Can Main Switch Be a Load Break Isolator?

02/05/2012 11:57 PM

Dear Friends,

If one wish to use Havells make DHMIODPX040 Isolator as main switch immediate after residential Tariff Meter of Electricity Board,that is the input to the isolator will be from Meter and output will go to distribution board. Whether this isolator will give short circuit protection or this is just act as a load break switch and will not have O/L or Sckt protection.I don't see any sckt breaking current rating of the isolator in manual. Can anyone confirm.

Thanks

__________________
BNDas
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Can Main switch be a load break Isolator?

02/06/2012 12:44 AM

Normaly off load switching only. Under fault it could have bad results.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Can Main switch be a load break Isolator?

02/06/2012 1:12 AM

Isolators, switches, switch-disconnectors are switched ON and OFF manually. Do you seriously expect them to have a short-circuit breaking capability? This is only possible by devices which can switch off automatically, like circuit breakers.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Associate

Join Date: Jan 2012
Location: chennai.
Posts: 27
#3

Re: Can Main switch be a load break Isolator?

02/06/2012 1:19 AM

Dear biswanath as u mentioned its only act as a load break switch.

__________________
Prabakar
Register to Reply
Associate
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jun 2011
Location: Chennapattanam (Coromandel Coast of the Bay of Bengal).
Posts: 31
Good Answers: 1
#4

Re: Can Main switch be a load break Isolator?

02/06/2012 1:45 AM

http://www.electroconcepts.in/havells/PDF/havells_Product_wise_Catalogue.pdf

the given model is an havells MCB (Pg:29 describies )

They are switch disconnectors with independent

manual operation, capable of making, carrying

and breaking currents under normal circuit

conditions, which may include operating

overload condition and also carry currents under

specified abnormal circuit conditions such as

those of short circuit for a specified time....Ref .p30 tech specification....

Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#6
In reply to #4

Re: Can Main switch be a load break Isolator?

02/06/2012 6:53 AM

O/l Condition automatic trip or manual load breaking capacity?

__________________
BNDas
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: Can Main switch be a load break Isolator?

02/06/2012 6:59 AM

Well, if it were to have automatic overload breaking capability then it would be called an overload circuit breaker and not an isolator.

Sheesh.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Can Main switch be a load break Isolator?

02/06/2012 4:35 AM

It doesn't provide overload breaking. That's why it is called an isolator.

Nor would it. It is the job of individual circuit breakers downstream of it to provide overload protection on the smaller circuit cables. The overload protection on the isolator may well be the utility company's fuse upstream of the isolator.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply