MCB, MPCB (Panel Design)

04/02/2012 2:43 AM

How can i decide rating of MPCB,MCB & MCCB??if i m using 2 Hp drive for motor then what should be rating of MCB? again if i m using 2 hp motor(DOL) then what should be ratings of MPCB & Contactor?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: MCB,MPCB(panel design)

04/02/2012 3:26 AM

It is usual to use an appropriately-rated overload device to protect the motor and appropriately-rated fused to protect the wiring that feeds it. The method is called "co-ordination" and details of the principle and a methodology for using it may be found within national electrical standards, such as British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: MCB,MPCB(panel design)

04/02/2012 3:27 AM

Ever thought of doing you own homework?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
3
Commentator
France - Member - New Member

Join Date: Feb 2012
Location: Grenoble, France
Posts: 76
Good Answers: 4
#3

Re: MCB,MPCB(panel design)

04/02/2012 4:27 AM

To protect your 2HP motor the first and important parameter to know is the nominal current of motor at full load.This information should be printed on motor performance label and you should find different current rating in regard of nominal voltage.
Then it depends if you select an MPCB (Motor Protection Circuit Breaker ), MCB ( Minaiture Circuit Breaker ) or MCCB ( Molded Case Circuit Breaker ).Some of them protect only for short circuit and some of them protect for short circuit and thermal overload.- If you select the Circuit Breaker with thermal protection embeded you just need a contactor to switch "ON/OFF" your motor.-

If you select the circuit breaker withtout thermal protection you need to add an overload protection relay to protect your motor agaisnt overload and the contactor to switch "ON/OFF" your motor.- You should never use a circuit breaker to switch "ON/OFF" a motor. The circuit breaker is not designed for this and will wear faster than normal.- Your motor starter shall always include a contactor to switch "ON/OFF" motor.
Now you have selected the Circuit breaker with or without thermal overlaod.

You will have to know :

1 - Motor inrush current can goes up to 8 x In ( In = Motor nominal current at full load. Motor plate label information ). This value could be higher with poor quality motors.

2 - MPCB ( Motor protection Circuit breaker ) are designed to accept this inrush current without tripping.If you select electrical protection circuit breaker you may face nuisance tripping on motor starting.

3 - Your Overload protection separate or embeded in the circuit breaker shall be adjusted to motor nominal current.

In conclusion- The circuit brealker shall accept inrush current and shall have a setting range which include the motor nominal current.

Hope this will help

Register to Reply Good Answer (Score 3)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4

Re: MCB,MPCB(panel design)

04/02/2012 4:50 AM

One caution in addition to the good responses already given. A thermal overload relay is (a) more accurate than the thermal trip system of any breaker and (b) it is sensitive to phase loss (most MPCBs also are, but MCBs and MCCBs are not)

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: MCB, MPCB (Panel Design)

04/02/2012 10:24 AM

Follow the Type-2 Co-ordination Switchgear Selection Charts published by leading switchgear manufacturers. But, please note that you would find charts only for MPCB + Contactor and MCCB + Contactor + Thermal OVerload Relay Charts. You would not find a selection chart with MCB back-up as it is not recommended. Why it is not recommended, I have answered to another question in this forum itself. Pl. do a search.

Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); kvsridhar (1); obouill (1); PWSlack (1); TonyS (1)

Previous in Forum: Dual Input Power Supply   Next in Forum: IM & PM Used with PLC

Advertisement