Transformers

05/21/2012 12:21 PM

what are all the tests is important before precharging the x-mers?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Transformers

05/21/2012 12:54 PM

Passing your electrician qualifying exam is the most important test. There will be many more tests and exams before that but one does not have to pass all of these earlier exams, just the critical ones.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Transformers

05/21/2012 2:40 PM

Well we check the nameplate to ensure we have been supplied the correct one (you may be surprised how important this first check is).

A check of the oil level and a kick of the tires is always good too.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Transformers

05/21/2012 5:40 PM

This site is not the proper place to go for an education.

Maybe try here:

Basic Electricity - Electricity Forum

Register to Reply
Participant

Join Date: May 2012
Posts: 1
#4

Re: Transformers

05/22/2012 1:50 AM

When completing the installation of electrical transformers several tests are required to determine the electrical, thermal and mechanical suitability for the system where they will be applied or used. Most of the tests performed on power transformers are defined in national standards created by IEEE, NEMA and ANSI.Electrical Transformers: Test TypesField testing can be divided into three categories.Acceptance testsPeriodic testsFailure Tests.

Automatic Electric Servo Stabilizer

Register to Reply
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#5

Re: Transformers

05/22/2012 2:20 AM

First of all Mr Prabhu You must be aware @ Primary/secondary of Tr with it's voltage level as well @ Tr use like power, distribution .lighting and so on.

You must as well know if the Tr is dist or Light than @ it's cooling as Oil type or dry type etc.

Well, you must elaborate your question as what tests for pre charging? what do you mean by charging and pre charging?

Give detail @ TR you wants to charge.

Do you know about IS code , which mentions routine tests and type test , The mandatory test pre dispatch needs to refer and that is @ Ur answer

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 11
#8
In reply to #5

Re: Transformers

05/22/2012 1:02 PM

Dear Mr. nascon,

voltage 6.6KV/415V, distrbution tr, dry type, 2.0MVA

Register to Reply
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#10
In reply to #8

Re: Transformers

05/23/2012 3:08 AM

before commencing the commissioning, please ascertain as the Transformer under installation is physically OK, The all accessories are properly attached/assembled.

Earthing etc., are in line with requirement.

Since it is 6.6 KV -415 that means this may be one of the transformer in down stream of distribution network.

The cables/jumpers as applicable are connected with proper joint box/lugs etc.

1. take insulation test with megger for primary phase to phase, phase to body

2. as above for secondary, (The secondary load side panel relay coordination, and all other megger results needs to be checked by 415 volts after megger and prior to switching 6.6 kv power.

3. Between primary to secondary earth

4. Apply 415 volt in primary side of 6.6 kv side keeping secondary open

5. After a Hrs disconnect the supply of 415 and charge the 6.6 KV power on satisfactory results of above readings

After a while start secondary feeder switching on one by one.

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Transformers

05/22/2012 3:25 AM

Did the thought of reading the transformer manufacturer's installation and commissioning instructions not occur?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: Transformers

05/22/2012 9:52 AM

Is it "pre-charging" or "charging"? What is pre-charging?

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#9
In reply to #7

Re: Transformers

05/22/2012 2:52 PM

What is pre-charging

Standing behind a wall and ramping the primary voltage up with a variac with the transformer unloaded the very first time. For when you really have 'confidence' in the transformer supplier or repairer.

__________________
jack of all trades
Register to Reply Off Topic (Score 5)
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#11

Re: Transformers

05/23/2012 3:14 AM

it is charging or you can say it is commissioning

The assembled Transformer with accessories, cables,jumpers, earthing, NGR is any etc., should be adequately and properly installed/erected.

On satisfactory insulation test as per input voltage level setting Load tap change suitably , Transformer are ready for commissioning.

Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); jack of all trades (2); lyn (1); nagaronlinepowers (1); nascon (3); prabhurak (1); PWSlack (1); redfred (1)

Previous in Forum: LT SWGR Erection & Testing   Next in Forum: MCB Energy Limiting Class

Advertisement