Insulation Class F/B

02/20/2012 3:33 PM

One of our siemens 450KW motor has insulation class as F/B. what does that mean.is it a class F motor with temperature limit of 155 degree or class B motor with temperature limit of 130 degree.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: insulation class F/B

02/20/2012 3:43 PM

NEMA Insulation Classes

Check the Sieman's web site?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Insulation Class F/B

02/20/2012 5:45 PM

Most likely the motor was designed to class F standards as a minimum standard by the manufacturer...meaning it is designed to operate in either F or B standard...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#3

Re: Insulation Class F/B

02/20/2012 11:59 PM

This means that the motor is so designed that its temperature will not exceed class B limit i.e. 130 degree, although the class of insulation for the winding is selected as F. Thus adequate margin (25 degree) will be provided for temperature rise and the expected life of motor insulation will be more as compared to another motor of same rating but with insulation class B.

Register to Reply
Member

Join Date: Feb 2012
Posts: 5
#4

Re: Insulation Class F/B

02/21/2012 12:29 AM

it is a class F motor with temperature limit of 155 degree. Temperature rise according to B. So 155-80=75. The motor can be use in a place that the teperature no more than 75 degree.

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#5
In reply to #4

Re: Insulation Class F/B

02/21/2012 12:50 AM

Can you please explain what is 80 degree and what is meant by " The motor can be use in a place that the temperature no more than 75 degree " ?

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#6

Re: Insulation Class F/B

02/21/2012 7:20 AM

Most likely, the answer is, insulation of the motor is designed to class F and temperature rise of the motor is restricted to class B under rated voltage, frequency, and full load condition. That is to say there is a temperature buffer of 25 degree celcius( 155C- 130C). The cooling system of the motor is designed to achieve the above.

Manindra

__________________
Manindra
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#7
In reply to #6

Re: Insulation Class F/B

02/21/2012 7:46 AM

Yes, you are right.

Register to Reply
Active Contributor

Join Date: Jan 2012
Posts: 16
#8

Re: Insulation Class F/B

02/22/2012 12:47 AM

Motor has class F insulation with temperature rise limited to class B. That is to say, though the insulation of the motor windings have been designed as per class F motor, under normal running conditions, the winding temperature shall not exceed class B. However in this regard, the duty of the motor has also to be considered. If the motor is designed for S1 duty is not recommended to use it for S4 duty.

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#9
In reply to #8

Re: Insulation Class F/B

02/22/2012 1:30 AM

Along with duty type S1, S4 etc. you should also mention cyclic duration factor (CDF) and duty cycle which has direct influence on temperature rise of the motor. S1 duty motor can very well be used for S4 duty if the rest and de-energised time of the motor is more.

Register to Reply
Active Contributor

Join Date: Jan 2012
Posts: 16
#10
In reply to #9

Re: Insulation Class F/B

02/22/2012 1:39 AM

sorry debata, I thought that much is pretty well understandable and so didnt be specific But I am glad u got my point

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#11
In reply to #8

Re: Insulation Class F/B

02/22/2012 2:36 AM

S1duty motor may be used for S4 duty with reduced KW rating in exceptional/ under compelling situation. The reduced rating should be carefully considered.

Manindra

__________________
Manindra
Register to Reply
Commentator

Join Date: Oct 2009
Location: Dubai,UAE
Posts: 62
Good Answers: 2
#12

Re: Insulation Class F/B

02/22/2012 2:25 PM

Insulation Class B allows temperature rise 130C and class F allows 155C.

__________________
There are no shortcuts on the road to a great experience.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#13

Re: Insulation Class F/B

03/25/2018 3:40 AM

Dear Mr. coolyar,

It indicates that the Motor is designed for Insulation Class F, but the Temp. Rise is (or will be) restricted to Insulation Class B.

DHAYANANDHAN.S

Register to Reply