MCB

03/02/2012 11:40 PM

Hi All,

i've install two DB then main DB is 6kaic and the sub DB is 10kaic.

Any help please.

Regard

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: mcb

03/02/2012 11:43 PM

How would that be?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster #2
#2

Re: mcb

03/03/2012 2:12 AM

I think you mean kA rating of breakers....Then it is wrong. kA rating of breakers shall be based on the short curcuit current levels at each levels such as MDB, SMDB and DBs...however it might be Main DB at 10 kA and sub DB at 6 kA...calculate the fault current and find out the exact range.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: MCB

03/04/2012 7:23 AM

Okay! What about that? What help do you need?

Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#4

Re: MCB

03/04/2012 10:56 PM

This kind of post is exactly what scares me about unqualified personnel working with electricity! If they were qualified, they wouldn't need to ask the question! People can get killed! Re kaic: what units are those?

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Reply
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#5

Re: MCB

03/05/2012 2:46 AM

Of course the first thing to do is to calculate the prospective SC rating needed at the incomer level .

If it is 6 KA or below, using a 6 KA incomer and 10KA feeders won't harm . A 10 KA works well on a 6 KA short circuit ! It is not economically optimized, but technically OK.

Reply
Active Contributor

Join Date: Feb 2012
Posts: 13
Good Answers: 1
#6

Re: MCB

03/31/2012 6:50 AM

Hi,

Of course MCB short circuit rating has to select based on the load short circuit current, Usually Main DB should be higher KA rating and downstream SDB's designed with lesser than Main DB KA rating, otherwise if any short circuit happens and it is less than SBD short circuit level and more than main DB short circuit level, then main DB will trip first, so the SDB also disconnected. Hence choosing right co-ordination is very important. Second thing is MCB Class of operation, there is Class A, B, C type MCB's available. Mainly these classes represents the tripping time. You have to careful on this otherwise unnecessary tripping will happen.