In our test bed for testing ac motors of LT Range, we observe analog ammeter and correspondingly wattmeters- showing fluctualing and oscilating current, instead of steady current. Request your kind solutions for this phenomenon.
The test bed consists of a DC Motor driven alternator; which gives the ac supply required for the test motor. The ac motor is coupled to a dc generator. The DC generator and DC Motor are paralleled; and subsequent to which the load on the ac motor is adjusted by controlling the excitation of the DC Generator.
It appears that the fluctuating current the analog meter showing is due to low frequency current in the stator of the ac motor; superimposed on the fundamental current, showing fluctuating current.
Which machine in the above set up can result in this problem?
Re: AC MOTOR TESTING- METER SHOWING FLUCTUATING CURRENT..
02/07/2012 3:23 AM
Just add a huge f-off-sized lump of weight to the ammeter needle.
Good Answers: 181
Re: AC Motor Testing- Meter Showing Fluctuating Current
02/07/2012 11:27 AM
How is the field of the DC load generator controlled?
Out of interest has this system worked OK in the past?
If the DC load generator and the DC motor are paralleled how does the system start?
Good Answers: 102
02/08/2012 6:10 AM
I was asking the third question you posed myself.
Is this some sort of attempt at over unity?
OP, post a drawing of your setup please.
Good Answers: 73
02/07/2012 12:03 PM
It sounds like you need to isolate the problem some more.
Perhaps you can substitute some large resistors for the test motor to see if the source is stable. Perhaps some axis if off center. This would be a mechanically induced instability. Sometimes you have to test the test!
Good Answers: 181
02/07/2012 8:59 PM
Unless you give more information an answer is unlikely.