burning of our gen-set excitation rotating diodes occurs just after excitation what is the reasons behind this?
Re: Burning of excitation rotating diodes
05/18/2012 3:21 AM
Overcurrent.
Good Answers: 444
Re: Burning of Excitation Rotating Diodes
05/18/2012 10:13 AM
...probably caused by short circuit in the field windings. Assuming that this is the same generator from your previous posts then the reason is that you did not perform any of the electrical tests that are mandatory after energizing a generator at zero speed.
Good Answers: 88
05/18/2012 3:39 PM
Any chance a poltergeist has reversed phase sequence? S.M.
Engineering Fields - Petroleum Engineering - Rig Electrician United States - Member - the Oil Patch Engineering Fields - Power Engineering - Drives & Gen's Engineering Fields - Instrumentation Engineering - Drive Control Popular Science - Cosmology -
05/19/2012 12:26 AM
bet this is a PMG excited gen. An AVR usualy does't open the rotating diodes when they fail, i find them still in the shorted failure mode but a PMG will make enough current to blow them open after they fail shorted and i find them burned open
Check the PMG and it's exciter Faiz
Why do they make manhole covers round? so they won't fall in [before asking "Who is John Galt?"]
05/20/2012 4:21 AM
1) overcurrent
2) you need to replace higher kva than you ussage full load
3) calculate your full operation load in your facilities then chose the generator fit for!
example : your full load is 100kw you need to have 200kw generator
if you do this this will not give you a exciter doid burn out !!!!
i want ot helf piple need assistance and to share my knowleged in technical