Power Factor

02/06/2012 11:08 PM

does power factor controller works at single phasing if then how ? Please define clearly.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: POWER FACTOR

02/06/2012 11:13 PM

This guy might help you, again. Ron Nombri

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: POWER FACTOR

02/06/2012 11:22 PM

Please define the question more clearly. When you say "single phasing," do you mean a 3-phase system with a lost phase, or do you mean an actual single-phase system? What does the "power factor controller" consist of?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Jul 2011
Posts: 32
#3
In reply to #2

Re: POWER FACTOR

02/06/2012 11:27 PM

YES SIR...i mean a 3 phase system with a lost phase. and i mean if there is a power factor system already installed in our company.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #3

Re: POWER FACTOR

02/06/2012 11:35 PM

Is this the same system you have been having problems with all along?

Register to Reply
Commentator

Join Date: Oct 2011
Posts: 95
#5

Re: POWER FACTOR

02/07/2012 3:19 AM

I guess the question is : what is the effect of running a capacitor bank (automatic power factor control panel ) connected to the electrical systems (3 phase ) if one phase line is missing .

Single phasing is a term used to represent operation of 2 phases in a 3 phase system due to missing of one phase.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: POWER FACTOR

02/07/2012 4:37 AM

Sure, your guess is right...that is the question.

"A very good question" says the Prime Minister.

"Thanks............. but...... what is the answer, Prime Minister?" asks the TV interviwer in "Yes, Prime Minister"

Sorry, couldn't help it

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#9
In reply to #6

Re: POWER FACTOR

02/08/2012 12:05 AM

1)If one phase fails for a 3phase capacitor will the other two become overloaded and if there is no OL protection will the fuse blow?.

2) If the failed phase(in main CB/Fuse) was feeding the control circuit everything(all contactors) will release and pf becomes very low,but if another phase fails will the situation be similar to 1) above,will the PD in CB operate?. If it is fuse should we include an OCPD?.

__________________
pnaban
Register to Reply
Commentator

Join Date: Oct 2011
Posts: 95
#7

Re: POWER FACTOR

02/07/2012 5:16 AM

I have no answer. I am also looking for the answer.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: POWER FACTOR

02/07/2012 5:48 AM

Until the circuit protective device(s) operate(s), there will be too much capacitance in the circuit.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Oct 2011
Posts: 95
#10

Re: Power Factor

02/09/2012 2:10 AM

Thanks

Will this high capacitance cause any damages in the system ?

Normally we will be providing relay to protect against single phasing, whether we have to consider the protection against high capacitance also ?

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#11
In reply to #10

Re: Power Factor

02/09/2012 5:01 AM

Where is the relay connected at input of individual capacitors after the CB/Fuse or at the main CB/fuse?.

__________________
pnaban
Register to Reply