Anonymous Poster #1

Inst & DCS

06/26/2012 11:08 AM

Hi All,

We having issue in process measurement, the field instrument and DCs reading doesn't match. any advise???

Regards

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Inst & DCS

06/26/2012 11:49 AM

It could be any of a number of things. Eliminate the possibilities of loop voltage too low/loop resistance too high, and instrument ranging errors, and re-post afterwards with the findings. Do feel free to describe the instrument and the DCS in use as well. <subscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Commentator

Join Date: Jul 2008
Posts: 56
Good Answers: 1
#2

Re: Inst & DCS

06/27/2012 1:16 AM

what is distance between Instrument and system, some time problems are very basics don't forget to check scaling in DCS for that instrument.

Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#3

Re: Inst & DCS

06/28/2012 8:47 AM

To what tolerance are you reading the outputs and comparing them?

We try very hard to not put in an instrument display if the system HMI is also to display the same reading. (never happens - customers always want an instrument readout) The conversion from 4-20ma (analog) to digital in the processor introduces a potential for a minor error. It is very common for a temperature transmitter to display, for example, 25.67 degrees C while the HMI on the DCS shows 25.64 degrees. Is this what the problem is? If so, little can be done, other than setting one display to round to the nearest whole number. At that tolerance they should match. If not, then you have more serious problems and we need more information to decipher.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#4

Re: Inst & DCS

07/11/2012 8:46 AM

How big is the difference? If it's small, it could be a calibration problem, as Phys says.

If it's big, it may be a scaling problem. Your instrument is, say, 0 to 100°C, and converts temperature to 4 to 20mA. DCS, however, is configured to interpret 4 to 20mA as 0 to 200°C. I've seen this happen a lot.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.