Flow Measurement Inside Cement Duct

04/15/2012 11:51 PM

Hello. I am thinking of installing waste heat recovery boiler(WHRB) between PH and ID fan and so I am looking for the way to continously measure flow (and heating value if possible) inside the duct between PH and WHRB. Since there are a lot of dust inside duct, I am not sure what kind of flow meter would function without problem in a which way and so I would appreciate it if someone recommends. Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Flow measurement inside cement duct

04/16/2012 3:31 AM

Non-invasive types such as clamp-on ultrasonics spring to mind.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#2
In reply to #1

Re: Flow measurement inside cement duct

04/16/2012 2:10 PM

Ultrasonics is a good idea.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#3

Re: Flow Measurement Inside Cement Duct

04/16/2012 7:21 PM

Please keep us informed as to what you choose and how it works out.

Many ultrasonics require minimum gas pressures to get the density high enough to function get sufficient signal strength through the gas medium.

Dust probably eliminates transit time ultrasonic, leaving doppler. It isn't clear to me how well doppler pings through cement, nor its suitability for low pressure gas.

Register to Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#5
In reply to #3

Re: Flow Measurement Inside Cement Duct

04/16/2012 11:57 PM

Doppler shift takes place only due to velocity. Particulate matter and voids cause reflections for ultrasonic wavefront. Ultrasonics is frequently used for velocity measurement in thick concrete. I think that is not a serious matter. One can select proper frequency for ultrasonic probe for density, size of the duct etc. Temperature variations may be of concern as Ultrasonic velocity changes with temperature. Temperature measurement and reading correction is essential.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply
Participant

Join Date: Jul 2011
Posts: 3
#4

Re: Flow Measurement Inside Cement Duct

04/16/2012 11:20 PM

What is the pressure, temperature and expected flow rate, size of the duct and the wall thickness? What is the gas composition?

Register to Reply
Active Contributor

Join Date: Jan 2012
Posts: 16
#6

Re: Flow Measurement Inside Cement Duct

04/17/2012 2:10 AM

Hello, I am unaware of Cement processes. would you mind sharing the medium which you want to measure i.e. Liquid, gas, steam or abrasive? for flow and heat measurement Thermal and Vortex with thermal option is best. Ultrasonic wont meaure heat BTU/hr etc.

Vortex (with thermal sensor) is a safer choice as it is compatible with higher temperatures and pressures. Hope it would help.

Register to Reply
Power-User

Join Date: May 2011
Posts: 102
Good Answers: 2
#7

Re: Flow Measurement Inside Cement Duct

04/17/2012 8:05 AM

I've worked on a cement plant as electrical engineer. I recall ball mills for raw materials, ball mills for coal pulverisation, a long cylindrical rotary furnace converting the raw materials to clinker, more ball mills & fans converting clinker into cement powder and bag filters to catch the stuff.

Are you trying to recover the heat at the end of the long rotary furnace where the raw materials go in and clinker comes out? What are you trying to control by measuring flow, and temperature if you need to know the heat available?

Register to Reply
Associate

Join Date: Nov 2011
Posts: 42
#8

Re: Flow Measurement Inside Cement Duct

04/18/2012 5:10 AM

Thanks for many comments. Here is what I am trying to do with measuring flow in the cement duct.

First of all, I am thinking of installing waste heat recovery boiler between PH and ID fan, and between AQC and EP to generate power. It looks like below.

.

I wish to continuously measure the flow in the duct to check boiler performance and for some other reasons.

There are several kilns which I would like to install above system, so Waste gas composition varies according to the kiln, but it is like N2(78%), O2(3%), CO2(15%), H20(4%) and dust contents is over 50 (g/Nm3).

The gas pressure and temperature after PH and AQC also varies, but it is like 700 mmAq and 400 °C after PH and -100 mmAq and 420 °C right after AQC.

Thanks.

Register to Reply
Associate

Join Date: Nov 2011
Posts: 42
#9
In reply to #8

Re: Flow Measurement Inside Cement Duct

04/18/2012 5:12 AM

-700 mmAq right after PH boiler(due to ID fan) is correct.