DG

02/07/2012 2:14 AM

my load is 700 amps,what capacity of dg set required for that

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: DG

02/07/2012 3:04 AM

700 amps; how could it be anything else?.

How many volts? (Then we can calculate kw.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: DG

02/07/2012 3:22 AM

Yep. Something over 700 amps will do it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Oct 2011
Posts: 95
#3

Re: DG

02/07/2012 3:44 AM

Power = √3 V I CosØ

= 1.73 x 415 x 700 x 0.8 Assuming voltage 415V

= 427 kW

Depending on the load , like if it is single unit, the staring current will be much more. If it is small loads together, like 100+125+ 75+ 50 + 150+100+200, the staring current can limit by scheduling the starting of machines.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Feb 2012
Posts: 3
#4
In reply to #3

Re: DG

02/08/2012 10:23 AM

thnks arif

I have to run welding & drilling m/cs on dg. how much percent of additional power i need

Register to Reply
Commentator

Join Date: Oct 2011
Posts: 95
#5

Re: DG

02/09/2012 1:58 AM

What are the loads of machines ?

This case of welding machines and drilling machines need more attention as it is not a constant load.

If it would have been a normal load 500kVA is Ok. The load is 80% .

But your load is not a normal load.

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

arifkunnath (2); PWSlack (1); ravimumbaikar (1); Tornado (1)

Previous in Forum: AC Motor Testing- Meter Showing Fluctuating Current   Next in Forum: Synchronization Problem

Advertisement