DG Set Capacity Calculation

05/02/2012 10:48 AM

What should be the capacity of DG set to run three nos of 1.5Tonn Split Air Conditioner and 2KW of light & fan load?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: DG Set Capacity Calculation

05/02/2012 11:02 AM

30-50% more than those all added together?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: DG Set Capacity Calculation

05/02/2012 11:54 AM

Why not pose this question directly to the potential suppliers of the gen sets? Our crystal ball is presently in use.

Convert tonns to BTU then convert to KWh, roll it all together and there ya go!

Ask a supplier!!!!!!!!!!! Get a good answer.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: DG Set Capacity Calculation

05/02/2012 2:24 PM

Depending on manufacturer, each AC condensing unit will be about 1.5 KW. Thus the total is about 6.5 KW. In addition, for starting you need a reserve of about twice the largest motor; i.e, another 3 KW. This sums to 9.5 KW, which could be rounded to 10.

This estimate can be refined by knowing the exact KW of the ACs, from the manufacturer. If you are contemplating future expansion, you can go larger.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: DG Set Capacity Calculation

05/02/2012 4:24 PM

15kw...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5

Re: DG Set Capacity Calculation

05/02/2012 4:54 PM

42!

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #5

Re: DG Set Capacity Calculation

05/02/2012 4:58 PM

Ahh, a futurist, planning for expansion!

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#7
In reply to #5

Re: DG Set Capacity Calculation

05/02/2012 5:23 PM

As the response given by redfred is The Answer to the Ultimate Question of Life, The Universe, and Everything, I agree, and also suggest 42.

Unless I have misinterpreted your answer, and instead you refer to a '42 Henway. If that is the case, then I would say Six by Nine (which is also 42) is the answer.

It's about time for this again, isn' it?

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#8
In reply to #7

Re: DG Set Capacity Calculation

05/02/2012 5:45 PM

Towel Day is Friday May 25.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#9
In reply to #8

Re: DG Set Capacity Calculation

05/02/2012 5:52 PM

Oh, that's right! I had forgotten. Thanks for reminding me.

I'll see if I can get a reservation for us for supper at Milliways. My treat! Anybody else want to come along? I understand their Pan Galactic Gargle-Blaster is out of this world!

__________________
Semper Ubi Sub Ubi
Register to Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#15
In reply to #7

Re: DG Set Capacity Calculation

05/03/2012 11:55 PM

OK, i'll bite....whats a Henway?

Preferably a Tandoori chicken

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#16
In reply to #15

Re: DG Set Capacity Calculation

05/04/2012 10:49 AM

"OK, i'll bite....whats a Henway?"

About 3 and a half pounds...

Thanks to kvsridhar for being the straight man!

__________________
Semper Ubi Sub Ubi
Register to Reply
Commentator

Join Date: Jun 2011
Posts: 67
Good Answers: 2
#10

Re: DG Set Capacity Calculation

05/03/2012 2:26 AM

DG set should be able to take the starting KVA. The starting KVA for lights and fans which will come on immediately will be 2.35KVA at 0.85PF. The split units will come on after a time delay. Assuming that all will time out simultaneously, the starting load could be about 1.5 times the running load. the running load is about 1.8KW for each unit. Thus at 0.85 PF the total staring KVA for the split units will be 9.53KVA. The total starting KVA will be 9.53+2.35=11.88 KVA. The DG sets are sized for .8PF and hence a 10KW set should do, but I will go for another 25% derating and go for a 12.5KW set.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#11
In reply to #10

Re: DG Set Capacity Calculation

05/03/2012 2:35 AM

Well, that was amusing; part right but part weird.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 473
Good Answers: 13
#12

Re: DG Set Capacity Calculation

05/03/2012 7:03 AM

Bijay1964 ??...that's hilarious!. Anyone else notice?...Lyn?...OT but C'mon I dyin' over here!

Register to Reply Off Topic (Score 6)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#13

Re: DG Set Capacity Calculation

05/03/2012 9:14 AM

Eeenie Meenie Chili Beany the spirits are about to speak....

The SEER rating of your air conditioners is 42.

That is all.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#14

Re: DG Set Capacity Calculation

05/03/2012 10:05 AM

Type of HVAC? Heat pump? Split system? Gas Pack? Is there suplemental electric heat circuitry? If so, the HVAC unit KW usage cannot be based strictly upon the BTU ratings. The current will be significantly higher when the heating elements are in use and you will need to add this load into your calcs. Check the equipment nameplate for the required power consumption rating on each of the units. If you do not physically have the units in your possesssion, contact the manufacturer and get the IOM and technical DATA sheets. Add all of the loads together then add 25% of the total for unexpected condtions such as line voltage drop, mechanical issues, and ambient temperature changes that are out of the equipment design range.

Register to Reply