Air Conditioner Tripping

06/21/2012 3:30 PM

My room air conditioner (1.5ton, 9.6A,220VAC single phase) is supplied through a C20 i.e 20A MCB. When the air conditioner starts, the breaker trips after some time. I have noted the current of the air conditioner, and it takes 23A. What can be the problem? I have checked the cable and wiring, everything is ok. Is it a problem of the conditioner compressor?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Participant

Join Date: Jun 2012
Posts: 1
#1

Re: Air Conditioner Tripping

06/21/2012 4:51 PM

You need to monitor the current to see if after start up it exceeds the 23amps. If it does the compressor could be deffective, other wise replace the breaker.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#2

Re: Air Conditioner Tripping

06/21/2012 5:29 PM

If you replace the breaker, Chief, make sure it is the same size one. It is there to protect the wiring against the overcurrent that might arise from a faulty air conditioner.

__________________
Good moaning!
Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#3

Re: Air Conditioner Tripping

06/21/2012 5:30 PM

Sounds like you have a fault in the A\C unit. If it was wiring issue such as a short, the breaker in most cases would trip instantly.

At this stage, unless you know the units workings, I would be calling a A\C service provider.

It's probably the Compressor, but it could be an issue in the controls as well.

Regards,
Sapper.

__________________
It's all about the Boom! - MythBusters
Register to Reply
Guru

Join Date: Aug 2009
Location: Glen Mills, PA.
Posts: 2385
Good Answers: 114
#4

Re: Air Conditioner Tripping

06/21/2012 6:15 PM

When the A/C starts up, the fan starts first, then the compressor. Is this the "after some time" you refer to. Compressors use a higher current when starting-up than when running.

__________________
In a time of universal deceit, telling the truth is a revolutionary act. George Orwell
Register to Reply Score 1 for Good Answer
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#5
In reply to #4

Re: Air Conditioner Tripping

06/21/2012 8:22 PM

Good point!!!

Forgot about that little detail... Its is sounding more like have a compressor problem..

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#6

Re: Air Conditioner Tripping

06/21/2012 9:07 PM

If your lucky the centrifugal start switch is not switching out of start mode. You might even have a failed starter capacitor that preventing the motor from getting up to speed. My next guess is that your coolant levels are low. You may even have some motor windings that have shorted. If methods to test for any of these plausible failure modes elude you then you have a few choices. Change parts at random and hope that you get lucky. Change the whole air conditioner. Call a repairman that knows how to test this appliance.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7

Re: Air Conditioner Tripping

06/21/2012 9:33 PM

Could be a bad start/run capacitor....test it with your capacitor tester....or it could be your heat coming on at the same time, if you have a heater....

Typical wiring schematic for window unit...

http://www.american-appliance.com/old_Site/service_pages/window_ac/

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8

Re: Air Conditioner Tripping

06/21/2012 10:04 PM

There are many possible causes, but for these symptoms I would check the condenser for cleanliness, the condenser fan for operation, and the system for possible overcharge of refrigerant.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#9

Re: Air Conditioner Tripping

06/22/2012 12:29 AM

Could be too much voltage drop in wiring.

1. Has this air conditioner ever worked on this outlet/breaker? If yes, what changed just before this problem started happening?

2. You checked the cable and wiring - what size/gauge wire is it and how long is the wire from the breaker to the receptacle?

3. How much time elapses from when you push the 'ON' button until the breaker trips?

4. When you push the 'ON' button, does the compressor actually start and cool air comes out, or does the compressor just 'hum'?

5. Is this a new unit or used? If used, how old?

6. Do you have another receptacle/circuit that you could try the air conditioner on before you call a repairman?

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #9

Re: Air Conditioner Tripping

06/22/2012 3:20 AM

<...Could be too much voltage drop in wiring....>

In that case the wiring hasn't been installed correctly and the circuit should be de-energised until a local qualified electrician has checked it out.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#10

Re: Air Conditioner Tripping

06/22/2012 12:40 AM

Is it new or how long it was running w/o tripping?. The mcb may be defective or use C type MCB. Also tell us when was it last serviced,normally agents should do it.

__________________
pnaban
Register to Reply
Associate

Join Date: Dec 2010
Location: Australia
Posts: 46
Good Answers: 5
#11

Re: Air Conditioner Tripping

06/22/2012 12:50 AM

www.youtube.com/watch?v=KpH1Zn3hPuIw

Check this out for technical assistance.....

__________________
Have you tried turning it off and on?
Register to Reply Off Topic (Score 5)
Anonymous Poster #1
#12

Re: Air Conditioner Tripping

06/22/2012 12:58 AM

There are some pieces of information missing to pinpoint the problem.You didn't mention if a) The 23A reading was at start up and then levels to full load (9.6A). b) What wire gauge is used in that circuit. c) If is a dedicated circuit. Is this the unit you always had or is a new one with higher tonnage than what you had before?. Let me go orderly.First read the specs label it should show the FLA on the cold mode and also on the heat mode (if it's an AC/Heat pump).

a) If the 23A is a constant reading that's just a little less than 2.5 the normal load so you've got either bad compressor, overcharged refrigerant lines, low level refrigerant ( in the compressor it acts as a lubricant too), or bad bearings, adding mechanical drag and therefore increasing the load demand; that means you've got bad motor, bad compressor or both. If the unit is an AC/Heat pump and the sum load of both modes comes about 23A it means it's pulling both modes simultaneously. That would not happen with an electromechanical control because the 2-pole (?) relay would connect either load not both by swinging over. If it's an electronic control it could happen if it's faulty and is sending signal to both modes. Result will trip the breaker because it's overloading it. You've got a bad control module.

b) If it's an old house, it was mostly used #14 gauge wire which max load is 15A, is going to trip the breaker after a while for 2 reasons: It's overloading the breaker (23/20) and it's overloading the wire ampacity (23/15) so the problem gets compounded. The breaker is doing its job!.

c) If it's not a dedicated circuit, something else might kick in while the unit is running, overloading the circuit and tripping the breaker. Again, the breaker is doing its job!. To summarize. Make sure you've got the right wire gauge in the circuit. Make sure it's dedicated. Last but not least, if it's a new unit with higher tonnage you've got 2 options bring her down to the original specs or replace the wiring in the circuit to bring it up to specs. A 20A breaker should never trip on a 9.6A load.

Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#13

Re: Air Conditioner Tripping

06/22/2012 2:07 AM

Check operation of condenser fan motor, compressor winding, condition of coils, capacitors and control wire diagrams with the as stance of trained a.c mechanic.

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#15

Re: Air Conditioner Tripping

06/22/2012 5:57 AM

Make sure the breaker is HACR rated.These breakers are designed to take the high-start current of the compressor.

If the breaker is also used for turning the unit off and on, the breaker should also be rated for Switch-Duty.

Based on the information you provided, the the 23 amps seems to be the starting current,which will be solved by using the right type breaker.

If this is the running current,you have other problems, such as a fan motor with bad bearings(They are not always noisy,they are usually sleeve type bearings that wear out and let the rotor drag the stator) replacement end-bells are usually available. (A very simple repair:4 screws+nuts after removing fan from unit).

High head pressure on the compressor can also increase current draw.

Make sure the evaporator and condenser coils are clean.They can be cleaned easily at a manual car wash, but be careful not to bend the fins with the high pressure, and do not direct the water into the control box.Everything else outside of the window is safe to wash down.The inside(evaporator coil) is safe to wash down if you observe the previous caveat.

After cleaning, let the unit rest at a slight angle toward the back to drain.When it has drained properly, reinstall in window.

Install a new air filter of the proper type.

A coil cleaning chemical is also available the foams and pushes dirt out of the coils, but it is not a good as the car-wash wand.If you buy the coil cleaner, be sure to get the "No Rinse" type that is safe to leave on the coils without the need to rinse it off.

Good luck!

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#16

Re: Air Conditioner Tripping

06/22/2012 7:23 AM

Is that 23A continuous or only when starting?

If it is only on starting then that's about right.

If it is continuous then you are either over gassed or the supply voltage (at the compressor) is low.

If the supply voltage is low then you either have loose connections or undersized conductors.

Does the aircon actually seem to work ok apart from this nuisance tripping?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#17

Re: Air Conditioner Tripping

06/22/2012 12:13 PM

No one asked yet-

Has this A/C unit been in place for some time and operated OK, but now is a problem or is this a NEW installation?

IF it is new, your breaker may need to be changed to one that is designed to tolerate the inrush current of the compressor start-up. Some residential units do not have this capacity and will see that inrush as a short and trip "too soon".

If it has been operating OK for a while and is just now causing a problem, you are back to the service call.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#18

Re: Air Conditioner Tripping

06/22/2012 12:57 PM

It could be a few things but it depends on when it trips the breaker. On most single phase A/C units the compressor has a start winding with a start capacitor. When the compressor is called for the start relay will energize the capacitor and give the compressor a "kick start" in the start winding of the compressor motor. After the compressor comes up to speed it develops back EMF (electro motor force) that de-energizes or opens the relay and moves the power directly to the run winding keeping the motor running. If the compressor bearings are getting tight or if the start capacitor is weak the compressor will draw high amps trying to start.

If it trips while running, again the compressor may have tight bearings in it (replace compressor) or the unit may simply be dirty causing high discharge pressures causing the compressor to run over amps. Wash out the unit thoroughly and try again.

If it is a window style unit it would be cost effective to simply replace the entire unit instead of the compressor since you would get a new warranty with a new unit and odds are that after you change the compressor out the fan motor will fail next.

__________________
To be or not to be........ok that's a trick question.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2012
Posts: 31
Good Answers: 1
#19

Re: Air Conditioner Tripping

06/22/2012 4:16 PM

Many good points have been presented hear, like the wire size, and length, are the connections tight. If the problem is new, and the A/C has functioned properly in the past we need to determine what has changed, creating the malfunction. If you find the compressor windings shorted or grounded (or other major repair required), consider the age of the unit; can you relied on a warranty. A window shaker is like a Bick Lighter, not designed to be worked on, but replaced. If you get more than six years of service, your doing real good.

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#20

Re: Air Conditioner Tripping

06/22/2012 6:01 PM

It could be the compressor or possibly the condenser coil is plugged on the air side with debris from nearby cottenwood trees. You can check that visually and clean the condenser coil if needed.

If it isn't that obvious, call a reputable serv ice company to check it out for you.

Lou Bindner

Register to Reply
Commentator

Join Date: May 2012
Location: Sutter buttes - East 50 miles you found me
Posts: 59
Good Answers: 3
#21
In reply to #20

Re: Air Conditioner Tripping

06/22/2012 6:10 PM

Its cousin Lou

__________________
Lurking Always Lurking.........................in the Shadows
Register to Reply
Register to Reply 21 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!