Anonymous Poster #1

Tertiary Connected Reactors

04/29/2012 10:25 PM

I need some advice on the following,

At a substation we are replacing the 5MVAR 11kV oil filled reactors connected to the transformer tertiary with air cored reactors. The present oil filled reactors are delta configuration. The new reactors will be separate individual coils and we meant to connect these coils in delta configuration to maintain the existing configuration. The issue is that manufacturers cannot offer us coils that can be connected in delta. They propose we change the configuration to star.

The question is, will there be any change in size or other parameters if we change to star, (surely protection will change, as fault paths will)

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Tertiary connected reactors

04/29/2012 10:52 PM

Can you not obtain separate single phase oil filled reactors you could then connect in Delta?

__________________
jack of all trades
Reply
Participant

Join Date: Apr 2012
Posts: 2
#2
In reply to #1

Re: Tertiary connected reactors

04/29/2012 11:00 PM

Yes, but the manufacturers wont build us small single phase oil filled reactors. what they offered was 3 individual air coils and we can connect them in delta, but they are hesitant for us to connect them in vertical installation and in delta. they offer vertical but connect as star configuration.

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3
In reply to #2

Re: Tertiary connected reactors

04/29/2012 11:10 PM

Why is that, is there an issue with the clearance voltage or mechanical support that Star may not have over Delta, or do they just not offer a tested Delta connection solution?

Jack - More a Neutral Earth Resistor man.

__________________
jack of all trades
Reply
Participant

Join Date: Apr 2012
Posts: 2
#5
In reply to #3

Re: Tertiary connected reactors

04/30/2012 1:18 AM

they wouldnt say, but i reackon its to do with the type testing.

i have asked, will see what thier response is. if we do go for a star config, will i need to re specify the reactance?

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6
In reply to #5

Re: Tertiary connected reactors

04/30/2012 3:16 PM

I am not sure (probably), you would need to check to see how the star configuration is going to affect your protection and the rest of the system.

__________________
jack of all trades
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #2

Re: Tertiary connected reactors

04/29/2012 11:54 PM

5MVAR is a "small" reactor?

Avoiding a vertical stack may keep heat from the lower ones from affecting the upper ones; so that's understandable.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#7

Re: Tertiary Connected Reactors

05/01/2012 5:13 AM

When you connect the 5MVAR, 11kV rated reactors in Star, the effective reactance in each limb and the net MVARs connected in the system will be lower (by 1/v3) than when connected in Delta. Hence, we need to connect in Star only (for wahetever reason), you will have to go for higher (by v3) rated reactors, keeping the voltage rating same.

__________________
Raghunath
Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#8

Re: Tertiary Connected Reactors

05/01/2012 11:03 AM

Really, the overarching question is what purpose do the reactors on the tertiary serve? Whether they are oil-filled or air-core doesn't impact their electrical function. You need to determine if reactors in a Wye (star) configuration will provide the same function as in Delta, except possibly with some adjustment in value, as raghun has suggested. Does the tertiary feed something in your system (station service power?)? Does it perform a function in your protective relaying scheme? You need to figure that out first before you change the connection of the reactors.

Also, just because the manufacturer won't connect them in delta doesn't mean you cannot do it. You may need to add some bus bar or tubing, and some insulators and supports, but it is not impossible to connect them in delta. Put your engineering skills to work!

__________________
To get the right answers, first you need to ask the right questions.
Reply
Associate

Join Date: May 2009
Location: Kansas City, Missouri
Posts: 48
Good Answers: 2
#9

Re: Tertiary Connected Reactors

05/01/2012 4:24 PM

yeah....what raghun said. Remember that the current through the reactor connected in delta is lower than in the wye (star) configuration by a factor of 1/√(3) at the same voltage level. you can connect them in wye (star), but in order to maintain the same voltage level you might need to reevaluate your ratings.

__________________
E pur si muove -- Galileo
Reply