Variable Speed Drives

05/18/2012 2:04 AM

Dear friends, I have an assignment to investigate the possibility of using VSD's on large existing water pumps (over 500 kW) operated on 3.3 kV supply. The idea is to keep the flow constant in order to ensure the pump operates at the optimum efficiency.

My question is: VSD's can also be used for starting induction motors. What should I specify to ensure that the VSD can be used for both constant flow as well as a means of starting with low inrush kVA.

Register to Reply
Pathfinder Tags: vsd
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Variable Speed Drives

05/18/2012 3:20 AM

<...ensure that the VSD can be used for...constant flow...>

What will be needed is a flowmeter and a proportional+integral controller.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Variable Speed Drives

05/18/2012 9:36 AM

VFD's are happy running at a constant speed.

If you are really serious about this, contact three suppliers here Search GlobalSpec and tell them what you need.

Use their experience to help you.

Register to Reply
5
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Variable Speed Drives

05/18/2012 1:12 PM

I love VFDs, I live and breath VFDs because I make my living with VFDs, this is something that a VFD can definitely accomplish, both fronts.

That said, you have a potential pitfall here. You said that you want CONSTANT FLOW. Unless the head or pressure changes, ANY pump will provide constant flow, you do not need a VFD for that. So if you have a static head and no change in pressure, but want a different flow from your pump, just trim the impellers. If you use the VFD to run at a constant speed all of the time, you will actually WASTE energy compared to trimming the impellers.

If however there is some other form of variable in the system that you need to compensate for, then by all means a VFD is a more efficient way to accomplish that.

Considerations for MV VFDs:

  1. Heat. MCCs are about 97% efficient, so 3% is waste heat. On a large motor, that can add up to a lot of heat in the room with the drive, you must be able to deal with that heat effectively and not let it build up or the drive will cook itself. They must be in an ambient no greater than 40C.
  2. Harmonics. Again because you are typically dealing with large motors when using MV power, the TDD (Total Demand Distortion, i.e. as a percent of your total plant Demand) will often be very high if you do nothing to mitigate it. I recommend an Active Front End (AFE) drive as the best solution.
  3. Servicability. Some drives are very very complicated and have a lot of components, making them very difficult to service. These are often sold cheap up front because they require a very very expensive annual service contract to keep them working. So you can end up having a much higher cost of ownership by shopping only on unit price. Others have far fewer components and are easily serviced by local personnel with very little training necessary for routine tasks. Current Source Inverters are of the type with fewer and more reliable components. Multi-pulse Voltage Source Inverters with low voltage cells in complex series parallel arrangments are the ones with the highest component count and the lowest MTBF (Mean Time between Failures) andthe highes MTTR (Mean Time To Repair). Consider all of these factors.
__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Variable Speed Drives

05/19/2012 12:00 AM

How does keeping the flow constant ensure optimum efficiency, especially if pressure conditions change? The VFD part of all this is fine, but the main concept seems questionable.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#5

Re: Variable Speed Drives

05/19/2012 12:14 AM

Dear Mr. Akram Khan,

In addition to the CR4 MEMBERS SUGGESTIONS, I want to SUPPLEMENT that

1. Pl. Specify the Percentage of Hormonics, for 5th, 7th, 11th and 13th in terms of Voltage and Current. If not specified, VFD manufacturers adopt their own Standards which will be a problem, if it is not with in the Standards.

2. Find out from the offers the Level of Heat to be DISSIPATED by VFD while working on Full-Load.

Thanks,

DHAYANANDHAN.S

Register to Reply
Associate

Join Date: Jun 2008
Location: India,Pune
Posts: 46
Good Answers: 1
#6
In reply to #5

Re: Variable Speed Drives

05/19/2012 5:21 AM

Sir,

Please note that whenever you chop the waveform your power factor gets affected.

For such a large load You may end up more charges to utility supplier. Please put variable capacitor bank to adjust the power factor.

__________________
if you are a managment professional or youth who wants to start business contact for free help for your project including financial assistance through NGO in and around Pune India
Register to Reply Score 2 for Off Topic
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#9
In reply to #6

Re: Variable Speed Drives

05/19/2012 9:45 AM

Dear Mr. Kiranwawathe,

It is OK. Where do you suggest to add the capacitor bank.?

Thanks,

DHAYANANYDHAN.S

Register to Reply Score 1 for Off Topic
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10
In reply to #6

Re: Variable Speed Drives

05/19/2012 10:29 AM

Horrible horrible answer, please refrain from posting things that you have no clue about. If someone were to take your suggestion seriously without very specific engineering, they could blow up a VERY expensive VFD!

VFDs inherently present a near unity power factor to the supply already, there is NO NEED for variable capacitors or any sort of capacitors, unless they are part of a specifically engineered harmonic filter solution designed for a specific drive in a specific installation where existing harmonics have been measured and accounted for in the design.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#11
In reply to #10

Re: Variable Speed Drives

05/20/2012 1:59 AM

What JRaef says here is important. I'll add that the engineered harmonic filters I am familiar with also include inductors, to form a tuned LC circuit that is very effective at trapping the specified and unwanted harmonics before they get reflected back to the power line.

Another post has mentioned the question of whether the motor is designed for application with a VFD. This is because the windings within the motor present a very different impedance than the feeder to the motor, so the higher frequency harmonics in the VFD output get reflected, thus (approximately) doubling the voltage in the first few turns of the winding. Motors designed for VFD use have insulation on their windings that is with a higher voltage rating, to withstand this higher effective voltage. There are methods for minimizing or eliminating this problem, so a VFD can be applied to a motor not rated for VFD use, but this must be part of the overall design from the beginning of the project.

--JMM

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2009
Location: Ontario Canada
Posts: 930
Good Answers: 31
#7

Re: Variable Speed Drives

05/19/2012 7:16 AM

You may want to look into a Magnetic drive to solve this issue. One company I am somewhat familiar with is Magnadrive. http://www.magnadrive.com/ You can control your flow with this type of device.

__________________
The fine line between cuddling and holding one down to prevent escape must be learned
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#8

Re: Variable Speed Drives

05/19/2012 8:08 AM

what type of pump are you using?

what is the OR of that pump at different frequencies?

Is the motor rated for a VSD/VFD application?

What is your required flow rate, and can the pump match your requirements at the various frequencies? What does the pump curve tell you?

If your motor is a DOL started motor using 60Hz then the RPM of the motor & pump will be constant, ( plus or minus) therefore the flow will be constant. As for inrush current.. have you thought about a "soft-starter"?

__________________
The square root of nothing is what you make it!
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#12

Re: Variable Speed Drives

05/21/2012 12:57 AM

1. VFD is costly equipment. However its higher cost can be justified if the driven pump needs variable flow. Power drawn by the motor at reduced speed will be less, thus ensuring energy saving.

2. I n a retrofit application the existing motor may not be suitable for VFD application, because of presence of harmonics. Harmonics is having influence on increased core loss and shaft current which may find a path through the bearing to earth and back unless the bearing is insulated.

3. The motor will require cooling independent of motor speed with the help of separate fans fed from an independent power supply.

4. In case of high inertia of driven equipment use of VFD has an added advantage that it can deliver rated torque at lesser speed during starting with very low starting inrush current. Low starting current therefore doesn't cause any stress on the system particularly where the supply network is weak with low fault level

In your case there is no apparent reason for adopting VFD drive as there is no need for variable flow. Moreover the driven equipment i.e. pump being a low inertia equipment doesn't call for VFD for starting purpose. The motor is 3.3 kV, 500 kW motor, so starting current with DOL starting will be approximately 600A.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#13

Re: Variable Speed Drives

05/21/2012 1:23 AM

important point here.. not all VSD's are rated for high voltage, therefore they will require as "step down" & "step up" transformer.

More cost, more hardware, more harmonics, more losses.. more headache!!

ps: I don't know of VSD's rated at 3.3Kv... always willing to learn something new!!

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Off Topic
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

brich (2); debata07 (1); dhayanandhan (2); jmueller (1); JRaef (2); kirannawathe (1); lyn (1); PWSlack (1); roy hammy (1); Tornado (1)