrete input and the "controlling device" is a switch, or other sensor. Some of these sensors require their own source of power to run (so they would require three or even four wires), while others may draw their operating power as a small "parasitic" load on the two-wire loop to them.
For a digital/discrete output device, the "controlling device" is the digital/discrete output and the "load" is a relay, solenoid, light, motor starter coil, etc.
If you check the wiring diagram for your controller, you will see one or more terminals labeled as "common", with the label telling which inputs or outputs it is associated with. If you fail to make a connection from this common terminal to the appropriate power supply terminal, your controller may appear to have no faults, but there will be no control of your machine.
OK?--JMM