Anonymous Poster #1

Trip Coil Monitor

05/14/2012 2:57 AM

why trip coil monitored both pre closing and post closing

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Trip coil monitor

05/14/2012 3:31 AM

What does it say in the user manual for the equipment?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Trip Coil Monitor

05/14/2012 10:13 AM

Why not?

Are there no possibilities of the trip coil getting damaged during breaker closed condition as well as when the breaker is in open condition?

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3

Re: Trip Coil Monitor

05/21/2012 8:48 AM

If you look carefully at the wiring of the trip relay, you will usually find that the monitor relay circuit is looped through all the trip relay contacts. It checks the supply and wiring integrity as well as the coil. This wiring is often extensive and vulnerable to being dug-up by metal thieves, accident, fork-lifts, aside from maintenance error, corrosion - all of which could disable a breaker and lead to a fault being cleared by off-site breakers causing outage.

Reply